Default Gas Range, No Vent

Inspecting a home today I found a gas cook-top unit that was installed in an island in the middle of the kitchen (replacing an electric unit I believe). There is probably 5 to 6 feet clearance to the ceiling, but the buyer is worried that there is no vent. I'm pretty sure one is not required, but I was hoping to get some feedback from someone who knew for sure.

Thanks.
Reply With Quote
Need a home inspection in Texas? Check out InterNACHI's listing of Texas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/7/10, 7:53 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Gas Range, No Vent

Quote:
Originally Posted by ehyde View Post
Inspecting a home today I found a gas cook-top unit that was installed in an island in the middle of the kitchen (replacing an electric unit I believe). There is probably 5 to 6 feet clearance to the ceiling, but the buyer is worried that there is no vent. I'm pretty sure one is not required, but I was hoping to get some feedback from someone who knew for sure.

Thanks.
Have you checked the local codes?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 4/7/10, 8:00 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Gas Range, No Vent

Gas combustion produces large quantities of water vapor (I believe it's about six liters of water per 100,000 BTU).

An exhaust fan is always advisable to help exhaust the excess water vapor outside of the building envelope.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 4/7/10 at 8:03 PM..
Reply With Quote
  #4  
Old 4/7/10, 8:12 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Gas Range, No Vent

What I say, whether gas or electric: "No range hood or exhaust system was provided for the kitchen appliance cooking surface. Although not required, we and the manufacturers of most cooking appliances recommend it."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 4/7/10, 8:15 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Gas Range, No Vent

Did you check to see if it had a downdraft vent? I know just asking



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #6  
Old 4/7/10, 8:40 PM
Bobby G. Michael Bobby G. Michael is offline
InterNACHI Member
 
Join Date: Jan 2010
Posts: 187
Default Re: Gas Range, No Vent

Same here Joe.



Alabama Home Inspections
www.thebirminghamhomeinspector.com
Home Inspections in Birmingham, Montgomery, Huntsville, and Tuscaloosa.
Reply With Quote
  #7  
Old 4/7/10, 9:05 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Gas Range, No Vent

Quote:
Originally Posted by jbushart View Post
Have you checked the local codes?
Exactly, exhaust to the exterior is not always required.
Reply With Quote
  #8  
Old 4/8/10, 10:01 AM
rspermo rspermo is offline
Active Poster
 
Join Date: Feb 2009
Posts: 155
Please Note: rspermo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Range, No Vent

Eric,

Don't forget to recommend a quality (10 - 35 ppm) CO detector.
Reply With Quote
  #9  
Old 4/8/10, 10:32 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Gas Range, No Vent

Your statement that "the buyer is worried" means that you should not guess your way through this or assume anything. If there is a local code governing this, refer to it and recommend that your client do a permit research (to include the building permit) to ensure that the local codes were applied. Avoid making any statement that it does or does not "meet code". With the code book in front of you, you have a 50/50 chance of being right, at best.

If there is no codes governing it, make your recommendation based upon safety and protection to the property.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #10  
Old 4/15/10, 9:31 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Gas Range, No Vent

Would you have been equally concerned if it had been a gas cooktop with a microwave/fan (not vented to the outside) above it?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA

Last edited by fnewman; 4/15/10 at 10:26 PM..
Reply With Quote
  #11  
Old 4/15/10, 1:06 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Gas Range, No Vent

Quote:
Originally Posted by fnewman View Post
Would you have been equally concerned if it had baan a gas cooktop with a microwave/fan (not vented to the outside) above it?
I had this exact scenario on Tuesday mornings inspection. I wrote a comment about it stating that it would be best to vent it to the exterior but if that is not possible, that they should at the very least install a CO monitor.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #12  
Old 4/15/10, 10:29 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Gas Range, No Vent

Quote:
Originally Posted by mnahrgang View Post
I had this exact scenario on Tuesday mornings inspection. I wrote a comment about it stating that it would be best to vent it to the exterior but if that is not possible, that they should at the very least install a CO monitor.
I have some boiler plate/narrative now in all reports that have Gas and or fireplaces that recommend at least one CO Detector.......
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Kitchen Range Down Draft Vent rnewland General Inspection Discussion 3 2/27/09 10:18 PM
Microwave range vent clearance mbarnett Inspecting HVAC Systems 3 5/15/08 5:21 AM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 9:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM


All times are GMT -4. The time now is 11:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts