Is there a reference code regarding the placement of a gas shut off valve within the furnace cabinet. I think it should be mounted outside of the cabinet.
|
|
#2
|
|||
|
|||
|
xxxx
Last edited by ddivito; 3/8/09 at 10:40 PM.. |
|
#3
|
||||
|
||||
|
This wording should help.
12. SHUT-OFF VALVES: Valves used in connection with gas piping shall be approved types. An accessible approved shutoff valve shall be installed in the fuel supply piping outside of each appliance and ahead of the union or connector within 6 feet of the appliance and in the same room. |
|
#4
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
|||
|
|||
|
The installation you are showing would be failed by any AHJ in my area, if properly inspected, and caught by the inspector.
As for HUD/FHA,etc. standards, I doubt they require that type of shut-off installation, especially when the typical gas appliance Manufacturer requires the shut-off be installed outside the appliance. |
![]() |