Default Gas Shut Off Location

Is there a reference code regarding the placement of a gas shut off valve within the furnace cabinet. I think it should be mounted outside of the cabinet.

gas-shut-off-location-lincoln-002-medium-.jpg.jpg
Views:	160
Size:	72.2 KB
ID:	27310




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #2  
Old 3/8/09, 10:36 PM
Dennis DiVito Dennis DiVito is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Fairfield, VA
Posts: 38
Default Re: Gas Shut Off Location

xxxx

Last edited by ddivito; 3/8/09 at 10:40 PM..
Reply With Quote
  #3  
Old 3/8/09, 11:43 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Gas Shut Off Location

This wording should help.
12. SHUT-OFF VALVES: Valves used in connection with gas
piping shall be approved types. An accessible approved shutoff
valve shall be installed in the fuel supply piping outside of
each appliance and ahead of the union or connector within 6
feet of the appliance and in the same room.
Reply With Quote
  #4  
Old 3/9/09, 7:26 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Shut Off Location

Quote:
Originally Posted by relliott View Post
This wording should help.
12. SHUT-OFF VALVES: Valves used in connection with gas
piping shall be approved types. An accessible approved shutoff
valve shall be installed in the fuel supply piping outside of
each appliance and ahead of the union or connector within 6
feet of the appliance and in the same room.
For manufactured homes you have to use the HUD standards as most gas piping comes up from the flooring straight into the furnace cabinet. Shut offs are located in the compartment.
Reply With Quote
  #5  
Old 3/9/09, 8:21 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Gas Shut Off Location

The installation you are showing would be failed by any AHJ in my area, if properly inspected, and caught by the inspector.
As for HUD/FHA,etc. standards, I doubt they require that type of shut-off installation, especially when the typical gas appliance Manufacturer requires the shut-off be installed outside the appliance.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
2 Shut offs for exterior A/C dmacy Electrical Inspections 12 10/12/06 10:29 PM
A/C location of expansion device vs line temps. bking Inspecting HVAC Systems 9 5/29/06 4:16 PM
Gas line is shut off but pilot light is burning... jweinberg Inspecting HVAC Systems 15 2/13/06 1:43 PM


All times are GMT -4. The time now is 11:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts