  #1  
Old 12/29/06, 6:27 PM
Mark R. Long's Avatar
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 315
Default Gas Venting Concern for Water Heater

The vent for this NG water heater slopes downward, about 3/4" in 1' length before it goes into the larger vent from the NG furnace, which does a have sharp upward slope. Then larger vent then feeds immediately into a masonry chimney. Is this downward slope off the water heater appropriate?



Mark
MD HI Lic # 30090
BPI Certified Building Analyst

PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #2  
Old 12/29/06, 6:32 PM
Mark R. Long's Avatar
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 315
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by mlong
The vent for this NG water heater slopes downward, about 3/4" in 1' length before it goes into the larger vent from the NG furnace, which does a have sharp upward slope. Then larger vent then feeds immediately into a masonry chimney. Is this downward slope off the water heater appropriate?

Forgot to load my picture the first time!
Attached Thumbnails
gas-venting-concern-water-heater-p1010056.jpg  



Mark
MD HI Lic # 30090
BPI Certified Building Analyst

PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #3  
Old 12/29/06, 6:50 PM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 371
Default Re: Gas Venting Concern for Water Heater

No, it's not right...it should have an upward grade of 1/4" per foot. Looks they ran out room to slope properly and didn't bother to re-do the tie-in in the proper location so they would have enough room for proper grade.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #4  
Old 12/29/06, 8:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by mlong
Is this downward slope off the water heater appropriate?
Absolutely not. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 12/29/06, 9:46 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by jpope
Absolutely not. . .

Ditto my man Jeff P.

Heated gas only flows uphill.
Reply With Quote
  #6  
Old 12/30/06, 12:40 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Gas Venting Concern for Water Heater

The biggest issue with reverse slope vent connectors is that condensation/moisture/debris can build up at a low point. It doesn't appear to be a huge issue with that one assuming there are no low points between the elbow and the connection to the larger (furnace/boiler?) vent connector (hard to tell from such a small pic), and the larger one has correct pitch back to the equipment. But that doesn't make it right, and I would still write up the concern.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #7  
Old 12/30/06, 3:29 PM
Mark R. Long's Avatar
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 315
Default Re: Gas Venting Concern for Water Heater

Thanks for the replies, everyone!



Mark
MD HI Lic # 30090
BPI Certified Building Analyst

PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #8  
Old 12/30/06, 3:35 PM
Mark R. Long's Avatar
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 315
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by roconnor
The biggest issue with reverse slope vent connectors is that condensation/moisture/debris can build up at a low point. It doesn't appear to be a huge issue with that one assuming there are no low points between the elbow and the connection to the larger (furnace/boiler?) vent connector (hard to tell from such a small pic), and the larger one has correct pitch back to the equipment. But that doesn't make it right, and I would still write up the concern.

JMO & 2-nickels ...
I too, was not sure that it was a "big" deal since it was such a short run and it was close to the larger vent. That was the reason that I even posed the question. My "feeling" was that it was probably getting adequate draft.

Since this does deal, however, with a potentially lethal situation, I did write it up.



Mark
MD HI Lic # 30090
BPI Certified Building Analyst

PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #9  
Old 1/2/07, 8:12 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by mlong
My "feeling" was that it was probably getting adequate draft ... Since this does deal, however, with a potentially lethal situation, I did write it up.
Even though determining adequate draft is beyond an inspection, adequate draft is another concern ... but at least in my mind not as big an issue as creating a low point since it's not a long run and/or severe pitch down to the larger vent connector from the pic/description (would be a significant concern in my mind if that was the case). But again it doesn't make it right, and I think you made the correct call to write it up.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #10  
Old 1/3/07, 8:48 AM
Mark R. Long's Avatar
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 315
Default Re: Gas Venting Concern for Water Heater

Thanks, Robert.



Mark
MD HI Lic # 30090
BPI Certified Building Analyst

PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #11  
Old 1/3/07, 9:18 AM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,548
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by roconnor
The biggest issue with reverse slope vent connectors is that condensation/moisture/debris can build up at a low point. It doesn't appear to be a huge issue with that one assuming there are no low points between the elbow and the connection to the larger (furnace/boiler?) vent connector (hard to tell from such a small pic), and the larger one has correct pitch back to the equipment. But that doesn't make it right, and I would still write up the concern.
I agree, additionally the low slope interferes with proper draft which creates a condition where back drafting is that much easier. It wouldn't take too much negative pressure to cause it, might be as simple as operating a clothes dryer and a bath fan at the same time.

These days when I inspect homes with natural gas I automatically add a note cautioning that it would be wise to replace one of the smoke detectors in the sleeping area with a combo Smoke/Carbon Monoxide detector.



"A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"

Last edited by jburkeson1; 1/3/07 at 9:22 AM..
Reply With Quote
  #12  
Old 1/3/07, 9:46 AM
Mark R. Long's Avatar
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 315
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by jburkeson1
These days when I inspect homes with natural gas I automatically add a note cautioning that it would be wise to replace one of the smoke detectors in the sleeping area with a combo Smoke/Carbon Monoxide detector.
I do the same if the home has any fuel burning appliance, gas, oil, wood, etc.



Mark
MD HI Lic # 30090
BPI Certified Building Analyst

PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #13  
Old 1/4/07, 1:53 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by jburkeson1
... additionally the low slope interferes with proper draft which creates a condition where back drafting is that much easier. It wouldn't take too much negative pressure to cause it ...
More of a concern with a long vent connector or severe downward pitch after the elbow ... but again, it doesn't make it right, and is also poor practice.

Quote:
Originally Posted by jburkeson1
These days when I inspect homes with natural gas I automatically add a note cautioning that it would be wise to replace one of the smoke detectors in the sleeping area with a combo Smoke/Carbon Monoxide detector.
Especially the CO detector if there is a sleeping room on the same level as the equipment ... and new smoke detectors throughout is always a good recommendation if the system is suspect/lacking.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #14  
Old 1/4/07, 8:30 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Venting Concern for Water Heater

If the hot gas will NOT GO downhill...where does it go in this situation?
Reply With Quote
  #15  
Old 1/4/07, 9:16 AM
Mark R. Long's Avatar
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 315
Default Re: Gas Venting Concern for Water Heater

Quote:
Originally Posted by tneumann
If the hot gas will NOT GO downhill...where does it go in this situation?
Since you put the smiley face after your statement, Tony, I'm not sure if you were being serious or not.

The exhaust gases can possibly backdraft out into the room, the living space of the house. The exhaust vent on a water heater is not sealed at the top of the heater, there is a gap between the heater and the vent. So if the venting isn't working/drafting properly, fumes/carbon monoxide can easily backdraft into the room.



Mark
MD HI Lic # 30090
BPI Certified Building Analyst

PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Heater Venting kgoff Plumbing Inspections 5 3/10/07 9:18 AM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
Venting of Heater and Water heater dnasser Inspecting HVAC Systems 3 11/6/06 11:57 AM
Water Heater Venting dedwards Plumbing Inspections 1 8/19/06 12:46 PM


All times are GMT -4. The time now is 5:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts