The vent for this NG water heater slopes downward, about 3/4" in 1' length before it goes into the larger vent from the NG furnace, which does a have sharp upward slope. Then larger vent then feeds immediately into a masonry chimney. Is this downward slope off the water heater appropriate?
|
|
#2
|
|||
|
|||
|
Quote:
Forgot to load my picture the first time! |
|
#3
|
||||
|
||||
|
No, it's not right...it should have an upward grade of 1/4" per foot. Looks they ran out room to slope properly and didn't bother to re-do the tie-in in the proper location so they would have enough room for proper grade.
Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right!
|
|
#4
|
||||
|
||||
|
Quote:
|
|
#5
|
|||
|
|||
|
Please Note:
tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Ditto my man Jeff P. Heated gas only flows uphill. |
|
#6
|
||||
|
||||
|
The biggest issue with reverse slope vent connectors is that condensation/moisture/debris can build up at a low point. It doesn't appear to be a huge issue with that one assuming there are no low points between the elbow and the connection to the larger (furnace/boiler?) vent connector (hard to tell from such a small pic), and the larger one has correct pitch back to the equipment. But that doesn't make it right, and I would still write up the concern.
JMO & 2-nickels ... Robert O'Connor, PE Eagle Engineering & Inspections Adjunct Professor NACHI Education Committee www.reporthost.com/eagleengineering I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#7
|
|||
|
|||
|
Thanks for the replies, everyone!
|
|
#8
|
|||
|
|||
|
Quote:
Since this does deal, however, with a potentially lethal situation, I did write it up. |
|
#9
|
||||
|
||||
|
Quote:
JMO & 2-nickels ... Robert O'Connor, PE Eagle Engineering & Inspections Adjunct Professor NACHI Education Committee www.reporthost.com/eagleengineering I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#10
|
|||
|
|||
|
Thanks, Robert.
|
|
#11
|
||||
|
||||
|
Quote:
These days when I inspect homes with natural gas I automatically add a note cautioning that it would be wise to replace one of the smoke detectors in the sleeping area with a combo Smoke/Carbon Monoxide detector. Last edited by jburkeson1; 1/3/07 at 10:22 AM. |
|
#12
|
|||
|
|||
|
Quote:
|
|
#13
|
||||
|
||||
|
Quote:
Quote:
JMO & 2-nickels ... Robert O'Connor, PE Eagle Engineering & Inspections Adjunct Professor NACHI Education Committee www.reporthost.com/eagleengineering I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#14
|
||||
|
||||
|
If the hot gas will NOT GO downhill...where does it go in this situation?
Tony Neumann AtEase Home Inspections Http://www.aeinspections.com 719-243-2996 Colorado Springs, Colorado Woodland Park, Colorado Teller and El Paso County, Colorado |
|
#15
|
|||
|
|||
|
Quote:
The exhaust gases can possibly backdraft out into the room, the living space of the house. The exhaust vent on a water heater is not sealed at the top of the heater, there is a gap between the heater and the vent. So if the venting isn't working/drafting properly, fumes/carbon monoxide can easily backdraft into the room. |
![]() |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Water Heater Venting | kgoff | Plumbing | 5 | 3/10/07 10:18 AM |
| Venting an oil-fired water heater | mh718 | HVAC | 3 | 11/16/06 10:36 AM |
| Venting of Heater and Water heater | dnasser | HVAC | 3 | 11/6/06 12:57 PM |
| Water Heater Venting | dedwards | Plumbing | 1 | 8/19/06 1:46 PM |