  #1  
Old 11/12/10, 3:26 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default What is going on here?

This was in a home built in 2003 in Lake Worth, Fl.
It is a fresh air intake from the exterior into the intake line which is in the garage.
Attached Thumbnails
going-here-baseman-006-small-.jpg.jpg
Views:	118
Size:	51.4 KB
ID:	40101   going-here-baseman-007-small-.jpg.jpg
Views:	113
Size:	50.2 KB
ID:	40102  
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/12/10, 3:45 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: What is going on here?

Seems like a make shift Radon mitigation system.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #3  
Old 11/12/10, 5:55 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: What is going on here?

Could it be for a HRV(Heat recovery ventilator) or ERV (energy recovery ventilator)?
Reply With Quote
  #4  
Old 11/12/10, 6:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: What is going on here?

Is this a Cat 4 furnace and do you have any pics showing the other end?
Reply With Quote
  #5  
Old 11/12/10, 10:27 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: What is going on here?

We don't have Cat 4 furnaces here in S Florida...hell 1/2 the houses don't have ANY type of heat.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #6  
Old 11/12/10, 11:42 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: What is going on here?

Well he did say air intake and this is the HVAC section.
Maybe he meant makeup air to closet.
Reply With Quote
  #7  
Old 11/13/10, 6:57 AM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default Re: What is going on here?

It is an electric, 3 ton split system air conditioning unit.
The line is, as you can see, metal and not insulated. The box, which is above the soffit, goes to a vent outside.
The homeowner stated that this was a new requirement when the home was built.

It is for make-up air that runs through the attic, down through the garage ceiling , and into the return plenum, which attaches to the stand the air handler sits on and then goes through the ceiling and connects with the other return registers in the bedrooms. There is also a damper right where the line connects to the plenum.

I am assuming that the box pictured is some type of filter so that unwanted odors do not enter the home.

I couldn't tell if condensation was building up which caused the sheathing to rot, or if it was from a roof leak.

If the hot air from the outside can get in, what is to prevent the cold air from the home to get out?
Reply With Quote
  #8  
Old 11/13/10, 8:47 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is going on here?

Quote:
Originally Posted by evandeven View Post
It is an electric, 3 ton split system air conditioning unit.
The line is, as you can see, metal and not insulated. The box, which is above the soffit, goes to a vent outside.
The homeowner stated that this was a new requirement when the home was built.

It is for make-up air that runs through the attic, down through the garage ceiling , and into the return plenum, which attaches to the stand the air handler sits on and then goes through the ceiling and connects with the other return registers in the bedrooms. There is also a damper right where the line connects to the plenum.

I am assuming that the box pictured is some type of filter so that unwanted odors do not enter the home.

I couldn't tell if condensation was building up which caused the sheathing to rot, or if it was from a roof leak.

If the hot air from the outside can get in, what is to prevent the cold air from the home to get out?
I doubt very seriously that the local AHJ requires outside make up air but on the other hand anything is possible.

Don't assume anything the box pictured probably has no filter just a square transition from the round duct to allow a square grill in the soffit.

All duct work associated with the central systems are required to be insulated in non-conditioned spaces such as attics.

You last question tells me that HVAC is not your high suit and that you do not understand the system as a whole. I am not trying to be nasty here but some good advice would be to do some serious reading on the subject



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 11/13/10, 11:38 AM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default Re: What is going on here?

Quote:
Originally Posted by cbottger View Post
I doubt very seriously that the local AHJ requires outside make up air but on the other hand anything is possible.

Don't assume anything the box pictured probably has no filter just a square transition from the round duct to allow a square grill in the soffit.

All duct work associated with the central systems are required to be insulated in non-conditioned spaces such as attics.

You last question tells me that HVAC is not your high suit and that you do not understand the system as a whole. I am not trying to be nasty here but some good advice would be to do some serious reading on the subject

I thank you for your reply, most of it.
I am posting this because it is something I haven't seen in 22 years of performing inspections.
Trust me, I am well aware of how the system works.

I am also well aware of the code requirement for insulation (R-4.2) in an enclosed attached garage, which is where this line is located. I sent that along with another code reference


Quote:
(2. No ventilation or air-conditioning system makeup air shall be provided to conditioned space from attics, crawl spaces, attached enclosed garages or outdoor spaces adjacent to swimming pools or spas.)
Which would imply, that there is a possibility that make up air from the exterior is allowed.

If you have anything, constructive to add, please do so.
Reply With Quote
  #10  
Old 11/13/10, 3:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is going on here?

Quote:
Originally Posted by evandeven View Post
I thank you for your reply, most of it.
I am posting this because it is something I haven't seen in 22 years of performing inspections.
Trust me, I am well aware of how the system works.

I am also well aware of the code requirement for insulation (R-4.2) in an enclosed attached garage, which is where this line is located. I sent that along with another code reference


Which would imply, that there is a possibility that make up air from the exterior is allowed.

If you have anything, constructive to add, please do so.

I don't know if it is constructive or not but I REALLY STRUGGLE with the last question you posted as to your understanding of the system as a whole. Nuff said

As to make up air of course it is allowed from the exterior of the home just restricted as to where it can be taken from. Normally not required as 10% of make up air into a home is obtained through doors and windows



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 11/13/10, 4:08 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default Re: What is going on here?

Quote:
Originally Posted by cbottger View Post
I don't know if it is constructive or not but I REALLY STRUGGLE with the last question you posted as to your understanding of the system as a whole. Nuff said
I'll enlighten you as to the last question. Here , on new construction, it is required that there is an intake in each room for make up air in addition to the main intake. This is tied into a box in the attic, in this case, in the middle of the hallway. This is also the filter location. There is a 16 inch line that runs to another box in the garage, which extends through the garage ceiling.

The fresh air intake line goes from this box, in the garage, through the garage ceiling, and this is the line that exits the building through the box shown.

So, when the system is off, what is to prevent the air that is in the rooms, to go through the duct work for make up air and then out of the home?

I will be gracious enough to assume that you meant that I was referring to air in the system, going backwards, through the cooling coils and then out of the building.
That may be possible, but highly unlikely. It wasn't what I was referring to with the comment you are referring to.

As to a filter, what I was referring to was some type of odor arrestor. Where the vent is happens to be on the side of the home where an ally is. Which is where all of the others place their garbage for pick up. There is also a neighbors house right near the vent. Unwanted odors may enter the home.

Although this may be required by the code, and I have a call in to the building department regarding the installation, I wouldn't want it in my home.
Reply With Quote
  #12  
Old 11/13/10, 4:49 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: What is going on here?

Correct me if I misread something but it appears the original post is all about a portion of the return air being drawn in from the exterior.

This is typical on energy star homes or homes built with attempted energy saving methods. Research is being done to change the standards since the big savings are not being achieved so far.

http://www.google.com/url?sa=t&sourc...DE9a0gQrI7jzOA


http://www.greenbuildingadvisor.com/...ort/html/13663

http://en.wikipedia.org/wiki/Ventilation_(architecture)



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #13  
Old 11/13/10, 4:56 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: What is going on here?

Quote:
Originally Posted by rhensel View Post
We don't have Cat 4 furnaces here in S Florida...hell 1/2 the houses don't have ANY type of heat.
why is it that I'm getting the inclination that you're talking out your ***! ?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/13/10, 4:59 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: What is going on here?

Quote:
Originally Posted by evandeven View Post
I thank you for your reply, most of it.
I am posting this because it is something I haven't seen in 22 years of performing inspections.
Trust me, I am well aware of how the system works.

I am also well aware of the code requirement for insulation (R-4.2) in an enclosed attached garage, which is where this line is located. I sent that along with another code reference


Which would imply, that there is a possibility that make up air from the exterior is allowed.

If you have anything, constructive to add, please do so.
why do you have to insulate a fresh air intake that is working on the same temperature as that in the garage?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 11/13/10, 5:11 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: What is going on here?

Quote:
I'll enlighten you as to the last question.
I'll enlighten you, you don't know what your talking about.

If you knew what you're talking about you wouldn't be posting the question.

We all know what this is, you obviously don't.

Who assigned you to be in charge over the authority having jurisdiction (AHJ)in Florida?

I can only surmise that you played with HVAC equipment for a portion of your life.

If that chunk of metal pipe you showed us from the attic enters into the garage, I'd be more concerned about it not being fire rated!

Go ahead and call the AHJ and show them just how stupid the rest of us are.

Thanks

Quote:
So, when the system is off, what is to prevent the air that is in the rooms, to go through the duct work for make up air and then out of the home?
you're the one that knows exactly what's going on! It doesn't matter how big of a hole you have in the side of your house if there is not a difference in pressure between the inside and the outside the air will not flow. need I remind you of this?

It appears that you're making some sort of assumption without any documented testing results. What is the pressure differential of the building? Where is the neutral plane within the building?

With this type of system installed it will generally create positive pressure in the building (in most circumstances). What is the pressure of the building? Or did you actually evaluate that?

You ask us to evaluate which you have not evaluated. We cannot give you a definitive answer unless you provide the necessary data.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts