Default grinding noise on startup

I have 2 ac units that grind on startup (one worse than the other) It only lasts for a second then stops. I had the hvac guy here to check it out and he's stumped. amp test proved normal. Things I can thing of are bent fins, bad blower motor (or low/no oil) and low amount of refigerant although the air is cool as it blows into the home. Any other thoughts?
Reply With Quote
  #2  
Old 7/12/07, 5:36 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: grinding noise on startup

motor bearings maybe? You would be suprised at how much damage some units can have and still run.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 7/12/07, 9:50 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: grinding noise on startup

Quote:
Originally Posted by Scott Schultz
I have 2 ac units that grind on startup (one worse than the other) It only lasts for a second then stops. I had the hvac guy here to check it out and he's stumped. amp test proved normal. Things I can thing of are bent fins, bad blower motor (or low/no oil) and low amount of refigerant although the air is cool as it blows into the home. Any other thoughts?
You can rule out low oil/no oil and low freon would not be your problem.

You stated that both units were making similar noises leading me to believe that both units were serviced and or installed by the same person and could have an overcharge with some liquid lying in the crankcase on startup and this would make a noise.

A bent or broken internal compressor mounting spring could also make a noise but the probability of both compressors having that same problem is un-likely.

If it is not the fan or the freon charge but is an internal noise from the compressor there is no exact way to determine this on a hermetically sealed unit and you will probally never know the reason until failure.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 7/13/07, 12:31 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: grinding noise on startup

Refrigerant lines that rise to a vertical height of more than what is stated in the installation manual will cause this.

ie. Compressor on ground and air handler in attic of two story house can exceed the limit.

Will sound like gravel churning for a few seconds.

They sell a kit I think to solve this, check valve or something?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 7/13/07, 1:13 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: grinding noise on startup

Quote:
Originally Posted by bking
Refrigerant lines that rise to a vertical height of more than what is stated in the installation manual will cause this.

ie. Compressor on ground and air handler in attic of two story house can exceed the limit.

Will sound like gravel churning for a few seconds.

They sell a kit I think to solve this, check valve or something?
Bruce where would you put a check valve in what freon line and what would be its purpose.

I personally have never read any MFG instulation instructions that restricted verticle height they will require the size of the liquid and suctions lines to be increased for length but not necessarly for height. Have installed tons of units on two story homes with no problems



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 7/13/07 at 1:27 AM..
Reply With Quote
  #6  
Old 7/13/07, 5:33 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: grinding noise on startup

This may also be a simple rain shield on the fan motor.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #7  
Old 7/13/07, 7:10 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: grinding noise on startup

Bruce & Charlie,

I think you are on to something there.
It's impossible to hear the grinding over this board so this is a WAG not a SWAG.

Seeing that both units are doing it, it should not be a defect. It is unlikely that both would have the same defect at the same time. (ie. fans, motors rubbing, bearings, blower wheels)

Also, scroll compressors have a tendency of being loud (starting, running and especially when stopping as they run backwards during pressure equalization).

Now, on to you guys.
Refrigerant migration could be a factor.

Evap up, cond down: If the refrigerant metering device is other than a TXV it may flood the compressor as it allows the liquid refrigerant to pass through the metering device rapidly until equalized. You guys hear this surging of refrigerant for a while after the unit shuts down from up in the house at the air handler?. A TXV will "slam shut" when the compressor suction stops (most residential valves still have a small equalizing orifice inside the valve).

Creating a "Pump down" or just a "shut down" configuration by installing a solenoid valve in the liquid line will correct this. However, a hard start kit may be needed if the compressor doesn't have a start capacitor as the compressor must start against the head pressure of the refrigerant caused by the elevated AHU.

Excessive refrigerant charge (due to system design): The amount of refrigerant in a system must be kept to a minimum. Arbitrarily installing over sized lines may cause this. These flooding conditions are more prone in over sized refrigerant circuits.

No crankcase heater in a scroll compressor (or reciprocal compressor where slugging is occurring): Mfgs think the scroll is tuff and doesn't need an accumulator, start capacitor or crank heater. Refrigerant has an infinity for oil and during shut down it will migrate to the crankcase of the compressor. At start up the refrigerant (and the oil) are sucked up through the compressor. It makes one hell of a noise! Look for a compressor in a cooler location than the AHU (like the AHU in a 200 degree attic space).

Installing an accumulator in an A/C that doesn't have one will help with a flooding situation.

The HVAC Tech should be able to identify this stuff.

Last edited by dandersen; 7/13/07 at 7:21 AM..
Reply With Quote
  #8  
Old 7/13/07, 8:48 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: grinding noise on startup

I looked it up, a LSV, liquid line solenoid (not check valve) is needed for lines longer than 50 feet or 20 ft vertical rise. (The manual had 10 ft printed but the engineer told me it was a misprint, 20 ft. is correct.)

LSV goes between filter drier and indoor coil on a Bryant heat pump and as close as possible to the filter drier.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 7/13/07, 9:09 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: grinding noise on startup

Quote:
Originally Posted by bking
I looked it up, a LSV, liquid line solenoid (not check valve) is needed for lines longer than 50 feet or 20 ft vertical rise. (The manual had 10 ft printed but the engineer told me it was a misprint, 20 ft. is correct.)

LSV goes between filter drier and indoor coil on a Bryant heat pump and as close as possible to the filter drier.
Now you are making sense to me with the exception that I have always installed a LSV if required just prior to the entry of the A-coil box.
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buzzing noise from panel cbrands Electrical Inspections 6 5/30/07 1:00 PM
Sewage water drain noise dnasser Plumbing Inspections 3 3/30/07 7:51 AM
Noise from Meters?? mlong Electrical Inspections 9 2/3/07 8:08 PM
Water heater noise JL1 Plumbing Inspections 10 10/30/06 10:38 PM
Heat Pump Noise dduffy Inspecting HVAC Systems 2 8/13/06 12:46 AM


All times are GMT -4. The time now is 11:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts