Default Gurgling in Vent

Fellow Inspectors,

New construction, two zone system. The basement unit is a condensing furnace, with concentric vent exiting front bsmt. wall about 30-35 feet from unit. All visible vent pipes were pitched toward furnace. While doing the exterior, I heard a gurgling sound coming from the vent. My suspicion is somewhere along the run, water (condensation) is trapping the exhaust, then enough pressure is created and the vent gasses pass through the water and the sound is created. There was water draining from the unit into the sump as you would expect. Has anyone seen / heard this before?

I did write it up. And of course the attic furnace was not operational, so I will be returning to do another final walkthru.

Anatol
Reply With Quote
  #2  
Old 12/13/06, 9:00 PM
David J. Moran David J. Moran is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Clarkston, MI
Posts: 30
Default Re: Gurgling in Vent

All I can think of is that it may possibly have construction debris in the vent pipes causing the water gurgling through as you described.



David J. Moran
DJM Home Inspections, LLC
Clarkston, MI 48346
Reply With Quote
  #3  
Old 12/22/06, 2:20 AM
Jeremy Tucker Jeremy Tucker is offline
New User
 
Join Date: Dec 2006
Location: Spruce Grove, Alberta, Canada
Posts: 7
Please Note: Jeremy Tucker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gurgling in Vent

The "gurgling" as you describe it is almost always caused by a clogged or partially clogged condensate line or Internal componant of the condensate drain system. If you could list the Make and model number of the furnace, it might help me with the problem. Best step though would be to get the client to have a qualified tech. have a closer look into the furnace to ensure it isnt the beginnings of a larger issue. I dont exactly agree with David's above posting. 99% of the time if any one of the vents (intake or exhaust) are plugged or blocked, the furnace will fail to run or lock out due to the air prooving switches failing to close (blocked exhaust) or the rollout saftey switch opening due to lack of combustion air (blocked Intake)

Last edited by Jeremy Tucker; 12/22/06 at 2:24 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 4 10/12/07 6:38 PM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM


All times are GMT -4. The time now is 3:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts