Default Has anyone seen this type of vent material?

Has anyone ever seen this type of vent material? It was off of a gas furnace installed in 1993.
All the joints were loose, and Im not sure if you can tell but thats smoke from by smoke pen getting blown by exhaust leaking throught the fitting.
I have never seen this type of vent piping, it wasn't very sturdy either, it would flex if you squeezed on it.
Attached Thumbnails
has-anyone-seen-type-vent-material-label.jpg   has-anyone-seen-type-vent-material-piping-cond.jpg   has-anyone-seen-type-vent-material-warning.jpg  
Reply With Quote
  #2  
Old 2/28/07, 10:49 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Has anyone seen this type of vent material?

The rest of the pictures.
Attached Thumbnails
has-anyone-seen-type-vent-material-sloppy.jpg   has-anyone-seen-type-vent-material-smoke.jpg  
Reply With Quote
  #3  
Old 2/28/07, 10:49 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,091
Default Re: Has anyone seen this type of vent material?

I have never seen it , but it looks cool.
Reply With Quote
  #4  
Old 2/28/07, 10:56 PM
bbenjamin bbenjamin is offline
New User
 
Join Date: Feb 2007
Location: Round O, SC
Posts: 45
Please Note: bbenjamin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Has anyone seen this type of vent material?

This is the early form of the popular single wall and double wall b-vent that is currently made by Hart and Cooley back then ("1998") it was called plexvent. This link should help as well: http://www.cpsc.gov/cpscpub/prerel/prhtml06/06022.html
Reply With Quote
  #5  
Old 2/28/07, 10:58 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Has anyone seen this type of vent material?

Yup, thanks, just finished looking it up.
Reply With Quote
  #6  
Old 3/1/07, 10:03 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Has anyone seen this type of vent material?

Did you check on re-calls?
The gray pipe like this has been re-called.
Reply With Quote
  #7  
Old 3/1/07, 8:46 PM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Has anyone seen this type of vent material?

I remember reading about a plexivent recall, might want to do some research..



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #8  
Old 3/1/07, 9:17 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Has anyone seen this type of vent material?

According to Carson-Dunlop the plex-vent pipe was banned in Canada due to cracking and joint failure. Maybe the Canadians can chime in on this.
Reply With Quote
  #9  
Old 3/1/07, 9:19 PM
Matt Berman Matt Berman is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Exclamation Re: Has anyone seen this type of vent material?

Main reason for recall was softening of pipe and break down of glue at joints causing some piping systems to fall apart.Matt Berman
Reply With Quote
  #10  
Old 3/1/07, 9:24 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Has anyone seen this type of vent material?

CPSC recommends that every home should have at least one CO alarm that meets the requirements of the most recent Underwriters Laboratories (UL) 2034 standard or International Approval Services 6-96 standard.

Recall Program to Replace Vent Pipes

Consumers should also have the vent pipes on their heating systems inspected. In 1998, virtually the entire furnace and boiler industry together with the manufacturers of high-temperature plastic vent (HTPV) pipes joined with CPSC to announce a vent pipe recall program. The program's purpose is to replace, free of charge, an estimated 250,000 HTPV pipe systems attached to gas or propane furnaces or boilers in consumers' homes. The HTPV pipes could crack or separate at the joints and leak CO.

Consumers can check the vent pipes attached to their natural gas or propane furnaces or boilers to determine if they are part of this recall. They can be identified as follows: the vent pipes are plastic; the vent pipes are colored gray or black; and the vent pipes have the names "Plexvent®," "Plexvent®II" or "Ultravent®" stamped on the vent pipe or printed on stickers placed on pieces used to connect the vent pipes together. Consumers should also check the location of these vent pipes. For furnaces, only HTPV systems that have vent pipes that go through the sidewalls of structures (horizontal systems) are subject to this program. For boilers, all HTPV systems are subject to this program. Other plastic vent pipes, such as white PVC or CPVC, are not involved in this program.

After checking the vent pipes, consumers should call the recall hotline toll-free at (800) 758-3688 Monday through Friday from 7 am to 6 pm CST, to verify that their appliance venting systems are subject to this program. Consumers with eligible systems will receive new, professionally installed venting systems free of charge. Additionally, consumers who already have replaced their HTPV pipe systems may be eligible for reimbursement for some or all of the replacement costs.
Reply With Quote
  #11  
Old 3/8/07, 9:56 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Has anyone seen this type of vent material?

Thanks for the links guys!
Inspected a house yesterday with this pipe on one of the original HVAC systems.
I had a business card with the recall information numbers on it that I haven't had to use it for quite some time and I think I'll have trouble finding it.
Reply With Quote
  #12  
Old 3/8/07, 11:47 AM
jrabanus jrabanus is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Dayton, IN
Posts: 44
Default Re: Has anyone seen this type of vent material?

What is a B- Vent?
Reply With Quote
  #13  
Old 3/9/07, 3:30 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Has anyone seen this type of vent material?

http://www.duravent.com/catalogs/bve...bout_bvent.htm

Don't you know how to use "Google"?????
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM
Help with identifying vent material mthomas2 Inspecting HVAC Systems 3 1/1/07 1:10 AM
Type BW Vent jpope Inspecting HVAC Systems 14 5/9/06 12:38 PM


All times are GMT -4. The time now is 12:52 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts