Default Have not seen this before

From today's inspection. 2 story residence, built in 1997, both the Master bath and Hallway bath exhaust vent hoses terminate into the attic floor structure. As you can see, hose is foamed in place, the only exterior vent ports are the dryer and microwave. New one on me, can someone explain?

Thanks
Attached Thumbnails
have-not-seen-before-bath-vent-003.jpg   have-not-seen-before-bath-vent-004.jpg  



Andrew MacDonald
MacDonaldPropertyInspections.com
InsightThermalDiagnostics.com

ITC/FLIR Certified Building Science Thermographer
ITC/FLIR Certified Level 1 Thermographer


Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/2/10, 6:34 PM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 364
Default Re: Have not seen this before

Check to see if it has a central fan unit down in the furnace room. Quite common in our area. Usually its piped in with solid tin ducting though? It typically vents out the side of the home down around the sill plate.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #3  
Old 2/2/10, 6:35 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,527
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Have not seen this before

Quote:
Originally Posted by amacdonald View Post
From today's inspection. 2 story residence, built in 1997, both the Master bath and Hallway bath exhaust vent hoses terminate into the attic floor structure. As you can see, hose is foamed in place, the only exterior vent ports are the dryer and microwave. New one on me, can someone explain?

Thanks
The foam may have been for airsealing purposes or possibly just to hold the hose in place.(They don't use screws and brackets / metal strapping there??)

Of course, the bath fans must go to the exterior. (and not just out into the eaves with perforated soffit but fully to the exterior through a vent hood.)
Reply With Quote
  #4  
Old 2/2/10, 7:44 PM
Larry J. Michael Larry J. Michael is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Greensboro, N. C.
Posts: 305
Default Re: Have not seen this before

Should be to the exterior.



Greensboro Home Inspector
Providing home inspections in Greensboro, High Point, Burlington and the surrounding areas.
greensboro-home-inspector.html

Raleigh Home Inspector
Home inspections in Raleigh, Durham, Cary, Chapel Hill, Apex and surrounding areas.
Raleigh-home-inspection.html

Home Spectors
Home Spectors provides home inspections in Greensboro, Winston-Salem, High Point, Burlington, Durham, and surrounding areas.

Reply With Quote
  #5  
Old 2/2/10, 9:28 PM
Andrew MacDonald's Avatar
Andrew MacDonald Andrew MacDonald is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Elgin, IL
Posts: 181
Default Re: Have not seen this before

I think you are missing my point. I realize the foam was there to hold the hose in place and to provide a barrier. I realize they need to be exhausted to the exterior. Can anyone explain the building principal of running the hoses into the interior cavity of the home with NO means of exit and how could this EVER be an acceptable practice. That is my point.



Andrew MacDonald
MacDonaldPropertyInspections.com
InsightThermalDiagnostics.com

ITC/FLIR Certified Building Science Thermographer
ITC/FLIR Certified Level 1 Thermographer


Reply With Quote
  #6  
Old 2/2/10, 10:10 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,527
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Have not seen this before

Quote:
Originally Posted by amacdonald View Post
I think you are missing my point. I realize the foam was there to hold the hose in place and to provide a barrier. I realize they need to be exhausted to the exterior. Can anyone explain the building principal of running the hoses into the interior cavity of the home with NO means of exit and how could this EVER be an acceptable practice. That is my point.
Thought the flex duct was coming up from the wall and into the insulation on the attic floor.

Then Darrell's post #2 probably hit it right on....or were they planning on some central exhaust fan that never got installed?

Last edited by Brian A. MacNeish; 2/3/10 at 2:24 AM..
Reply With Quote
  #7  
Old 2/2/10, 10:25 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,412
Send a message via Yahoo to jfunderburk
Default Re: Have not seen this before

The duct is undoubtedly going to the soffit.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 2/5/10, 2:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,441
Default Re: Have not seen this before

Quote:
Originally Posted by amacdonald View Post
Can anyone explain the building principal of running the hoses into the interior cavity of the home with NO means of exit and how could this EVER be an acceptable practice. That is my point.
I don't think it can be explained, because I don't believe it is an acceptable practice.

I would also be incline to believe that this was a "homeowner" installation, rather than part of the original build.

I would comment in the report that "the vent terminations were not visible and should be verified as venting to the exterior of the residence, or proper venting should be established by a qualified contractor."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 2/5/10, 2:05 PM
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 3,275
Default Re: Have not seen this before

My guess is with Joe. Just turn on the fan and listen for it outside.
Reply With Quote
  #10  
Old 2/8/10, 7:55 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,982
Default Re: Have not seen this before

Common around here. Stupid install. BTW: The bathroom exhaust pipe should be insulated.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #11  
Old 2/9/10, 5:06 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,644
Default Re: Have not seen this before

This is what I typically see that happens when you vent an exhaust fan out an soffit vent. The one pictured may have even missed the soffit opening.

There are a few problems that I see with installing out a soffit.

1) reduced insulation
2) Stained sheathing

It make more sense to vent towards a exhaust roof vent and not an intake roof vent like a soffit.

I do have an illustration that states it can be vented out a soffit. See attached
Attached Thumbnails
have-not-seen-before-153910-022.jpg   have-not-seen-before-bathroom_vent_wall_cap.jpg  

Last edited by dmacy; 2/9/10 at 5:10 PM..
Reply With Quote
  #12  
Old 2/9/10, 7:51 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,412
Send a message via Yahoo to jfunderburk
Default Re: Have not seen this before

Quote:
Originally Posted by dmacy View Post
There are a few problems that I see with installing out a soffit.

1) reduced insulation
2) Stained sheathing

It make more sense to vent towards a exhaust roof vent and not an intake roof vent like a soffit.
I disagree for this reason: anywhere you penetrate your roof, you are more likely to have a leak. Punching holes in my roof would not be an option. My personal preference would be to vent to a soffit using an approved soffit vent (there would be no stained sheathing in that case). The insulation loss is negligible.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 2/9/10, 7:59 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,412
Send a message via Yahoo to jfunderburk
Default Re: Have not seen this before

Time for another Global Warming summit!



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/9/10, 8:07 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,644
Default Re: Have not seen this before

Quote:
Originally Posted by jfunderburk View Post
I disagree for this reason: anywhere you penetrate your roof, you are more likely to have a leak. Punching holes in my roof would not be an option. My personal preference would be to vent to a soffit using an approved soffit vent (there would be no stained sheathing in that case). The insulation loss is negligible.
I did not say punch a hole in the roof, in most cause a vent opening is already there. I stated direct towards an exhaust roof vent like a ridge or roof top.

I disagree with your disagreement.
Reply With Quote
  #15  
Old 2/9/10, 8:36 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,412
Send a message via Yahoo to jfunderburk
Default Re: Have not seen this before

Your illustration showed a dedicated roof bathroom vent. I misunderstood your position. Sorry.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 9:08 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts