I'm looking for feedback on any requirements regarding the discharge end and intake of pvc pipes at the exterior.

Do either require a screen? Are there any requirements regarding a tee or an elbow, etc. Also, I find several HE furnaces where there is no pipe connected to the intake. The furnace is using the basement air. Any thoughts on this?

Thank you in advance for your response.

Kevin
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/14/11, 7:50 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: HE intake & Exhaust

I only tell my clients that it is a good idea to have a screen on them to prevent nesting during the summer.
Yes you can take air from the basement.
When I see this design I tell them about the intake for air and never put anything on top, I also mention that it is safer to bring in the air from outside and explain why.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 12/14/11, 3:56 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HE intake & Exhaust

Quote:
Originally Posted by kgoff View Post
I'm looking for feedback on any requirements regarding the discharge end and intake of pvc pipes at the exterior.

Do either require a screen? Are there any requirements regarding a tee or an elbow, etc. Also, I find several HE furnaces where there is no pipe connected to the intake. The furnace is using the basement air. Any thoughts on this?

Thank you in advance for your response.

Kevin
Going to depend on what your local AHJ requires on intake most areas do not require a screen on intake but common sense prevails in a area with varmints.
If intake and exhaust penetrate the roof together the intake should have a 180 degree fitting to prevent intake drawing exhaust. The exhaust does not require a fitting because it has a drain hose connected within the furnace cabinet



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 12/14/11, 4:39 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: HE intake & Exhaust

No screen required just a good practice for low exterior. None for the roof penetration.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #5  
Old 12/14/11, 5:02 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HE intake & Exhaust

Quote:
Originally Posted by kwood View Post
No screen required just a good practice for low exterior. None for the roof penetration.
We have squirrels here that like to stuff pecans in any pipe opening on the roof that they can find. Once found a 3 inch plumbing vent on the roof blocked with pecans



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 12/14/11, 5:29 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: HE intake & Exhaust

Cool I have never run into this. I have found bird nests at the junctions on vent pipes. I have found nests for Hornets and Wasps also but never any Pecan nuts. LOL



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #7  
Old 12/14/11, 7:12 PM
Kevin R. Goff Kevin R. Goff is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Holt, MI
Posts: 98
Default Re: HE intake & Exhaust

Thank you for the feedback.

Kevin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
The Importance of Bathroom and Kitchen Fans mkyriacou Interior Inspections 35 6/4/10 5:27 PM
Way More Intake To Supplement Minimal Exhaust Ventilation? Ed Fako Exterior Inspections 1 12/19/08 6:07 PM
Intake vent dmacy Inspecting HVAC Systems 8 1/3/07 8:24 AM


All times are GMT -4. The time now is 11:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts