Old 2/17/08, 4:30 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Heat?

What kind of test could be preformed, when a home owner says that the Master bedroom really doesn't warm up to a comfortable level?
This bedroom is the farthest away from the heat source, 80,000btu, 3000 sf house. There are 3 heat registers in the bedroom.

This is a warranty inspection, 11 month.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #2  
Old 2/17/08, 5:00 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat?

Quote:
Originally Posted by nbhi
What kind of test could be preformed, when a home owner says that the Master bedroom really doesn't warm up to a comfortable level?
This bedroom is the farthest away from the heat source, 80,000btu, 3000 sf house. There are 3 heat registers in the bedroom.

This is a warranty inspection, 11 month.
This problem is way too common!!!

Have walls and attic been checked for insulation?

Is the heat source at one end of the house and the bedroom at the other? If so, it's a bad design decision to begin with!!! But It could have been corrected/improved by oversizing ducts running to the room a bit, sealing the duct joints, and insulating those ducts to conserve heat.

Check heating system plans to ensure that designed duct sizes were used.

Check/re-balance air flows to rooms. Ensure that the dampers/registers to the bedroom are wide open. Damper down airflows to the rooms closest to the source; this forces more warm air to the other rooms and may not affect comfort in these closer rooms. Keep doing this to see if airflow and heat supply to the bedroom increases significantly. Do not shut off any airflows!!


More technical:

-Calculate heat loss for the room at outdoor design temperatures for the area (this should have been done by the designer/installer of the heating system and may be available from them)

-Again check installation against design.

-Check airflows and temps using an air balancing technician. He will use a flow hood or velometer to get air velocities and then calculate flows for each register. Then using the air temps it can be calculated how much heat is getting to the room.

Last edited by Brian A. MacNeish; 2/19/08 at 9:34 AM..
Reply With Quote
  #3  
Old 2/19/08, 9:10 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Heat?

Quote:
Originally Posted by nbhi
What kind of test could be preformed, when a home owner says that the Master bedroom really doesn't warm up to a comfortable level?
This bedroom is the farthest away from the heat source, 80,000btu, 3000 sf house. There are 3 heat registers in the bedroom.

This is a warranty inspection, 11 month.
My first red flag I have a problem with that size furnace on a 3K house blower motor and blower wheel does not have the capability of moving the proper CFM regardless of the insulation.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 2/19/08, 9:45 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Quote:
Originally Posted by cbottger
My first red flag I have a problem with that size furnace on a 3K house blower motor and blower wheel does not have the capability of moving the proper CFM regardless of the insulation.
I concur.

80,000 BTU's for 3,000 sq. feet? Are you sure the BTU's are 80,000?

http://www.hvacopcost.com/equipsize.html

Last edited by dvalley; 2/19/08 at 9:48 AM..
Reply With Quote
  #5  
Old 2/19/08, 9:48 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat?

Quote:
Originally Posted by cbottger
My first red flag I have a problem with that size furnace on a 3K house blower motor and blower wheel does not have the capability of moving the proper CFM regardless of the insulation.
I thought that at first also but only one room has the problem.

Some of today's better built homes with highre insulation levels, good airtightness, Low "E"/Argon gas fill windows with "warm edge" spacers will have design heat losses down in this range or lower.

It would be interesting to find out how long the furnace is running on the coldest days of the year. If it's only running 30-35 minutes/hr, then there's still lots of capacity to heat that room but the duct design has been botched or there's been a bad installation.

ps: Just checked the local yearly degree days- approx 5000-5200- not too severe. I'm living in 7400 DD or so and might consider that furnace to be a bit small for that size of house here. Couldn't easily find the design low temp for the area....which would, along with the heat loss characteristics of the home, really determine the furnace size.

Last edited by Brian A. MacNeish; 2/19/08 at 10:17 AM..
Reply With Quote
  #6  
Old 2/19/08, 11:24 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Heat?

Quote:
Originally Posted by nbhi
What kind of test could be preformed, when a home owner says that the Master bedroom really doesn't warm up to a comfortable level?
This bedroom is the farthest away from the heat source, 80,000btu, 3000 sf house. There are 3 heat registers in the bedroom.

This is a warranty inspection, 11 month.
I've got a similar problem in my home. Only I've got 120,000 BTU's and am right over the furnace... Our BR only gets warm if we leave the door open...Any guesses? Yep, no cold air return.

80,000 BTU for 3000 sf is pretty small, but I would think it would just run all the time.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #7  
Old 2/19/08, 12:19 PM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 605
Default Re: Heat?

This may be way to obvious but when I get the same question the first thing I do is check my thermometer to see that the temp is coming out of the vent in question. 100-110 degrees (thats what I usually see here) and then make sure all them are the same or are close to the same.
If that one is not then I would go to the crawl space and check the ducting to see if there is debris in the duct work. You would be surprised how I often I find this to be the case, 2x4's, and misc wood debris not to mention water in the ducting . I would say that 1 out of 20 homes will have standing water (usually new construction ). As far as the previous posts I agree this is just something I check for as well. Good luck.



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #8  
Old 2/19/08, 4:17 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Heat?

If the furnace blower is not properly sized it will not build static pressure within the duct to provide proper CFM at the most remote register I generally tried to have between 300 and 400 CFM on a residential unit at each register preferably at the 400 level. If you have an undersized blower the air just looses itself within the duct. Air flow is just like water flow it takes the path of least resistance



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 2/19/08, 6:18 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Quote:
Originally Posted by cbottger
If the furnace blower is not properly sized it will not build static pressure within the duct to provide proper CFM at the most remote register I generally tried to have between 300 and 400 CFM on a residential unit at each register preferably at the 400 level. If you have an undersized blower the air just looses itself within the duct. Air flow is just like water flow it takes the path of least resistance
Charley,

It would be nice if they had a smaller measurement tool to check CFM's.
Reply With Quote
  #10  
Old 2/19/08, 6:20 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Quote:
Originally Posted by tfarmer
This may be way to obvious but when I get the same question the first thing I do is check my thermometer to see that the temp is coming out of the vent in question. 100-110 degrees (thats what I usually see here) and then make sure all them are the same or are close to the same.
If that one is not then I would go to the crawl space and check the ducting to see if there is debris in the duct work. You would be surprised how I often I find this to be the case, 2x4's, and misc wood debris not to mention water in the ducting . I would say that 1 out of 20 homes will have standing water (usually new construction ). As far as the previous posts I agree this is just something I check for as well. Good luck.
Troy,

I basically work my temp readings the same way. If a register isn't supplying adequate heat (compared to others on the same level), I'll find the problem in the basement somewhere. Ducts are usually not connected or insulated, kinked, or too long.
Reply With Quote
  #11  
Old 2/19/08, 8:46 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Heat?

Quote:
Originally Posted by dvalley
Charley,

It would be nice if they had a smaller measurement tool to check CFM's.
There is fits in the palm of your hand will try to look it up for you still writing todays junked up house.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 2/19/08, 11:43 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat?

Quote:
Originally Posted by cbottger
There is fits in the palm of your hand will try to look it up for you still writing todays junked up house.
Here's a page with a few vane anemometers. I said velometer (another velocity measuring tool) this AM......been out of the air balancing field for 16 years now!!!

http://www.coleparmer.com/catalog/pr...x.asp?cls=7418
Reply With Quote
  #13  
Old 2/20/08, 1:02 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Heat?

David Professional equipment also has anemometers but a little pricey.

http://www.professionalequipment.com/



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 2/20/08, 1:08 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Heat?

I have one of these somewhere.



http://www.coleparmer.com/catalog/pr...0&lstBool=true


I think alnor makes a smaler one too.
Reply With Quote
  #15  
Old 2/20/08, 7:32 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat?

Quote:
Originally Posted by bkelly2
I have one of these somewhere.



http://www.coleparmer.com/catalog/pr...0&lstBool=true


I think alnor makes a smaler one too.
Brian:
Not too many people would know of Alnor (or Shortridge, for that matter). What background do you have to know of this company?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
efficiency of 15 yr old peerless afrost Inspecting HVAC Systems 11 11/19/07 10:51 AM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 9:17 PM
Heat pump in a 80+ year old masonry house jskrypka Inspecting HVAC Systems 9 11/25/06 11:47 PM
Radiant Heat Transfer rmyers1 Structural Inspections 0 6/1/06 12:21 AM