InterNACHI


Go Back   InterNACHI Inspection Forum > Specific Inspection Topics > Inspecting HVAC Systems

Notices

Inspecting HVAC Systems Topics include heating, venting, and air conditioning inspections.

Reply
 
LinkBack Thread Tools
  #16  
Old 2/20/08, 7:43 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

I just found some great deals HERE.

I'm going to go above and beyond and start to do these tests on HVAC.
Reply With Quote
  #17  
Old 2/20/08, 7:49 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Charley,

If I were to purchase this one, what readings should I be obtaining (approximately) on HVAC registers?
Reply With Quote
  #18  
Old 2/20/08, 8:02 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat?

I bought a whack of equipment through these folks in 1990. They had some of the best prices around then. haven't checked today's prices though.

http://www.davis.com/
Reply With Quote
  #19  
Old 2/20/08, 8:12 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Quote:
Originally Posted by Brian A. MacNeish
I bought a whack of equipment through these folks in 1990. They had some of the best prices around then. haven't checked today's prices though.

http://www.davis.com/
I just did the research for ya. They are not as cheap as the link I posted.
Reply With Quote
  #20  
Old 2/20/08, 8:22 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Heat?

Quote:
Originally Posted by Brian A. MacNeish
Brian:
Not too many people would know of Alnor (or Shortridge, for that matter). What background do you have to know of this company?
Busboy at a Lobster house.
Reply With Quote
  #21  
Old 2/20/08, 8:38 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Heat?

Quote:
Originally Posted by dvalley
Charley,

If I were to purchase this one, what readings should I be obtaining (approximately) on HVAC registers?
If you know what cubic/ft/minute or cubic/liters/min you want it is a simple math problem to convert David.

Lets see what Charley comes up with.
Reply With Quote
  #22  
Old 2/20/08, 8:42 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Quote:
Originally Posted by bkelly2
If you know what cubic/ft/minute or cubic/liters/min you want it is a simple math problem to convert David.

Lets see what Charley comes up with.
He did mention that he like to see his installs at 300-400 CFM's......the meter will not convert for me?
Reply With Quote
  #23  
Old 2/20/08, 8:46 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Heat?

Measure the register.

Say the register measures 1 square foot, and the velocity is 1 foot a minute.

That equals 1 cfm.

Eventually you will have a chart of the normal register sizes you come across with the proper conversions.
Reply With Quote
  #24  
Old 2/20/08, 9:05 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Quote:
Originally Posted by bkelly2
Measure the register.

Say the register measures 1 square foot, and the velocity is 1 foot a minute.

That equals 1 cfm.

Eventually you will have a chart of the normal register sizes you come across with the proper conversions.
Damn, I hate math.
Reply With Quote
  #25  
Old 2/20/08, 9:54 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: Heat?

Quote:
Originally Posted by Brian A. MacNeish
Brian:
Not too many people would know of Alnor (or Shortridge, for that matter). What background do you have to know of this company?
Alnor is the Hvac industry standard test equipment used that brand it seems like a hundred years ago. We had vent hoods with sash type glass doors that were connected to pneumatic/electronic controlled Bladder VAV's that increased or decreased CFM according to the position of the door a OSHA requirement for laboratory use in R&D. These doors were required Preventive maint checks



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #26  
Old 2/20/08, 12:56 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,873
Default Re: Heat?

Quote:
Originally Posted by dvalley
I just found some great deals HERE.

I'm going to go above and beyond and start to do these tests on HVAC.
David let me give you an example of why you don't want to go there. To many variables you will not be able to take an anemometer around to the registers and simply say this is correct or this is wrong. I am sticking my neck out further than I like to do as I normally do not quote Stats and or formulas on this board to many guys take it as chiseled in stone. You Stated you do not like math well if you decide on this path you better get to like it.

If The heated air is furnishing all of the heat for a room, 3 things must be known to be able calculate the air volume.
1. Heat Load
2.Room Temp
3. Duct temp
The heat load must be determined, The room temp is decided by the designer. Normally it is 72 degrees F. dry bulb. The duct air temp is more difficult to decide. If a low duct temp is used large air volumes will be necessary to carry enough heat. If high duct temps are used, the furnace will have to operate with a higher (Stack) temp.

Engineers recommend that a grille Temp be at least 125 degrees and that duct temps be near 140 degrees. The lowest temp needed to obtain these result depend on the duct lengths. Knowing that the specific heat of air is .24 BTU/LB the weight of air needed is found by the specific heat equation

Room heat load = .24 X wt, of air X the temp difference.


To obtain the volume you must first find the volume of one pound of air at the duct temp. This value is obtained from a psychrometric chart.

One pound of air = 17.1 Cu.Ft.



David I have a book with all of these formulas but I think I have made my point don't go there, not a good Idea for the HI, I do not use a meter to check air volume and do not state so in my reports. My statement is generally System appears to be performing or system appears not to be performing. Let the Hvac's make the determination.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #27  
Old 2/20/08, 11:06 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat?

Quote:
Originally Posted by bkelly2
Busboy at a Lobster house.
Obviously not using all your brain/skills at that point in your life!
Reply With Quote
  #28  
Old 2/21/08, 2:10 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Heat?

Quote:
Originally Posted by Brian A. MacNeish
Obviously not using all your brain/skills at that point in your life!
I have been on a Brain Rationing program from an early age, as you may have noticed on other threads, some people have run out.
Reply With Quote
  #29  
Old 2/21/08, 7:46 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Heat?

Quote:
Originally Posted by cbottger
David let me give you an example of why you don't want to go there. To many variables you will not be able to take an anemometer around to the registers and simply say this is correct or this is wrong. I am sticking my neck out further than I like to do as I normally do not quote Stats and or formulas on this board to many guys take it as chiseled in stone. You Stated you do not like math well if you decide on this path you better get to like it.

If The heated air is furnishing all of the heat for a room, 3 things must be known to be able calculate the air volume.
1. Heat Load
2.Room Temp
3. Duct temp
The heat load must be determined, The room temp is decided by the designer. Normally it is 72 degrees F. dry bulb. The duct air temp is more difficult to decide. If a low duct temp is used large air volumes will be necessary to carry enough heat. If high duct temps are used, the furnace will have to operate with a higher (Stack) temp.

Engineers recommend that a grille Temp be at least 125 degrees and that duct temps be near 140 degrees. The lowest temp needed to obtain these result depend on the duct lengths. Knowing that the specific heat of air is .24 BTU/LB the weight of air needed is found by the specific heat equation

Room heat load = .24 X wt, of air X the temp difference.


To obtain the volume you must first find the volume of one pound of air at the duct temp. This value is obtained from a psychrometric chart.

One pound of air = 17.1 Cu.Ft.



David I have a book with all of these formulas but I think I have made my point don't go there, not a good Idea for the HI, I do not use a meter to check air volume and do not state so in my reports. My statement is generally System appears to be performing or system appears not to be performing. Let the Hvac's make the determination.
Charley,

When I seen your numbers, it changed my mind.

Thanks.
Reply With Quote
  #30  
Old 2/21/08, 1:14 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Heat?

Quote:
Originally Posted by dvalley
Charley,When I seen your numbers, it changed my mind.
Good call ... it gets sticky ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
efficiency of 15 yr old peerless afrost Inspecting HVAC Systems 11 11/19/07 10:51 AM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 9:17 PM
Heat pump in a 80+ year old masonry house jskrypka Inspecting HVAC Systems 9 11/25/06 11:47 PM
Radiant Heat Transfer rmyers1 Structural Inspections 0 6/1/06 12:21 AM
Question on my heat pump dbush Inspecting HVAC Systems 7 3/12/06 1:15 AM


All times are GMT -4. The time now is 6:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts