I have a question and can't seem to find what I am looking for.
1800 squere foot home with a 3.5 Ton 12 Seer heat pump. There is only 1 return air vent with a filter. No filter on the air handler in the attic. Where can I find information on the proper supply and return. |
| Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
What do you want to know?
Sizing? "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#3
|
||||
|
||||
|
Please Note:
mivie is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is one return and one filter enough for this system.
|
|
#4
|
||||
|
||||
|
What are the dimensions of the return trunk?
|
|
#5
|
||||
|
||||
|
Please Note:
mivie is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am looking back I believe it was 14 inch
|
|
#6
|
||||
|
||||
|
14" dia. ?
|
|
#7
|
||||
|
||||
|
I don't size A/C ducts.
If there is only one return for multiple floors, simply note it and recommend a return per floor (minimum). A floor with no return will get stale air. If you're adamant on obtaining the proper sizing...This might help a bit Last edited by dvalley; 1/17/10 at 4:02 PM.. |
|
#8
|
|||
|
|||
|
Please Note:
rspermo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Michael,
If you want to learn alot about HVAC sizing in 2 days I recommend taking the National Comfort Institute "Introduction to Air Diagnostics" course. |
|
#9
|
||||
|
||||
|
Please Note:
mivie is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks.
|
|
#10
|
||||
|
||||
|
A 14" duct will do 1800 cfm @ .3 in. wg.
.3 in wg is maxed out. It should be more like .1 in wg. (don't put a filter at the end of it!) That would be an 18 in duct. 3.5 ton Heat Pump = aprox 1,750 cfm Is this one story? If so, one return will work if the house is open inside. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#11
|
||||
|
||||
|
Better be careful before you get into a pissing match with a licensed HVAC company. You may be asked by the seller or buyer to pay the fee for an evaluation of the system after they come out, find nothing wrong with it, and leave a $100 bill behind.
Unless it's obvious, like 1 return on a 2 story home, I stay away from pointing out suspected design defects. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#12
|
||||
|
||||
|
Exactly correct!
That was a closing thought as I hit the post button. Analysis of a system is not a requirement of a home inspector. You need more than a Ductulator to determine the proper sizing. You need a Manometer prove that it's wrong in the first place. Does anyone have these in their toolbox? "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Radiant ceiling heat? | bmargiotti | Inspecting HVAC Systems | 16 | 1/24/12 11:46 AM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 2:26 AM |
| Heat pump in a 80+ year old masonry house | jskrypka | Inspecting HVAC Systems | 9 | 11/25/06 11:47 PM |
| Question on my heat pump | dbush | Inspecting HVAC Systems | 7 | 3/12/06 1:15 AM |
| Heat Pump Check list for inspecting | dmacy | Inspecting HVAC Systems | 21 | 2/1/06 1:56 PM |