Default Heat Pump

I did a early morning inspection today at 7:30 AM. The townhouse had a heat pump installed. The outside temperature was 79 when I tested the system. The cooling side worked well. I got a 15 degree split. The heating side I got less than a 5 degree split. Based on other items I saw no service disconnect, unit unstable and out of level, fins dirty, no secondary drain pan drain plumbed I reccomended further evaluation and repairs. Any ideas on what could cause the problem. It was my understanding on a heat pump if one side worked it was almost a given the other side would as well. Ideas??



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!


www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #2  
Old 7/11/06, 9:42 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Heat Pump

Did you trip the head pressure switch?

Were you testing heat in Aux Heat setting or Heat?

If you are running the Heat Pump heat long enough to take temp splits (which tell you NOTHING, by the way) at 80 degrees, your running it too long.

There may be outdoor t-stats that keep the electric heaters off till it gets real cold out. Not common though.

I would not run a heat pump in heat (emergency or Aux heat is OK) during the summer unless you know what you are doing.
Reply With Quote
  #3  
Old 7/11/06, 10:33 PM
Peter Foxe Smothers's Avatar
Peter Foxe Smothers Peter Foxe Smothers is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Shreveport, LA
Posts: 912
Default Re: Heat Pump

Switch not tripped. Was running it in normal heat mode.
Quote:
temp splits (which tell you NOTHING, by the way)
Enlighten me why temp splits tell me nothing?



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!


www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #4  
Old 7/12/06, 6:06 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Heat Pump

What's a split? Anything to do with cheerleaders?



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #5  
Old 7/12/06, 8:35 AM
away away is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Aledo, TX
Posts: 229
Default Re: Heat Pump

Peter,
I know David will be along to further explain his comment. But the gist is that if you are taking dry bulb temps you can't really get the true pre and post evap coil temps. He has mentioned that a chart is used in conjuction with humidity and temperature to figure it correctly.

Also the temps taken at return and supply registers will be skewed due to heat loss/gain occurring in the ducts, loose ducts, holes, location, etc. These all would have a negative impact. Depending on how you write your report, you may suggest the system is not operating correctly when in fact, it is one or more of the other factors that is the real culprit.

I will disagree somewhat with what he says, it will tell you something, just not very much. I use it to check that air is being cooled/heated and not much else. If it is going in at x degrees and coming out at something less/more then the system is cooling or heating the air. That is how I write it in my report and leave it at that.

I have come across a few houses where the temp difference was only 2-3 degrees. Along with other factors, I used that as a basis to have the systems, including the ducts, fully evaluated/repaired as necessary.

RR,
Temp splits are those workers from staffing agencies that share duties, one works in the morning and one works in the afternoons.



Andrew Way
Keystone Residential Inspection Services PLLC
www.keystoneinspections.com
Reply With Quote
  #6  
Old 7/12/06, 10:02 AM
Peter Foxe Smothers's Avatar
Peter Foxe Smothers Peter Foxe Smothers is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Shreveport, LA
Posts: 912
Default Re: Heat Pump

Quote:
Originally Posted by away
Peter,


I use it to check that air is being cooled/heated and not much else. If it is going in at x degrees and coming out at something less/more then the system is cooling or heating the air. That is how I write it in my report and leave it at that.
Do you no longer check temps? I completely understand that the best way to due it would be cut holes and actually check at the coils. That being a little out of the scope I have resorted to checking the closest duct and behind the filter. I understand all about heat loss/gain from point a to point b and that the splits that I check (and most of the inspectors I personally know check) are a little off, but to say they mean nothing is off as well. Example. 95 degree summer day, 2 degree split, I would say it is safe to saw based on the split something is wrong correct? How would you suggest checking for the functionality of the unit? I not going to cut holes in the duct work, stick gauges on the system etc.



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!


www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #7  
Old 7/12/06, 12:58 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Heat Pump

Quote:
Originally Posted by psmothers
How would you suggest checking for the functionality of the unit?
Here's how I do it.

If the heating system is running, then I'll turn it off and then turn the cooling system on. I continue doing my inspection until someone comes and says, "Can we turn the air conditioning off? It's really cold in here."

If the cooling system is running, then I'll turn it off and then turn the heating system on. I continue doing my inspection until someone comes and says, "Can we turning the heating off? It's really hot in here."

Now on the off chance that everyone moves outside, I'll help them:

Me: "How come y'all moved outside?"
Them: "It's hot in there" or "It's cold in there."
Me: "Oh. Well at least we know the heating system works" or "Oh. Well at least we know the cooling system works."

Now can you see them calling me six months down the road:

Them: "My heater's not working" or "My air conditioning's not working."

I can't.
But if they do:

Me: "Remember the day of the inspection when you complained about it being too hot [or too cold]? Well, it was working then, so I suggest you get a heating and cooling guy out there to see why it's not working now.

Duh.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 7/12/06, 1:07 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Heat Pump

Quote:
Inspect a heat pump like you would a central air conditioning system. Testing in one mode is usually sufficient. However, do not operate air-to-air heat pumps in temperatures below 65 F (18 C) on the cooling cycle and above 55 F (13 C) on the heating cycle. In both conditions the amount of work the heat pump has to do to achieve interior comfort temperatures is not enough to really test the heat pump's ability to perform.
Heat pumps use the existing heat available and transfer it. They are not efficient at certain temperatures.
Reply With Quote
  #9  
Old 7/12/06, 1:20 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Heat Pump

Quote:
Originally Posted by bkelly2
Heat pumps use the existing heat available and transfer it. They are not efficient at certain temperatures.
Well they also use the existing cooling available and transfer it. I've never had a heat pump that is in working order not be efficient at any temperature.

If it is hot outside, then one is using the heat pump in the cooling mode, so one has heat in one place (outside) and cold in another place (inside).

If it is cold outside, then one is using the heat pump in the heating mode, so one has heat in one place (inside) and cold in another place (outside).

In both cases, there is heat and cold, which is what's needed for them work and which is why they work so well in our high desert and mountainous areas where it is 120° during the day and 20° at night.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 7/12/06, 1:37 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Heat Pump

Brian, it's your turn to get into a war of words with Rē and explain how a heat pump will not efficiently heat a dwelling when it's 20° outside and that is when the Aux/Emerg Heat is used to turn on the electric strip heaters or even a gas-fired furnace.
Reply With Quote
  #11  
Old 7/12/06, 1:41 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Heat Pump

Virtually all of the aux/emerg heat connections out here have been disconnected after the energy crisis of 2000-2001, so they're not working. The heat pumps, however, seem to do quite well when I'm out in Julian testing them, heat or cold.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #12  
Old 7/12/06, 1:50 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Heat Pump

Excellent! We should all be so lucky. My experience has been that a heat pump, at least here in the South, begins to lose the capability to efficiently heat somewhere around 28° - 30°. I'm sure wet-bulb temps have a lot to do with it and that balance point value may very well be much lower for your area, I wouldn't know.
Reply With Quote
  #13  
Old 7/12/06, 2:07 PM
lclark's Avatar
lclark lclark is offline
Active Poster
 
Join Date: Jan 2005
Location: Wabash, IN
Posts: 191
Please Note: lclark is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat Pump

Bottom line, If you want heat, you need FIRE.

Now back to testing.

I went to IV Tech for continuing ed a couple months ago. The teacher there told us and showed us how to inspect the heating and cooling system. Along with the visual and running the equipment part of the inspection. Take your thermometer and place it on the suction line just outside the furnace housing. The temp. of the line should be 48 to 52 degrees. If the temp. is above 52 then the unit is low on freon and needs service.
Reply With Quote
  #14  
Old 7/12/06, 4:38 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Heat Pump

Quote:
Originally Posted by mboyett
Brian, it's your turn to get into a war of words with Rē and explain how a heat pump will not efficiently heat a dwelling when it's 20° outside and that is when the Aux/Emerg Heat is used to turn on the electric strip heaters or even a gas-fired furnace.
Michael stole this somewhere, and have found it does not work very well with my wife . But I still get a laugh from it.

" I can explain it to you, but, I can't understand for you."
Reply With Quote
  #15  
Old 7/12/06, 4:44 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Heat Pump

Quote:
Originally Posted by mboyett
Excellent! We should all be so lucky. My experience has been that a heat pump, at least here in the South, begins to lose the capability to efficiently heat somewhere around 28° - 30°. I'm sure wet-bulb temps have a lot to do with it and that balance point value may very well be much lower for your area, I wouldn't know.
I just find that absolutely astonishing.

I don't know of any home that is comfortable at 28° or so, so it just seems to me that a heater otta be able to heat up the place to something a little more comfortable. And, indeed, the heaters I have been inspecting out in the mountains and the snow have been able to do that.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat pump in a 80+ year old masonry house jskrypka Inspecting HVAC Systems 9 11/25/06 10:47 PM
Carrier heat pump fires? lprinzi Inspecting HVAC Systems 3 10/12/06 7:31 PM
Question on my heat pump dbush Inspecting HVAC Systems 7 3/12/06 12:15 AM
Armstrong heat pump -- good or bad? skipswift Inspecting HVAC Systems 3 2/13/06 9:17 PM
Heat Pump Check list for inspecting dmacy Inspecting HVAC Systems 22 2/1/06 12:56 PM