Default Heat Pump moisture

At today's inspection I observed dripping water coming out of the exterior pad mounted unit heat pump.It is suspended up on about 6" legs sitting on the pad.
Is it normal to have water dripping from it.
It seems to me that of water drips from it during the winter, it would build up into a big block of ice & be a problem with heaving of the unit etc.
The outdoor temp was about 40F.
Does the water dripping cease after it gets cold or is this a problem that needs to be fixed?

Roy Drangstveit



Sincerely,
Roy Drangstveit
Minnesota Valley Inspections LLC
Phone- 952-693-1777
Email- roy@mnvinspections.com
Website- www.mnvinspections.com
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/29/12, 6:44 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,794
Default Re: Heat Pump moisture

Its normal it just went through a defrost cycle and that is why its elevated to allow for ice build up



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #3  
Old 11/29/12, 8:10 PM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 3,181
Default Re: Heat Pump moisture

I will also make a strange noise when going in defrost and steam up.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #4  
Old 11/30/12, 10:58 PM
Marc-Andre Beauchemin's Avatar
Marc-Andre Beauchemin Marc-Andre Beauchemin is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: BROSSARD,Quebec Canada, Intl.
Posts: 393
Default Re: Heat Pump moisture

On a timer, for the heat pump to perform well, the heating element will generate heat that will melt iced water on coil in cold weather. When this happens the Heat pump is technically on an air conditionning cycle. When the coil has melted the ice, the reversing valve switches back from the air conditionning phase to the heating phase.



Beauchemin,Marc-Andre, B.A. Huissier (1988-2005), inspecteur immobilier CMI et courtier accrédité OACIQ.
BMAinspection CMI
Service dans les deux langues officielles du Canada.
Brossard based, Greater Montreal region, Quebec province, Canada
interNACHI Home inspector & OACIQ Broker . Proud member of interNACHI with CMI designation.
A Mari Usque ad mare.
http://www.inspectionbma.com
Reply With Quote
  #5  
Old 12/1/12, 3:03 AM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 3,181
Default Re: Heat Pump moisture

Quote:
Originally Posted by mbeauchemin View Post
On a timer, for the heat pump to perform well, the heating element will generate heat that will melt iced water on coil in cold weather. When this happens the Heat pump is technically on an air conditionning cycle. When the coil has melted the ice, the reversing valve switches back from the air conditionning phase to the heating phase.
You got part of it right...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #6  
Old 12/1/12, 11:18 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 7,914
Default Re: Heat Pump moisture

Yup, partly...

The Heat Pump Defrost cycle is probably the most complex operation in the heat pump, so we won't get into it here.

There are several defrost systems: Time -Temperature; Time- Refer Pressure; Time - Air Pressure - Temperature; Time -Air Pressure - Reefer Pressure...

Something starts the cycle and something else stops the process.

Electric heat does not melt the ice. Heaters are downstream to the evap coil.
Heaters prevent a cold blast of air when in defrost. The heat to melt outdoor ice comes from the heat pump's previous cycle.

Quote:
Does the water dripping cease after it gets cold or is this a problem that needs to be fixed?
There is less water, because there is less water vapor in cold air than when it is 40F outside. But it will always drip. As for ice build-up, if ice makes it up to the bottom coil, the unit will stay in defrost longer and melt this ice. It is more of an energy loss problem (not to raise the unit above the ice) than the ice on the coil. Contact with the hot outdoor coil and hot water running off the coil will melt more than it will freeze (unless the defrost cycle is not correct).

So if you see ice build-up into the OD Coil, there is a defrost problem.

If you have a low refrigerant charge, sensor out of calibration etc. this type of thing will result.

If you see stripes of ice on the OD Coil and they do not go away after a defrost, you have a low refrigerant charge (Very Low).



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #7  
Old 12/2/12, 7:19 PM
Kenneth Blair Kenneth Blair is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Jacksons Gap, AL
Posts: 80
Default Re: Heat Pump moisture

Just reading this post and I had a very similar situation the other day. The heat pump is dripping water all the time and the ground around the heat pump is soaked almost a mud hole. Is this much moisture from the unit normal as well. I've just never seen it this bad.
Attached Thumbnails
heat-pump-moisture-brian-cummings-021.jpg  
Reply With Quote
  #8  
Old 12/2/12, 7:21 PM
Kenneth Blair Kenneth Blair is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Jacksons Gap, AL
Posts: 80
Default Re: Heat Pump moisture

Also the temp around here has been in the 50s to 60s around the time of this inspection
Reply With Quote
  #9  
Old 12/2/12, 8:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,794
Default Re: Heat Pump moisture

Quote:
Originally Posted by kblair1 View Post
Just reading this post and I had a very similar situation the other day. The heat pump is dripping water all the time and the ground around the heat pump is soaked almost a mud hole. Is this much moisture from the unit normal as well. I've just never seen it this bad.
That appears a little much I am thinking of one situation where it could cause that much water on the ground and it being if the unit was low on Freon and was icing premature on the exterior condenser/evaporator thus creating a premature defrost cycle could be a possibility thus the extra water. Me thinks it should be checked by a HVAC tech



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #10  
Old 12/3/12, 8:50 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 7,914
Default Re: Heat Pump moisture

I had to turn my heat pump off and use the EM Heat setting because of outdoor air conditions last week.

Fog conditions at near freezing temps froze the OD Coil in minutes and blew cold air till the defrost cycle came around...

Alabama, gulf moisture and heat operation = lots of water.
If you have a lot of water on the ground, there is a lot of water vapor in the air.

A Heat Pump can't "make" water from nothing.

It makes the most water when it is operating correctly.

So, if it is making lots of water, it's working right.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 12/3/12, 9:39 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,794
Default Re: Heat Pump moisture

Quote:
Originally Posted by dandersen View Post
I had to turn my heat pump off and use the EM Heat setting because of outdoor air conditions last week.

Fog conditions at near freezing temps froze the OD Coil in minutes and blew cold air till the defrost cycle came around...

Alabama, gulf moisture and heat operation = lots of water.
If you have a lot of water on the ground, there is a lot of water vapor in the air.

A Heat Pump can't "make" water from nothing.

It makes the most water when it is operating correctly.

So, if it is making lots of water, it's working right.
Gulf coast or not I'm still skeptical that is a lot of water



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #12  
Old 12/3/12, 1:42 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 7,914
Default Re: Heat Pump moisture

where else would it come from ?

When it's 50° and 95% humidity and it touches 40° suction line/compressor we make water. Only other option I can think of. Unless it's not associated with the HVAC.

I think it's just acting like a big outdoor dehumidifier.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #13  
Old 12/3/12, 3:42 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,794
Default Re: Heat Pump moisture

Quote:
Originally Posted by dandersen View Post
where else would it come from ?

When it's 50° and 95% humidity and it touches 40° suction line/compressor we make water. Only other option I can think of. Unless it's not associated with the HVAC.

I think it's just acting like a big outdoor dehumidifier.
Does not matter that its 50 outside if its low on freon the exterior evap is going to freeze in the heat mode then its gona defrost starts short cycling creating more ice and water

How does a A/C unit form ice in 100 degree temp in the summer time



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/3/12, 5:47 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 7,914
Default Re: Heat Pump moisture

Not really.

An under charged HP will not sub-cool the entire surface of the OD Coil and will not produce the same quantity of frost as if it were fully charged. It happens faster, but not as much.

As for the 50F temp, that air has the capacity to hold more grains of moisture per pound of air than colder OA. When it gets into late winter and the OD Temps go down and stay down, this moisture is squashed out of the air. At 17F the unit may never go into a defrost cycle...

Just as in the 1st Law of Thermodynamics, energy can not be created or destroyed (except nuclear). Condensate is about heat energy (about 970 btu/lb water).



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 12/3/12, 11:49 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,794
Default Re: Heat Pump moisture

Quote:
Originally Posted by dandersen View Post
Not really.

An under charged HP will not sub-cool the entire surface of the OD Coil and will not produce the same quantity of frost as if it were fully charged. It happens faster, but not as much.

As for the 50F temp, that air has the capacity to hold more grains of moisture per pound of air than colder OA. When it gets into late winter and the OD Temps go down and stay down, this moisture is squashed out of the air. At 17F the unit may never go into a defrost cycle...

Just as in the 1st Law of Thermodynamics, energy can not be created or destroyed (except nuclear). Condensate is about heat energy (about 970 btu/lb water).
No a low charge will not frost the complete coil but it does frost and depending on The MFG how they iniatate a defrost will and does create short cycle of the reversing valve.

Notice my first statement was a possible cause its hard to trouble shoot from afar



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New HWT design kwood Green Building Inspections 1 11/8/12 3:17 AM
Furnace exhaust too close to heat pump Dale Trach Inspecting HVAC Systems 0 4/26/11 8:24 PM
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM
Heat pump in a 80+ year old masonry house jskrypka Inspecting HVAC Systems 9 11/25/06 10:47 PM

All times are GMT -4. The time now is 9:50 PM.
no new posts