jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Question....
Since a heat pump....when run in the heating mode....is basically a reverse Air Conditioner, does it make sense that the heat differential between return and supply vents should be similar to the differential found when it is run in the cooling mode (15 to 20 degrees)? |
Nope,
I typically find differentials as low as 6-7 degrees on an operational heat pump... Won't see much more usually unless you activate the "emer Ht" - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
If the heat pump is newer, seer 13 and up with variable speed and R410 the supply temp can be as high as 105 deg. with 70 return. 35 deg Diff with no aux heat strips!
I have two of them (bryant/carrier) and the heat strips are programmed to always stay off unless: 1. manually activated with aux heat mode 2. Outside temp less than 35 AND temperature lag of >2 deg. The old crappy heat pumps are a thing of the past. |
There is basically no set right answer with delta T. As the outdoor temperature dips the DT will be lower. Like Bruce said with variable speed machines it’s even tougher to say what is correct. A lot of manufactures will have a chart on the inside cover that can give you an idea. I did have some old charts somewhere that gave you a ballpark answer. I’ll see if I can dig them up out of mothballs.
James R Lilly, CMIA www.lhiservices.com jamesrlilly@lhiservices.com Home and Mold Inspections Radon Testing Based in Parkersburg, WV Serving West Virginia and Ohio |
What about temperature rise on Aux heat with the heat strips running? or a gas aux heat unit?
Foxe Smothers ( Owner / Inspector ) Pelican State Inspection Your Best Choice for Home Inspection in the Shreveport & Bossier City Area! www.PelicanState.Net www.ShreveportHomeInspector.net www.BossierCityHomeInspector.net foxe@pelicanstate.net LSBHI #10399 |
When I took Δ T as a tech I would disable the supp heat at the stat to ensure a true reading.
The best way to check the aux heat is to start with cold ducts so that any residual heat will not cause a false interpretation. Gas aux heat (dual fuel units) will have a higher output. |
So is it common for a newer heat pump unit to have a higher temp rise in HP mode than in Aux heat heat? Saw a newer unit today which in HP mode blew 105 and in Aux blew 92. Outside Temp was in the high 50's.
Basically what I am trying to get across is if you are taking temperatures on a heat pump in the normal mode you should make sure that the electric heat strips are not activated also because some times they are if improperly wired and the best way to determine this is with a amp meter on the strips. When I am operating the the emergency heat mode I use the amp meter anyway to determine if all of the strips are operating. Does this make sense. |
Even if wired properly the aux strips will come on if the temperature lags a few degrees. (unless a more advanced t-stat is present and programmed to keep the strips off)
Heat pumps will take more time to inspect. |
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Gas or oil furnaces would be a duel system and would be wired in such a way that if the thermostat shuts down the heat pump if 2 nd stage heating is engaged. For temperature rise you would use the information listed on the furnace data plate. |
[quote=Gary Reecher]The electric strips may or may not operate depending upon outdoor temperature and thermostat settings. I have seen some systems wired that only part of the heat strips will energize and the other part is wired with an outdoor thermostat that will only allow it to be energized until outdoor temperatures reach a certain point.
Thats my point if as a HI you are recording HP temperatures you should know what you are recording and you can not tell by just looking at the system or by the wiring. The strips may or may not be on when you take the temperatures. Remove the normal excess panel on the strips and use the amp meter and you will know exactly what you are recording. |
| Radiant ceiling heat? | bmargiotti | Inspecting HVAC Systems | 16 | 1/24/12 11:46 AM |
| Heat pump in a 80+ year old masonry house | jskrypka | Inspecting HVAC Systems | 9 | 11/25/06 11:47 PM |
| temperature rise | dnasser | Inspecting HVAC Systems | 4 | 6/12/06 11:56 AM |
| Question on my heat pump | dbush | Inspecting HVAC Systems | 7 | 3/12/06 1:15 AM |
| Armstrong heat pump -- good or bad? | skipswift | Inspecting HVAC Systems | 3 | 2/13/06 10:17 PM |