Old 10/17/09, 11:37 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Heat pump thermostat

Defect or no defect?

heat-pump-thermostat-101709-045.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #2  
Old 10/18/09, 12:04 AM
Jeffrey Moore Jeffrey Moore is online now
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 110
Default Re: Heat pump thermostat

Not sure I know what you may think is or is not a defect.
Thermostat is not programmable.
Set to heat, fan auto, inside temp 70, requested 68... inside temp is higher than requested so heat should be off.

I must be missing something so obvious its scary but I'm not sure what you are looking at.(been a long day and brain is tired)



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level 1 Thermographer
Mesa, AZ
Reply With Quote
  #3  
Old 10/18/09, 1:04 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Heat pump thermostat

Some small houses use a condensor outside and the heat strips in the airhandler are the only heat source, in that case all the t-stat needs is what you see in the picture.

Also, in some areas you find many heat pumps without the electric strip package installed so the t-stat can be what you see.

The heat strips are considered an accessory by the manufacturer but I think they are needed to prevent very cold air during the defrost cycle. They also are nice to have when the outside unit gets covered up during an ice storm or the temp drops into the single digits.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #4  
Old 10/18/09, 8:33 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,607
Default Re: Heat pump thermostat

Is this a two stage stat? Does the heat pump have an ambient low temp lock out? Would not call it a defect based on the pic.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #5  
Old 10/18/09, 10:48 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Heat pump thermostat

Is this an appropriate thermostat for a heat pump with heat strips? Would a heat pump in SC without heat strips be appropriate, where winter temperatures below 30 are frequent and they may go as low as 15 degrees?



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 10/18/09, 11:21 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Heat pump thermostat

Quote:
Originally Posted by jfunderburk View Post
Is this an appropriate thermostat for a heat pump with heat strips? ?

No, but you have to confirm that it really is a heat pump, many systems use electric strips for the only heat source and that is connected to the regular heat mode switch as shown.

Would a heat pump in SC without heat strips be appropriate, where winter temperatures below 30 are frequent and they may go as low as 15 degrees?

It depends on whether or not the unit uses R410, these systems are much better. I always educate my client, in the summary, about the four purposes of having these strips installed.

Eliminate some of the chill in defrost mode.
Heat source if ice storm covers the unit in ice.
Heat source if compressor quits running.
Additional heat if very cold outside or you need to raise the temperature several degrees quickly.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #7  
Old 10/18/09, 1:28 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 751
Default Re: Heat pump thermostat

Thermostat lacks an emergency heat setting to allow the heat strips to engage without the use of the outside compressor.



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com

Last edited by mhawley; 10/18/09 at 1:29 PM.. Reason: Typo
Reply With Quote
  #8  
Old 10/18/09, 2:06 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Heat pump thermostat

Quote:
Originally Posted by mhawley View Post
Thermostat lacks an emergency heat setting to allow the heat strips to engage without the use of the outside compressor.
possible scenario based on the above......

"Matt, you inspected my house last month and I had a guy come out and install a heat pump t-stat as you said I needed, ($150) the emerg heat still does not work so I had a guy come out and he said there were no strips in there as you reported, it cost me another $250 for the strips and the labor for installation. Please send me a check for $250 asap, and I have an electrician coming to verify the branch circuit size can handle the new heat strips so that could be another $400 if that is also needed, thanks."



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #9  
Old 10/18/09, 3:23 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 751
Default Re: Heat pump thermostat

Bruce,

If it was an inspection I would identify if the unit had electric heat stips or not by amp probing the conductor inside the panel. If the electric heat strips did not engage I would report the following:

The system is a heat pump without the normal electric heat strips that provide a source of auxiliary and emergency heat. The thermostat lacks an emergency heat setting to allow the heat strips to engage without the use of the outside compressor. Heat pumps require auxiliary (heat strips) to provide adequate heat when ambient temperatures reach 40 degrees and below. If the heat strips are present, they did not engage in the "Heat" setting and the system should be further evalauated to determine what repairs are needed.

We have a lot of heat pumps in Fl. If I see a reversing valve and confirm it's a heat pump, I check the unit while it's in heat pump mode, ensure cool air is blowing from the unit and that the suction line is warm. Once the thermostat is cranked up, the electric heat strips engage. I amp probe them to see how many Kilowatts the strips are and get the rating. Then I turn it to the emergency heat setting and make sure the outside unit turns off, then I check my amp probe again to make sure the strips are still on. There are some thermostats that do not have an emergency heat setting and you have to hit the mode buttom and up arrow at the same time.



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #10  
Old 10/18/09, 3:34 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 751
Default Re: Heat pump thermostat

After reading the entire thread,

It would not be a thermostat defect if heat strips are Not present, however the unit should have auxiliary heat stips and I would identify that the units lacks electric heat strips. If the the compressor failed then home would not have a heat source and if the outside temps were below 40 degrees the heat pump may not be aduquate to heat the home.

That's when the EH setting and electric heat strips would come in handy.



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #11  
Old 10/18/09, 4:03 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Heat pump thermostat

Matt,

Sounds like you have a good process for inspecting heat pumps. Many inspectors do not realize the extra effort these take as compared to gas furnaces. We have many in crawlspaces so its not feasible to do the exact same process as yours. I ike to run the eheat mode first while the air in the ducts is cool so that its easier to notice the strips running.

One thing though, I would not state that heat pumps may not be adequate when temps are less than 40. It all depends on how old the unit is, these newer R410 units are awesome. I have two of them that were new in 2001 and they will work fine in the low 20's. I have measured 105 degree air with the electric strips off on a low load day (low 40's). I have my strips programmed to stay off unless very cold outside, they still come on as needed during the defrost cycle.

You have to wonder how many heatpumps out there don't work correctly but are still being operated with only the electric strips for heat. I have never found a client or homeowner who really understood the modes and lights on the heat pump t-stat other than clients who are hvac techs or engineer types.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #12  
Old 10/18/09, 4:25 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Heat pump thermostat

The unit in question was definitely a heat pump. Heil unit. New construction.

heat-pump-thermostat-101709-010.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 10/18/09 at 6:41 PM..
Reply With Quote
  #13  
Old 10/19/09, 1:22 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Heat pump thermostat

Quote:
Originally Posted by bking View Post
Some small houses use a condenser outside and the heat strips in the airhandler are the only heat source, in that case all the t-stat needs is what you see in the picture.
This house was about 2600 SF, 2 stories. Not a "small house".

Quote:
Originally Posted by bking View Post
Also, in some areas you find many heat pumps without the electric strip package installed so the t-stat can be what you see.
After inspection over 1000 homes in NC and SC, about 40% of them heat pumps, I think I've found maybe 2 without heat strips. That's a defect in my view. I've confirmed the need for heat strips in our geographic area with a local HVAC contractor.

Quote:
Originally Posted by bking View Post
The heat strips are considered an accessory by the manufacturer but I think they are needed to prevent very cold air during the defrost cycle. They also are nice to have when the outside unit gets covered up during an ice storm or the temp drops into the single digits.
A necessary accessory.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #14  
Old 10/20/09, 11:32 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Heat pump thermostat

Joe, its good to see that we both agree, as usual.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #15  
Old 10/21/09, 8:58 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: Heat pump thermostat

I suppose it is area specific. My house has a heat pump, and no electric heat strips, and that is somewhat common for this area.

If you're certain it's a heat pump, and it has heat pumps, it needs a "heat pump" thermostat.

Any of you using an amp clamp to make sure that the heat strips are working? I can't tell you how many times I've found one not working.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Heat pump in a 80+ year old masonry house jskrypka HVAC 9 11/25/06 11:47 PM
Carrier heat pump fires? lprinzi HVAC 3 10/12/06 8:31 PM
Question on my heat pump dbush HVAC 7 3/12/06 1:15 AM
Armstrong heat pump -- good or bad? skipswift HVAC 3 2/13/06 10:17 PM


All times are GMT -4. The time now is 2:59 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts