Default Heat Recovery Ventillator

This was a first for me so I need to know if this is standard practice. The kitchen, laundry, bath and master bath bath exhaust fans were actually a timer device which operated the blower which pulls air thru the HRV. Owner stated that a humidity sensor reads the air and if it contains high moisture content, exhausts the moist air out of the home. Otherwise it cycles it thru the return ducts.

Does any of this sound right? I have very limited experience with HRV, but I cannot see cycling momma's burnt dinner smoke thru the return register into the HRV and back into the home?
Reply With Quote
  #2  
Old 7/14/07, 6:40 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat Recovery Ventillator

If all of the returns go to HRV and out of the house and not the furnace return should be acceptable. Returns from bathrooms or kitchens going to furnace or air handler returns is not.

Check the Home Ventilation Institute web site on codes. http://www.hvi.org/bcofficials.html
Reply With Quote
  #3  
Old 7/14/07, 7:17 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat Recovery Ventillator

I may be reading this wrong but venting the kitchen exhaust through the HRV (or anything else with a filter)can't be a good idea.
Reply With Quote
  #4  
Old 7/15/07, 12:47 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Heat Recovery Ventillator

Quote:
Originally Posted by kmcmahon
This was a first for me so I need to know if this is standard practice. The kitchen, laundry, bath and master bath bath exhaust fans were actually a timer device which operated the blower which pulls air thru the HRV. Owner stated that a humidity sensor reads the air and if it contains high moisture content, exhausts the moist air out of the home. Otherwise it cycles it thru the return ducts.

Does any of this sound right? I have very limited experience with HRV, but I cannot see cycling momma's burnt dinner smoke thru the return register into the HRV and back into the home?
I am not totally understanding what you are describing here, but I would state bathrooms and kitchens can not be connected to the return system in any form.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 7/15/07, 8:34 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Heat Recovery Ventillator

Quote:
Originally Posted by cbottger
I am not totally understanding what you are describing here, but I would state bathrooms and kitchens can not be connected to the return system in any form.
A good Read ..... Cookie
.http://www.oee.nrcan.gc.ca/Publicati...w=N#components.......



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 7/15/07, 8:39 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Heat Recovery Ventillator

Why would anyone install a bathroom vent into the return side of a furnace.

Sounds like they invented a home made (part-time) humidifier?
Reply With Quote
  #7  
Old 7/15/07, 8:51 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat Recovery Ventillator

Just looked through HVI 929 Installation Manual for Heat Recovery Ventilators. Removing air from the bathrooms and kitchen is just one ducting arrangement. However those returns are connected directly to the HRV which then expels that air outside through the HRV exhaust. The ducting arrangements illustrated do show that outside air can be ducted individually to room locations or centrally to a furnace or air handler return. Fresh outside air from the HRV is the only ducting arrangement to a return is the only configuration shown. Though not shown in the HVI manual individual HRV manufacturers do allow air connection of their HRV to a central return for outgoing and incoming air.

If the bathrooms and kitchen returns do connect to a central furnace or air handler return this is not allowed. If they connect only to the HRV then this arrangement would be allowed as this air would be expelled outdoors.
Reply With Quote
  #8  
Old 7/15/07, 9:18 AM
kmcmahon kmcmahon is offline
Active Poster
 
Join Date: Apr 2004
Location: Stevens Point, WI
Posts: 224
Please Note: kmcmahon is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heat Recovery Ventillator

Thank you everyone.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Waste Heat Recovery System hmcbride Inspecting HVAC Systems 10 5/15/07 12:17 AM
Heat Recovery Ventilators kshepard Inspecting HVAC Systems 4 5/5/07 9:45 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
Heat Recovery Systems Present Potential Fire Hazards Barrie Inspector Canadian Inspectors 1 2/1/07 3:13 AM