This was a first for me so I need to know if this is standard practice. The kitchen, laundry, bath and master bath bath exhaust fans were actually a timer device which operated the blower which pulls air thru the HRV. Owner stated that a humidity sensor reads the air and if it contains high moisture content, exhausts the moist air out of the home. Otherwise it cycles it thru the return ducts.
Does any of this sound right? I have very limited experience with HRV, but I cannot see cycling momma's burnt dinner smoke thru the return register into the HRV and back into the home? |
|
#2
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
If all of the returns go to HRV and out of the house and not the furnace return should be acceptable. Returns from bathrooms or kitchens going to furnace or air handler returns is not.
Check the Home Ventilation Institute web site on codes. http://www.hvi.org/bcofficials.html |
|
#3
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I may be reading this wrong but venting the kitchen exhaust through the HRV (or anything else with a filter)can't be a good idea.
|
|
#4
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#5
|
||||
|
||||
|
Quote:
.http://www.oee.nrcan.gc.ca/Publicati...w=N#components....... Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#6
|
||||
|
||||
|
Why would anyone install a bathroom vent into the return side of a furnace.
Sounds like they invented a home made (part-time) humidifier? |
|
#7
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just looked through HVI 929 Installation Manual for Heat Recovery Ventilators. Removing air from the bathrooms and kitchen is just one ducting arrangement. However those returns are connected directly to the HRV which then expels that air outside through the HRV exhaust. The ducting arrangements illustrated do show that outside air can be ducted individually to room locations or centrally to a furnace or air handler return. Fresh outside air from the HRV is the only ducting arrangement to a return is the only configuration shown. Though not shown in the HVI manual individual HRV manufacturers do allow air connection of their HRV to a central return for outgoing and incoming air.
If the bathrooms and kitchen returns do connect to a central furnace or air handler return this is not allowed. If they connect only to the HRV then this arrangement would be allowed as this air would be expelled outdoors. |
|
#8
|
|||
|
|||
|
Please Note:
kmcmahon is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank you everyone.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Waste Heat Recovery System | hmcbride | Inspecting HVAC Systems | 10 | 5/15/07 12:17 AM |
| Heat Recovery Ventilators | kshepard | Inspecting HVAC Systems | 4 | 5/5/07 9:45 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 8:17 PM |
| Heat Recovery Systems Present Potential Fire Hazards | Barrie Inspector | Canadian Inspectors | 1 | 2/1/07 3:13 AM |
| Radiant Heat Transfer | rmyers1 | Structural Inspections | 0 | 5/31/06 11:21 PM |