Heatilator Gas Fireplace (Direct Vent) installed in a Basement (sub grade application).

Vent pipe terminates at the rear foundation wall of the home.

After Construction, a Deck was installed......

Thoughts....Suggestions...?



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:33 PM..
Reply With Quote
  #2  
Old 12/3/07, 10:37 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heatilator Gas Fireplace

12 inch clearence under porch or deck.Hmm.
see page 13
http://content.hearthnhome.com/downl...s/4002-079.pdf
Reply With Quote
  #3  
Old 12/3/07, 10:45 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Heatilator Gas Fireplace

How is the measurement calculated (12 inch clearance) Framing or Decking.?

Suggestions for repair to improve clearances?



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:33 PM..
Reply With Quote
  #4  
Old 12/3/07, 11:20 PM
dharris dharris is offline
Active Poster
 
Join Date: Nov 2003
Posts: 1,392
Please Note: dharris is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heatilator Gas Fireplace

Quote:
Originally Posted by jhagarty
How is the measurement calculated (12 inch clearance) Framing or Decking.?

Suggestions for repair to improve clearances?
Let the wood burn back 12" then put the fire out.
Reply With Quote
  #5  
Old 12/3/07, 11:33 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heatilator Gas Fireplace

Deck , is same as a porch and the diagram shows you measure from the top
of that V frame.
Also you need 12 inches below.
What is that below the direct vent as it almost looks like a window well.
I know it is not , but what is it?
Reply With Quote
  #6  
Old 12/3/07, 11:34 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,058
Default Re: Heatilator Gas Fireplace

Quote:
Originally Posted by jhagarty
Heatilator Gas Fireplace (Direct Vent) installed in a Basement (sub grade application).

Vent pipe terminates at the rear foundation wall of the home.

After Construction, a Deck was installed......

Thoughts....Suggestions...?
Joe,

If it was me doing the report I would say it is a poor installation method, you have the heat melting snow, ice build-up when turned off, drying the wood decking, and if someone happens to be sitting outside when it's being used on top of the make-shift flue, well you know the rest of the story.

I cannot see the whole picture as to what could be done to divert the termination point, but I think I would recommend a qualified fireplace/chimney specialist take a look at it to take the burden off my *****.

Simply a poor set-up no matter how you look at it in my opinion.

Good Catch...!!
Reply With Quote
  #7  
Old 12/3/07, 11:41 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Heatilator Gas Fireplace

Quote:
Originally Posted by relliott

What is that below the direct vent as it almost looks like a window well.
I know it is not , but what is it?
Vent Well?

The well beneath was originally installed (prior to deck installation) to provide the minimum required distance below the vent termination.

Overall installation is Poor. The question now is how to repair it without removing the Porch / Deck.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #8  
Old 12/3/07, 11:49 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Heatilator Gas Fireplace

just a thought
heatilator-gas-fireplace-heatalater.jpg

Last edited by relliott; 12/3/07 at 11:53 PM..
Reply With Quote
  #9  
Old 12/4/07, 8:48 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Heatilator Gas Fireplace

post this at the deck elevation




ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #10  
Old 12/5/07, 7:24 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Heatilator Gas Fireplace

First, I'd advise your Client to ask that the seller call the AHJ to determine if this installation was inspected, and if it was, I'd make sure that AHJ inspector has been fired or retired, and no longer near the construction industry.

Secondly, I'd call the General Contractor who performed the work, and ask him what his plans were to correct the problem.

Thirdly, if that is an A/C unit next to the vent, under the same decking, that's going to be a major problem too.

Fourthly, whoever came up with the grate/footwarmer vent through the wood decking should probably get a pat on the back for ingenuity, right after someone gives him a swift kick in the *****.

More importantly, don't stop looking around for other problems, because this could be a sign of other things to come.

IMHO...Good Luck
Reply With Quote
  #11  
Old 12/5/07, 7:51 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Heatilator Gas Fireplace

Quote:
Originally Posted by gveal

First, I'd advise your Client to ask that the seller call the AHJ to determine if this installation was inspected, and if it was, I'd make sure that AHJ inspector has been fired or retired, and no longer near the construction industry.

Secondly, I'd call the General Contractor who performed the work, and ask him what his plans were to correct the problem.

Thirdly, if that is an A/C unit next to the vent, under the same decking, that's going to be a major problem too.

Fourthly, whoever came up with the grate/footwarmer vent through the wood decking should probably get a pat on the back for ingenuity, right after someone gives him a swift kick in the *****.

More importantly, don't stop looking around for other problems, because this could be a sign of other things to come.

IMHO...Good Luck
Unfortunately Pennsylvania did not have Building Codes when this was installed. (prior to 2005)

Permits and Inspections also were not required.

Contractors (GC, Carpenter, Electrician, HVAC, etc....) were, at time of construction, and continue to be Unlicensed Occupations in the State of PA.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #12  
Old 12/6/07, 1:21 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Heatilator Gas Fireplace

We still have spot areas (Counties) within Ga. that still have no Insp./Permit requirements, but business licensing on a county level is everywhere, and the State has, and enforces the latest IRC/IBC 2006, if called in to inspect. Although Building Contractors aren't licenced yet, they will be as of 1/1/08. Our industry will probably be licensed by the end of 2008, if what I have heard comes true.
Reply With Quote
  #13  
Old 12/6/07, 1:58 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,759
Default Re: Heatilator Gas Fireplace

Greg already caught the AC condenser unit under the deck. That is real stoopid. Good luck trying to do any work on it or better yet, change out a compressor, not to mention the extremely pi$$ poor efficiency due to restricted air flow. Must be kind of loud sitting on the deck in the summer.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
The Rumford Fireplace: Safety vs. Efficiency mbryan Interior Inspections 2 4/28/08 5:38 PM
Gas fireplace bkelly1 Inspecting HVAC Systems 1 4/12/07 11:36 PM
Brick fireplace chimney salexander General Inspection Discussion 6 9/23/06 5:37 PM


All times are GMT -4. The time now is 2:04 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts