Is anyone familiar with what I believe they called a baffle system? I have one furnace and one a/c unit and 3 thermostats, one for each floor. depending on which thermostat orders heat or a/c, the baffle system opens those ducts and closes the others. My problem is that when it blows it is quite loud at certain ceiling registers and I don't know if that is the norm. Any ideas or areas to conduct my search would be greatly appreciated. Thank you.
Reply With Quote
  #2  
Old 12/27/06, 3:18 PM
James A. King James A. King is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
James A. King has had a little positive feedback
Default Re: hvac baffle system

Is the sound always loud at the same registers, or does it depend upon which thermostat(s) are calling for air? I can imagine that there might be a whistling sound when one or more dampers (baffles) is closed, as some air will escape around the damper, be forced to a high velocity, and make the sound. If you are able to determine which damper is the main offender, you can then attempt corrective action, which might include adjusting the damper to close tighter, and verifying that the other dampers are opening fully. If those don't work, then adjusting the "closed" position of the dampers to be not so tightly closed might help. Those are the only actions that come to mind. Other inspectors may have some additional suggestions.

Jim King
Reply With Quote
  #3  
Old 12/27/06, 3:23 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
cbellefontaine has had a little positive feedback
Send a message via MSN to cbellefontaine
Default Re: hvac baffle system

In different parts of the country, it is referred to by different names. Here in Chicago, we refer to them as motorized dampers. As far as the noise; the blower fan does make noise, but shouldn't be annoying. Older units were loud. Depending on the type of noise, it could mean anything from a loose belt to damaged bearings. I may also just be dirty. You have to decide for yourself if you want to upgrade to a quieter fan.

I hope this helps. If not feel free to add additional information or give me a call.



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #4  
Old 12/27/06, 3:52 PM
Fran Walters Fran Walters is offline
New User
 
Join Date: Dec 2006
Posts: 5
Fran Walters hasn't had much positive or negative feedback
Please Note: Fran Walters is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hvac baffle system

it appears that the air/heat is being blown very forcefully and creates the noise coming through the registers. hope this helps describe what is taking place and gives you a better idea of what could be the fix. thank you.
Reply With Quote
  #5  
Old 12/27/06, 4:01 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
cbellefontaine has had a little positive feedback
Send a message via MSN to cbellefontaine
Default Re: hvac baffle system

Some fans have adjustable blower speeds. You should consult an HVAC contractor to make these changes. If they kicked up the pressure because a remote location is not getting enough air flow, then you have to decide which is more important. Noise or heat.



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #6  
Old 12/27/06, 5:59 PM
Fran Walters Fran Walters is offline
New User
 
Join Date: Dec 2006
Posts: 5
Fran Walters hasn't had much positive or negative feedback
Please Note: Fran Walters is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hvac baffle system

that would make sense. it is a 1 year new 3 story townhouse and the installers might have tweaked the fan speed to reach all areas. we'll have that looked into. thank you very much.

in keeping with that thought, the 3rd floor does not seem to have a very long blowing cycle and it is nearest the a/c unit. if it is blowing harder than it should, that area would get the brunt of the faster speed, heating or cooling faster. i believe i read that the unit should run a longer period of time as opposed to a shorter period in order to remove moisture from the air. would this be true?

and, if it is true, could moisture have built up in the ductwork causing a problem there? the townhouse comes out of warranty soon and i'd like to make sure it doesn't have any major flaws. thank you again.
Reply With Quote
  #7  
Old 12/27/06, 6:55 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
cbellefontaine has had a little positive feedback
Send a message via MSN to cbellefontaine
Default Re: hvac baffle system

I am assuming you are a homeowner. If this is the case, the best advice that I can give you is to have this property professionally inspected. You will most likely have a home inspector come through the property when you go to sell the home. That person will most likely find defects that you are not aware of. Since your warranty will be expired, you will be the one who will bear the consequences. You can find someone close to you at the top left of this page.

I would be happy to talk to you on the phone. You can reach me at the number below.



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #8  
Old 12/27/06, 7:13 PM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 347
Darrell B. Hadler is generally well trusted
Default Re: hvac baffle system

In Canada, it's known as ZONE heating.
There is also supposed to be another damper which is usually located somewhere on the plenum that lets excess pressure out when only one zone is calling for heat/AC. This usually has an adjustment lever on it for this purpose. Kind of a balancing damper if you will. I don't know the technical name for it or the specs on setting it though.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #9  
Old 12/28/06, 3:23 AM
Robert J. OConnor, P.E.'s Avatar
Robert J. OConnor, P.E. Robert J. OConnor, P.E. is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 739
Robert J. OConnor, P.E. is often very helpful Robert J. OConnor, P.E. is often very helpful
Default Re: hvac baffle system

From the description it seems you have what is called a "zone dampered system" around my neck of the woods, which is much less desirable to having separate equipment/zones for each area for exactly the reasons/problems you described (and others).

Talk to a local HVAC specialist to see what can be done.

JMO



Robert O'Connor, PE
Eagle Engineering & Inspections
Adjunct Professor
NACHI Education Committee
www.reporthost.com/eagleengineering

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #10  
Old 1/3/07, 2:33 AM
rsummers rsummers is offline
New User
 
Join Date: Oct 2003
Location: Chico, CA
Posts: 19
rsummers hasn't had much positive or negative feedback
Please Note: rsummers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hvac baffle system

Sounds like a poorly designed Zone System. They should have sized the smallest zone to handle 100% of available air or installed a bypass damper so the extra air the system delivers is dumped back in to the return. The best way to install these types of systems are with 2 stage heating and cooling equipment with variable drive motors sizing the smallest zone to handle 100% of 1st stage air flow. You can try changing the supply air grills with a one way adjustable grill such as the shoemaker 950 series thats the one we use on all zone systems.
Reply With Quote
  #11  
Old 1/3/07, 10:49 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,832
David A. Andersen .
Default Re: hvac baffle system

As posted by Darrell and Rolland, the barometric (bypass damper) is not properly installed/sized.

It is also likely that the system design is wrong.

Generally you will not find a residential zoned system that can handle just one zone at a time. The HVAC unit must be too small to handle all 3 zones in the worse case weather. The controller can be adjusted in many cases to allow 50% bypass rather than 100% when one zone is operating ect... This takes a VERY Qualified person to set up. So go for the gold and have a TAB Tech correct it.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues 293 2/10/08 2:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
Emergency Lighting (commercial) mcyr Electrical 24 6/10/06 11:06 AM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues 0 2/14/06 4:38 AM


All times are GMT -4. The time now is 12:41 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics