#1
|
|||
|
|||
|
I inspected a home today that is three level. Three split system hvac for main floor 3 ton 36,btu LRA. 24.3 with manufacture max breaker 30amp. Basement unit 18,000 BTU 2 1/2 ton RLA 11.9 Manufacture max breaker 20 amp and the upstairs unit 24,000 btu cooling output with RLA. 17.9 max breaker by manufacture 20amp max. This is straight from manufacture plate. At main panel each unit on Double pole 30amp. The home was 2005 built. No problem with hvac company. The manufacture plate should be your guide. What is the problem with double pole 30amp when 20amp is required.
|
| Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
The ones requiring a 20 Amp max are "overfused", and the appliances are not protected by the breaker, and could result in a fire or worse.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#3
|
|||
|
|||
|
I have been to 5 different HVAC company that do new installations. Even my brother in law who is a lic.Electricain said they see this alot. I write it up every time because over current can cause damage to electrical componets. These areas need address by a Lic. Electricain or Hvac compamy. You know What? I have had them send me references were this is allowed. It is not by codes NEC. I'm Certified Through ICC. I do not know what to tell these people some times. They always try to make us look stupid! When the client pay's for another opinion and get this answer they are confused on what to do. Why don't they learn their JOB!!!!!!!!!!!!!!!!!!!
|
|
#4
|
||||
|
||||
|
Quote:
Hard to damage components when they are already broke! You make it sound like big breakers push more current down the wire!?? I'm sure you didn't mean that. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#5
|
|||
|
|||
|
Curtis -
When I walk into a house I AM the home inspection guru - NOT the repair bozo. If the data tag says MAXIMUM size to be a 20 AMP fuse or Breaker and whats in the panel box is a 30 AMP / Its wrong. After writing it up I COULD CARE LESS if they correct it or don't. Not my problem. I DON'T CARE what a dumb *** repair bozo says about it. IF a buyer calls me and says the ELECTRICIAN says they see it ALL the time, I may simply say: " I see people doing 50 mph in a 40 mph speed zone all the time too / SO what - Its Wrong". I hope your repair bozo is better at croquet than he is at HVAC, because he doesn't seem to know squat about HVAC. Then MOVE ON ............................ |
|
#6
|
||||
|
||||
|
Quote:
House 2 Home LLC 503-602-1420 HomePros@House2HomeLLC.ORG Protecting Peace of Mind One House at a Time IAC2 Certified IR Certified A favorite place on Google Maps |
|
#7
|
||||
|
||||
|
There are conditions where this would be acceptable. For example if the sticker on the case says 20 AMP, but the guts have been replaced with a unit requiring a 40 amp breaker. In this case the sticker would be "wrong" for the appliance being used. While this scenario is highly unlikely, it is possible.
I'd write it up as being wrong, and tell my client that if the sellers HVAC tech says it's ok, get it in writing from the HVAC company on their letterhead or don't accept their hearsay. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#8
|
|||
|
|||
|
Mark,
You are kidding... aren't you? |
|
#9
|
||||
|
||||
|
No, why? As I said, there are conditions where it would be acceptable, as in additional or replacement components needing a higher breaker. However as an HI, you would write it up as being wrong, and let someone else take the heat for saying it's okay. 99.99% of the time (if not greater) it will be wrong. It's just not a universal statement.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| What is your HVAC procedure? | sstowe | Inspecting HVAC Systems | 66 | 5/28/09 1:48 PM |
| Elementary HVAC 101 | cbottger | Inspecting HVAC Systems | 75 | 4/7/09 11:48 PM |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 72 | 3/12/08 12:19 AM |
| Access to Electrical Panel in Ontario by HVAC Contractors | Nalliah Thayabharan | Canadian Inspectors | 8 | 5/21/07 4:01 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 9:17 PM |