Cool Hvac Breakers oversized ASAP Answer?

I inspected a home today that is three level. Three split system hvac for main floor 3 ton 36,btu LRA. 24.3 with manufacture max breaker 30amp. Basement unit 18,000 BTU 2 1/2 ton RLA 11.9 Manufacture max breaker 20 amp and the upstairs unit 24,000 btu cooling output with RLA. 17.9 max breaker by manufacture 20amp max. This is straight from manufacture plate. At main panel each unit on Double pole 30amp. The home was 2005 built. No problem with hvac company. The manufacture plate should be your guide. What is the problem with double pole 30amp when 20amp is required.
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/23/10, 6:43 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Hvac Breakers oversized ASAP Answer?

The ones requiring a 20 Amp max are "overfused", and the appliances are not protected by the breaker, and could result in a fire or worse.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 2/23/10, 6:58 PM
Curtis Petty Curtis Petty is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: fayetteville, ga
Posts: 68
Default Re: Hvac Breakers oversized ASAP Answer?

I have been to 5 different HVAC company that do new installations. Even my brother in law who is a lic.Electricain said they see this alot. I write it up every time because over current can cause damage to electrical componets. These areas need address by a Lic. Electricain or Hvac compamy. You know What? I have had them send me references were this is allowed. It is not by codes NEC. I'm Certified Through ICC. I do not know what to tell these people some times. They always try to make us look stupid! When the client pay's for another opinion and get this answer they are confused on what to do. Why don't they learn their JOB!!!!!!!!!!!!!!!!!!!
Reply With Quote
  #4  
Old 2/23/10, 8:33 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Hvac Breakers oversized ASAP Answer?

Quote:
over current can cause damage to electrical componets.
Actually it is the components that have failed that result in the breaker tripping.

Hard to damage components when they are already broke!

You make it sound like big breakers push more current down the wire!??
I'm sure you didn't mean that.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 2/24/10, 1:07 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,586
Default Re: Hvac Breakers oversized ASAP Answer?

Curtis -

When I walk into a house I AM the home inspection guru - NOT the repair bozo. If the data tag says MAXIMUM size to be a 20 AMP fuse or Breaker and whats in the panel box is a 30 AMP / Its wrong.

After writing it up I COULD CARE LESS if they correct it or don't. Not my problem. I DON'T CARE what a dumb *** repair bozo says about it.

IF a buyer calls me and says the ELECTRICIAN says they see it ALL the time, I may simply say: " I see people doing 50 mph in a 40 mph speed zone all the time too / SO what - Its Wrong".

I hope your repair bozo is better at croquet than he is at HVAC, because he doesn't seem to know squat about HVAC.

Then MOVE ON ............................
Reply With Quote
  #6  
Old 2/24/10, 1:26 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Hvac Breakers oversized ASAP Answer?

Quote:
Originally Posted by dbowers View Post
Curtis -

When I walk into a house I AM the home inspection guru - NOT the repair bozo. If the data tag says MAXIMUM size to be a 20 AMP fuse or Breaker and whats in the panel box is a 30 AMP / Its wrong.

After writing it up I COULD CARE LESS if they correct it or don't. Not my problem. I DON'T CARE what a dumb *** repair bozo says about it.

IF a buyer calls me and says the ELECTRICIAN says they see it ALL the time, I may simply say: " I see people doing 50 mph in a 40 mph speed zone all the time too / SO what - Its Wrong".

I hope your repair bozo is better at croquet than he is at HVAC, because he doesn't seem to know squat about HVAC.

Then MOVE ON ............................
Way to go david i agree.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #7  
Old 2/24/10, 1:26 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Hvac Breakers oversized ASAP Answer?

There are conditions where this would be acceptable. For example if the sticker on the case says 20 AMP, but the guts have been replaced with a unit requiring a 40 amp breaker. In this case the sticker would be "wrong" for the appliance being used. While this scenario is highly unlikely, it is possible.

I'd write it up as being wrong, and tell my client that if the sellers HVAC tech says it's ok, get it in writing from the HVAC company on their letterhead or don't accept their hearsay.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 3/1/10, 9:41 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Hvac Breakers oversized ASAP Answer?

Mark,

You are kidding... aren't you?
Reply With Quote
  #9  
Old 3/1/10, 10:11 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Hvac Breakers oversized ASAP Answer?

Quote:
Originally Posted by gveal View Post
Mark,

You are kidding... aren't you?
No, why? As I said, there are conditions where it would be acceptable, as in additional or replacement components needing a higher breaker. However as an HI, you would write it up as being wrong, and let someone else take the heat for saying it's okay. 99.99% of the time (if not greater) it will be wrong. It's just not a universal statement.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is your HVAC procedure? sstowe Inspecting HVAC Systems 66 5/28/09 1:48 PM
Elementary HVAC 101 cbottger Inspecting HVAC Systems 75 4/7/09 11:48 PM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 8 5/21/07 4:01 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 9:17 PM


All times are GMT -4. The time now is 1:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts