Default HVAC Design - Air Return

Have a Carrier gas furnace, model CNRVP3014ATAABAA, that is supplying
a two story home (800 down / 1200 up) with respective air return sizes of 14x14 and 20x20.

The owner complained of excessive noise from the air return......which I agree is loud.
The unit is housed in the laundry romm on the second floor with the return going directly to an adjacent wall that separates the laundry room and hallway.

The 20x20 air return is the only one upstairs that has to take care of 3 bedrooms plus the addtional rooms up there.

While I am no HVAC contractor it seems like this was a bad design.

Comments appreciated.

Jeff

Reply With Quote
Find an InterNACHI certified New Jersey Home Inspector (and anywhere else in North America)
  #2  
Old 9/13/08, 10:24 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,281
Charley L. Bottger .
Default Re: HVAC Design - Air Return

Jeff in the 40 years I spent working in that field lack of and or inadequate return air was the most common flaw that I observed on any system. When trying to explain return air I like to use the bottle approach one can only blow so much air into a bottle and when the bottle get full it starts to whistle and makes noise. Increase the size of the return or get some ear muffs



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 9/13/08, 11:21 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 166
Jeffery L. Haynes is often very helpful Jeffery L. Haynes is often very helpful
Default Re: HVAC Design - Air Return

I have heard of 200 sq. in. per ton for air returns, however I also know that many "rule of thumb formulas" used in the construction industry are just that.........you take a home that has 1200 sq. and its very open, then yes I would a 20x20 is adequate when strategically placed, however you take that same area and make a maze out of it, add interior doors that typically have a half inch gap...... than no matter what size your return is, it is still over taxed.

Trying to convey that point to the builder, especially a track builder, so that he will act is challenging; while I am not out to accomodate my client, I believe she does have a valid point regardless as to what the minimum code requirements state.


Jeff
Reply With Quote
  #4  
Old 9/13/08, 1:04 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Design - Air Return

Quote:
Originally Posted by jhaynes View Post
I have heard of 200 sq. in. per ton for air returns, however I also know that many "rule of thumb formulas" used in the construction industry are just that.........you take a home that has 1200 sq. and its very open, then yes I would a 20x20 is adequate when strategically placed, however you take that same area and make a maze out of it, add interior doors that typically have a half inch gap...... than no matter what size your return is, it is still over taxed.

Jeff
Haven't heard the 200 sq in/ton before but have seen this many times.....400 cfm /ton. That unit appears to have a 2.5 ton coil installed and therefore would need 1000 cfm. Decent (unlined) duct design for 1000 cfm would require 160 sq in (8"X20") on supply and 196 sq in on return (8"X24").

From your #'s, the returns are oversized (576 sq in) and the noise being heard must be fan or vibration; should not be velocity noises from too small ducts. There may not be any duct liner (sound absorbing insulation) installed in the returns, allowing the fan sounds to be carried easily to the hall/rooms.....especially if the return ducts are short.
Reply With Quote
  #5  
Old 9/13/08, 1:26 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 2,962
Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute
Default Re: HVAC Design - Air Return

If I'm understanding Jeff's post the return grill is a wall mount 20x20 into an approx. 3 5/8 stud bay, less than adequate, imo



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #6  
Old 9/14/08, 12:26 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,281
Charley L. Bottger .
Default Re: HVAC Design - Air Return

Quote:
Originally Posted by badair View Post
If I'm understanding Jeff's post the return grill is a wall mount 20x20 into an approx. 3 5/8 stud bay, less than adequate, imo

That would be correct the surface of the return air grill means absolutely nothing, Its what's behind the grill that has to be caluclated. you could have the whole wall covered with a grill and connect it to a 6 inch duct and wait for the noise



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #7  
Old 9/14/08, 8:34 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Design - Air Return

Quote:
Originally Posted by badair View Post
If I'm understanding Jeff's post the return grill is a wall mount 20x20 into an approx. 3 5/8 stud bay, less than adequate, imo
"a two story home (800 down / 1200 up) with respective air return sizes of 14x14 and 20x20"

When he didn't say "air return grilles or registers", I assumed he meant the return duct sizes.

Reply With Quote
  #8  
Old 9/14/08, 9:08 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 2,962
Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute
Default Re: HVAC Design - Air Return

Quote:
Originally Posted by Brian A. MacNeish View Post
"a two story home (800 down / 1200 up) with respective air return sizes of 14x14 and 20x20"

When he didn't say "air return grilles or registers", I assumed he meant the return duct sizes.
That's why I posted my dimensions for clarification from him and you gurus...we taught you better than too *****-u-me anything out of this motely crew...



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #9  
Old 9/15/08, 7:37 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 166
Jeffery L. Haynes is often very helpful Jeffery L. Haynes is often very helpful
Default Re: HVAC Design - Air Return

Barry,

You are correct, the unit is inside the laundry room and butts up against the wall (2x4 studs).. The grill is 20x20, at least the filter is that size, is located in the adjacent hallway near the ceiling. There really isn't any duct work per se other then the length it takes to run into the wall which is going to be maybe 5 - 6 inches at best.

I can not attest to any duct liner but even if I could, I don't think the noise is going to depreciate appreciably.

I will be speaking to the homeowner this evening about the write up's as well as the builder's obligation which is probably ZERO in regards to the unit.

Again, we are talking a large (national) track builder whose sole goal is to make money by simply cutting back on quality as well as quantity.

I was more curious about the design of the system but it appears that while there are obviously better designs, he does not and did not adhere to same.

Jeff
Reply With Quote
  #10  
Old 9/16/08, 8:52 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Design - Air Return

Quote:
Originally Posted by jhaynes View Post
Barry,

You are correct, the unit is inside the laundry room and butts up against the wall (2x4 studs).. The grill is 20x20, at least the filter is that size, is located in the adjacent hallway near the ceiling.

There really isn't any duct work per se other then the length it takes to run into the wall which is going to be maybe 5 - 6 inches at best.

I can not attest to any duct liner but even if I could, I don't think the noise is going to depreciate appreciably.

Jeff
Sounds like it's not too small returns but......

20X20" is a standard size for many plenum take-offs from the HP/AC unit. That short of a return (even if oversized and with duct liner installed) has not a chance in hell of dampening fan noise!!!
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM


All times are GMT -4. The time now is 4:55 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics