I am not able to identify the 2 orange conductors in the A/C disconnect box. Anybody know why they would be there? The condenser is about 10 years old.
Michael Merino Merino's Home Inspection & Education Inc. "Not just an Inspection, an Education"SM Phone/Fax 708~535~6057
|
| Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Anyone?
Michael Merino Merino's Home Inspection & Education Inc. "Not just an Inspection, an Education"SM Phone/Fax 708~535~6057
|
|
#3
|
|||
|
|||
|
Please Note:
sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Probably low voltage stat wires.
|
|
#4
|
||||
|
||||
|
yes they would be the low voltage from the Stat to the compressor contactor and not allowed to be in the same conduit with the 220 volt in most areas
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#5
|
|||
|
|||
|
Stat wires not allowed to run in conduit in IL.
|
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
It's a common misconception that LV Class 2 conductors can be run with power conductors in the same raceway if their insulation value is rated for the highest voltage within the raceway. Looks like those are 600 volt insulated condcutors. The NEC prohibits them in the same raceway because those control wires are rated as a Class 2 circuit which must be run separately.
This installation does not fit any of the permissions listed in this (B) through (I): Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Inspecting Furnaces. Please proof this new inspection article. | gromicko | Inspecting HVAC Systems | 4 | 9/15/09 9:54 PM |
| what to report on old hvac equipment | bking | Inspecting HVAC Systems | 8 | 7/6/08 4:10 PM |
| Access to Electrical Panel in Ontario by HVAC Contractors | Nalliah Thayabharan | Canadian Inspectors | 10 | 5/21/07 3:01 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 8:17 PM |
| HVAC Disconnect | kgore | Inspecting HVAC Systems | 11 | 7/11/06 6:58 PM |