I recently inspected a gas fired furnace located in a remodeled basement with no electrical disconnect and the circuit breaker box was in the garage. Is an electrical disconnect required to be at the furnace? It is my understanding that all furnaces must have a disconnect within sight of the unit.
|
|
#2
|
|||
|
|||
|
That's the way it's noted in Electrical Code Check under "Appliances". It's supposed to be a fused disconnect unless the furnace is thermally protected. The NEC code reference number is 422.33A
|
|
#3
|
||||
|
||||
|
Quote:
Roy Cooke sr |
|
#4
|
||||
|
||||
|
There must be a switch or breaker within sight of the equipment (to protect service technicians that shut off power), or it can be the feeder breaker in a remotely located panel if the breaker can be locked in the off position (i.e. a "breaker lock" is installed).
If you have a copy of the IRC look at Table E4001.5 which has a handy summary table of required "Disconnecting Means" for appliances and equipment. A lot easier read for HI's than sifting through numerous NEC sections ... Note that while most furnaces have blower motors that are more than 1/8 HP (usually 1/3 to 3/4 HP), they usually have internal overload protection so a disconnect switch that is also fused isn't usually required. In fact I can't remember one unit that I inspected or installed in a house that required a fused disconnect switch (commercial is a different story). JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#5
|
||||
|
||||
|
I've been seeing some like this lately--no dead front cover. However, it appears manufactured this way and you'd have to work real hard to contact a live part. What do ya'll think about it? "Servicable?"
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
||||
|
||||
|
Joe, I have not seen one of those, it looks nice, no problem with it here.
|
|
#7
|
||||
|
||||
|
Wow. We just plug them in and, if necessary, unplug them.
NACHI 2005 U.S. Member of the Year
|
|
#8
|
||||
|
||||
|
Quote:
I prefer the disconnects with a GFCI service receptacle (as a receptacle is required within 25' of outdoor units since the 2002 NEC). It's a little more expensive and requires a 3-wire + ground feeder, instead of the usual 2-wire + ground feeder. But it's usually less than installing a separate service receptacle. JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#9
|
||||
|
||||
|
Are we talking about furnaces or cooling condensers?
NACHI 2005 U.S. Member of the Year
|
|
#10
|
||||
|
||||
|
Quote:
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#11
|
||||
|
||||
|
Out here we just plug the gas furnaces into the outlet. If we need to work on them, we unplug them. Very simple.
NACHI 2005 U.S. Member of the Year
|
|
#12
|
|||
|
|||
|
Please Note:
ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Don't the margaritas keep you warm???
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Room size requirement for HVAC supply | kweiss | Inspecting HVAC Systems | 3 | 6/9/07 6:58 PM |
| Access to Electrical Panel in Ontario by HVAC Contractors | Nalliah Thayabharan | Canadian Inspectors | 10 | 5/21/07 3:01 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 8:17 PM |
| A/C Disconnect question | rslocum | Inspecting HVAC Systems | 15 | 9/21/06 12:16 AM |
| 100 Amp Meter, 200 Amp Disconnect | jweinberg | Electrical Inspections | 8 | 8/15/06 12:32 PM |