I recently inspected a gas fired furnace located in a remodeled basement with no electrical disconnect and the circuit breaker box was in the garage. Is an electrical disconnect required to be at the furnace? It is my understanding that all furnaces must have a disconnect within sight of the unit.
Reply With Quote
  #2  
Old 7/10/06, 2:51 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: HVAC Disconnect

That's the way it's noted in Electrical Code Check under "Appliances". It's supposed to be a fused disconnect unless the furnace is thermally protected. The NEC code reference number is 422.33A
Reply With Quote
  #3  
Old 7/10/06, 2:55 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,948
Default Re: HVAC Disconnect

Quote:
Originally Posted by kgore
I recently inspected a gas fired furnace located in a remodeled basement with no electrical disconnect and the circuit breaker box was in the garage. Is an electrical disconnect required to be at the furnace? It is my understanding that all furnaces must have a disconnect within sight of the unit.
Correct
Roy Cooke sr
Reply With Quote
  #4  
Old 7/10/06, 7:08 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: HVAC Disconnect

There must be a switch or breaker within sight of the equipment (to protect service technicians that shut off power), or it can be the feeder breaker in a remotely located panel if the breaker can be locked in the off position (i.e. a "breaker lock" is installed).

If you have a copy of the IRC look at Table E4001.5 which has a handy summary table of required "Disconnecting Means" for appliances and equipment. A lot easier read for HI's than sifting through numerous NEC sections ...

Note that while most furnaces have blower motors that are more than 1/8 HP (usually 1/3 to 3/4 HP), they usually have internal overload protection so a disconnect switch that is also fused isn't usually required. In fact I can't remember one unit that I inspected or installed in a house that required a fused disconnect switch (commercial is a different story).

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 7/11/06, 12:16 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: HVAC Disconnect

I've been seeing some like this lately--no dead front cover. However, it appears manufactured this way and you'd have to work real hard to contact a live part. What do ya'll think about it? "Servicable?"

heating-venting-air-conditioning-disconnect-070706-034.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 7/11/06, 1:20 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: HVAC Disconnect

Joe, I have not seen one of those, it looks nice, no problem with it here.
Reply With Quote
  #7  
Old 7/11/06, 1:36 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: HVAC Disconnect

Wow. We just plug them in and, if necessary, unplug them.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 7/11/06, 4:10 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: HVAC Disconnect

Quote:
Originally Posted by jfunderburk
I've been seeing some like this lately--no dead front cover. However, it appears manufactured this way and you'd have to work real hard to contact a live part. What do ya'll think about it? "Servicable?"
Sure ... I think it looks serviceable. Doesn't appear to be any exposed hot lugs or ends of hot wires.

I prefer the disconnects with a GFCI service receptacle (as a receptacle is required within 25' of outdoor units since the 2002 NEC). It's a little more expensive and requires a 3-wire + ground feeder, instead of the usual 2-wire + ground feeder. But it's usually less than installing a separate service receptacle.

JMO & 2-nickels ...
Attached Files
File Type: pdf AC Disconect-Receptacle SQD.pdf (180.8 KB, 386 views)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #9  
Old 7/11/06, 5:37 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: HVAC Disconnect

Are we talking about furnaces or cooling condensers?



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 7/11/06, 6:57 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: HVAC Disconnect

Quote:
Originally Posted by rray
Are we talking about furnaces or cooling condensers?
Both (as well as AC air handlers) require a disconnect switch within sight (or breaker lock) and a service receptacle within 25'.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #11  
Old 7/11/06, 7:48 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: HVAC Disconnect

Out here we just plug the gas furnaces into the outlet. If we need to work on them, we unplug them. Very simple.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #12  
Old 7/11/06, 7:58 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,719
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Disconnect

Don't the margaritas keep you warm???
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Room size requirement for HVAC supply kweiss Inspecting HVAC Systems 3 6/9/07 7:58 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 8 5/21/07 4:01 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 9:17 PM
A/C Disconnect question rslocum Inspecting HVAC Systems 15 9/21/06 1:16 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 1:32 PM


All times are GMT -4. The time now is 9:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts