  #1  
Old 11/6/08, 8:41 PM
Hubert A. Miles Hubert A. Miles is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Johnsonville, SC
Posts: 63
Default HVAC length of pipe from return

I have a situation on an inspection I did today I need some help with. The homeowner stated that the air flow from the registers in some rooms is stronger than others. When I got to the house and went in the attic I discovered multiple problems with the ductwork; crimped piping, improperly installed support straps, branch distribution laying over the return pipe, etc. Overall the system is a mess and could have been arranged better. There are 2 returns going into the attic unit.

My question is in the ductwork from the main ceiling return going into the unit is about 35 ft long. I've never seen one this long before. What generally is the appropriate distance for this? I have attached a photo of the attic.
Attached Thumbnails
heating-venting-air-conditioning-length-pipe-return-gedc0008.jpg  
Reply With Quote
  #2  
Old 11/6/08, 8:54 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: HVAC length of pipe from return

I have no idea. I'm not a system designer. Refer it out if you believe there is a problem.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 11/6/08, 9:28 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC length of pipe from return

You have all kinds of imporper bends in those ducts. Go to the Air Difussion council - they give you the standards for duct installation.
Reply With Quote
  #4  
Old 11/6/08, 9:31 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by lkage View Post
I have no idea. I'm not a system designer. Refer it out if you believe there is a problem.
Like Larry said, get a local HVAC contractor out there to sort it out.
Reply With Quote
  #5  
Old 11/6/08, 10:15 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by bkelly2 View Post
Like Larry said, get a local HVAC contractor out there to sort it out.
Guys there stands the problem local contractor was the one that made the mess to begin with do you really think he is going to say its wrong

No 35 feet is not an excessive run for a return air see them that long all of the time matter of fact I installed a longer return air run than that in my own house this last summer works just great.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 11/6/08, 10:46 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by hmiles View Post
I have a situation on an inspection I did today I need some help with. The homeowner stated that the air flow from the registers in some rooms is stronger than others. When I got to the house and went in the attic I discovered multiple problems with the ductwork; crimped piping, improperly installed support straps, branch distribution laying over the return pipe, etc. Overall the system is a mess and could have been arranged better. There are 2 returns going into the attic unit.

My question is in the ductwork from the main ceiling return going into the unit is about 35 ft long. I've never seen one this long before. What generally is the appropriate distance for this? I have attached a photo of the attic.
Hubert correct me if wrong but are you saying you think the weaker outflow from some registers might be due to the long return?

Just wondering as I do not think it would effect some and not others.

It would just be weaker overall from my understanding.

Did you trace the weaker register ducting from the attic to see if it was bent?
Reply With Quote
  #7  
Old 11/6/08, 11:10 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by relliott View Post
Hubert correct me if wrong but are you saying you think the weaker outflow from some registers might be due to the long return?

Just wondering as I do not think it would effect some and not others.

It would just be weaker overall from my understanding.

Did you trace the weaker register ducting from the attic to see if it was bent?
Bob the problem lyes with the supply trunk not the return just look at it some of the suppy lines are not on a 45 degree angle from the trunk line thay are actually trying to reverse the direction of air flow with the take off branch. The size of the trunk appears to be maybe 14 inch (SWAG) to many take offs on one trunk it will over feed some branches and under feed others



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 11/6/08, 11:17 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by cbottger View Post
Bob the problem lyes with the supply trunk not the return just look at it some of the suppy lines are not on a 45 degree angle from the trunk line thay are actually trying to reverse the direction of air flow with the take off branch. The size of the trunk appears to be maybe 14 inch (SWAG) to many take offs on one trunk it will over feed some branches and under feed others
Thanks Charlie as I noticed the bends ,but was wondering if Hubert was trying to factor the return as part of the problem.

I do not calculate either, but seem to recall (little off subject ) that it is 10 feet added for each bend, correct?

How much of a factor is the blower on the unit.Yes I see what you are saying though.
Reply With Quote
  #9  
Old 11/6/08, 11:22 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by cbottger View Post
Guys there stands the problem local contractor was the one that made the mess to begin with do you really think he is going to say its wrong

No 35 feet is not an excessive run for a return air see them that long all of the time matter of fact I installed a longer return air run than that in my own house this last summer works just great.
Ok then reccomend your client to send pictures to Charley for evaluation over internet with remedy as necessary.
Reply With Quote
  #10  
Old 11/6/08, 11:38 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by bkelly2 View Post
Ok then reccomend your client to send pictures to Charley for evaluation over internet with remedy as necessary.
I just luv it when you get cute I am feeling generous today one of my compitors just started work at Lowes send me all of your pics



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 11/6/08, 11:50 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by relliott View Post
Thanks Charlie as I noticed the bends ,but was wondering if Hubert was trying to factor the return as part of the problem.

I do not calculate either, but seem to recall (little off subject ) that it is 10 feet added for each bend, correct?

How much of a factor is the blower on the unit.Yes I see what you are saying though.
Yes I think he was trying to contribute lack of air flow to the return distance wrong approach on this one. I have made the comment many times that a system can and often is killed by the return air but don't think it is the case here

The size of the blower is very important must move the proper CFM to maintain Duct static pressure don't you mean 10 feet taken away for each bend not added

BED time for this old man hard day tomorrow



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 11/7/08, 12:35 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by cbottger View Post
Yes I think he was trying to contribute lack of air flow to the return distance wrong approach on this one. I have made the comment many times that a system can and often is killed by the return air but don't think it is the case here

The size of the blower is very important must move the proper CFM to maintain Duct static pressure don't you mean 10 feet taken away for each bend not added

BED time for this old man hard day tomorrow
No I meant added , because if you deducted 10 feet for each bend , then bends would be more efficient

Yeah I am reminded of the return above the supply vent in that redneck DIY presentation.
Always gets a laugh when I do the homebuyer seminar..
Reply With Quote
  #13  
Old 11/7/08, 7:11 AM
Hubert A. Miles Hubert A. Miles is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Johnsonville, SC
Posts: 63
Default Re: HVAC length of pipe from return

Thanks for the responses everyone. I used an infrared camera to get a visual picture of the air flow from the registers in each room and then traced each room from the register back to the source. The lines toward the front of the picture had good flow, but the lines closest to the unit with had the bends had significantly less air flow. Some had next to none, as you barely see the register in the infrared photo. I concluded from this that the air was attempting to branch out but the obstructions (bends, crimps, etc) were forcing the air back down the supply line to the other rooms. Generally, the farther away you go with the supply, the lower the air flow, but this was just the opposite. And yes you are correct in that I wanted to know if length of the duct from the return to the unit was part of the problem and if I should cite it as well as a contributing factor to the problem. She had a HVAC tech look at it and he said it should be shorter, but she wanted an independent opinion. And I really did not know, but I had never seen one that long in an attic before. Most HVAC techs install the unit in the middle of the attic close to the return but this one was not done this way. I am siting the location of the unit as undesirable due to the fact you can't get to the backside of the unit.


There is a second return also feeding into the unit from the garage bonus room. It is about 20 to 25 feet long. Is there a maximum length for flex duct here? Is this considered improper?
Reply With Quote
  #14  
Old 11/7/08, 7:25 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC length of pipe from return

Quote:
Originally Posted by relliott View Post
Thanks Charlie as I noticed the bends ,but was wondering if Hubert was trying to factor the return as part of the problem.

I do not calculate either, but seem to recall (little off subject ) that it is 10 feet added for each bend, correct?

How much of a factor is the blower on the unit.Yes I see what you are saying though.
Each 90 degree elbow or bend adds as much resistance to air flow as 10 feet of straight pipe. The term used is "equivalent length". Each boot/transition piece, hood, grille has an "equivalent length" number. e.g. some exhaust hoods with a simple swinging backdraft damper have the resistance or "equivalent length" of 60 feet of smooth straight pipe.

Using spiral round or flex duct adds about double the resistance to airflow as the same size of smooth galvanized pipe. e.g. If you need 6" pipe to supply/exhuast an area properly and you're using a flex duct, increase the diameter by 1" to ensure adequate airflow. In other words, the 7" flex is like using 6" smooth.

Residential duct systems in general are some of the worst designed (non-designed!!) parts of houses. Studies have shown that from 20-40% of the air moving through the air handler/fan, does not get to or from the rooms it was designed for due to duck leaks.
Reply With Quote
  #15  
Old 11/7/08, 7:57 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HVAC length of pipe from return

Can you tell me the diameter of the main trunk line I can see at least 4 take offs on it in the pic how many taps on the supply plenum or was the whole home being fed from one trunk line



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 6:39 PM


All times are GMT -4. The time now is 5:28 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts