Quote:
Originally Posted by cbottger View Post
Guys there stands the problem local contractor was the one that made the mess to begin with do you really think he is going to say its wrong

That is why, whenever I refer something to another professional, I recommend "qualified" professionals.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #17  
Old 11/7/08, 8:22 AM
Hubert A. Miles Hubert A. Miles is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Johnsonville, SC
Posts: 63
Default Re: HVAC length of pipe from return

I'll try to lay out the diagram here. There are 2 return lines coming in. Sorry, but I did not measure them. Then from the unit there are 2 main trunk lines: 1 you see in the above photo and another that runs to the attic on the other side of the vaulted area. The first main trunk line (above) has 9 taps. The second trunk has 8 taps. Here are more photos.





Also, the house is 1816 sq ft and the unit is a 3 ton unit. I feel the system should have been installed with 2 zones, one for this attic and one for the other side.

Last edited by hmiles; 11/7/08 at 8:40 AM..
Reply With Quote
  #18  
Old 11/7/08, 11:24 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: HVAC length of pipe from return

The complaint is about differential airflow.
Is there a comfort issue here? Different amounts of air are required in different parts of the house due to load requirements.

Basically, you probably have a duct system that is not balanced with the appropriate dampers installed.

From what I'm gathering in your post, it appears that there are too many takeoffs to have sufficient air "throw". The more takeoffs you have the lower the volume of air because you have more holes in the duct.

The length of the return should not be an issue if it's properly sized. The static pressure of a return duct must be lower than on the supply side or adverse conditions will exist.

Properly sizing the supply air duct, using the friction loss method will require the Main supply trunk line to be reduced in size as air volume is removed at takeoffs, maintaining static pressure along the entire length of the supply trunk. This design ensures an even static pressure throughout the supply. They can't stop there.

Balancing dampers must be installed in the shorter high volume takeoffs to restrict airflow to increase static pressure for the longer/crooked takeoffs.

These calculations are performed using a ductulator. As you remove CFM at takeoffs, you adjust the design friction pressure per 100 feet of duct to the remaining CFM scale. This indicates the new duct dimensions that the line should be reduced to.

Remember, the HVAC unit is a sucking machine not a blowing machine! It's about removing the air from the house, reconditioning the air to the proper temperature/humidity and putting it back in the right proportion at the right location.
It's not about blowing hot/cold air into a cold/hot room.

Both the supply and return systems must be balanced and properly located.

Also remember that one air duct system cannot be efficient in both heating and cooling modes. It must be designed for one or the other.

The location of your supply and return grills are critical for comfort. If you have the return registers and the supply registers in the ceiling, air stratification will occur and short cycling of heat air will occur at the ceiling resulting in a cold floor (in the heating mode).

What is the actual complaint?




"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 6:39 PM


All times are GMT -4. The time now is 5:28 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts