  #1  
Old 11/25/07, 7:02 PM
Larry King Larry King is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Athens, GA
Posts: 8
Larry King hasn't had much positive or negative feedback
Default HVAC Proper AMPS

If the max amp on heat pump states 30 amp and service man switch is 60 amp, how would you write this up? Over fused and needs to be changed? I know I may be over thinking this but would like any feedback.
Thanks
Reply With Quote
  #2  
Old 11/25/07, 8:41 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: HVAC Proper AMPS

I find many times the breaker at the unit will be 60 amps for what ever reason but the breaker in the main panel will be 30 amps. Nothing wrong with that the 60 amps is simply a disconnect means at the unit. But if both are 60 amps then you do not have proper protection for the unit and I would state it as such.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 11/25/07, 9:53 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 678
Mathew Hawley is often very helpful Mathew Hawley is often very helpful Mathew Hawley is often very helpful
Default Re: HVAC Proper AMPS

Larry,

The breaker in the main panel is the one that should be a 30 amp breaker. If not I would write as:

The AC condensing unit's data plate calls for a maximum fuse size of 30-amps. The unit is currently fused on an 60-amp breaker. This condition voids the manufacturer’s warranty and leaves the system susceptible to damage. Recommend having the necessary repairs made by a licensed electrician prior to the close of escrow.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Electricians Check List pabernathy Electrical 74 12/5/07 7:39 PM
Room size requirement for HVAC supply kweiss HVAC 3 6/9/07 7:58 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 8 5/21/07 4:01 PM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM


All times are GMT -4. The time now is 11:54 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics