Default HVAC in unvented, spray foam insulated attic?

Is there a verdict? pros and cons / effects
of unvented attic, sealed with Icynene spray foam
on HVAC system and ductwork?
[Plan is for 2-story construction, Central Texas
(read: outdoor temps around 100 F, humidity around 40%..) ]
Anybody with experience with such a setup
under these conditions?

How about considerations for "make up" air for HVAC system
for this?
Thanks!
Reply With Quote
  #2  
Old 4/24/07, 10:25 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: HVAC in unvented, spray foam insulated attic?

Quote:
Originally Posted by lfreeze
Is there a verdict? pros and cons / effects
of unvented attic, sealed with Icynene spray foam
on HVAC system and ductwork?
[Plan is for 2-story construction, Central Texas
(read: outdoor temps around 100 F, humidity around 40%..) ]
Anybody with experience with such a setup
under these conditions?

How about considerations for "make up" air for HVAC system
for this?
Thanks!
I would not be a fan of non-vented attics in Tx or Ok. due to moisture considerations. My thinking would be the ducts would have to be extra insulated to compensate for increased heat load.

Your use of the words make up air can be confusing, make up air is normally thought of as infiltration of normal use of external door use. Not to be confused with combustion air normally taken from an attic area. I would have concerns with combustion air on a totally sealed attic if truly sealed.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 4/24/07, 11:15 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: HVAC in unvented, spray foam insulated attic?

Larry...I inspected an icynene insulated house last summer just east of Pflugerville. I think it was around 4 years old or so and saw no issues with the ductwork in the attic. I'd have to go find the report and photos to refresh my memory but give me a call if you want some more information. Just visit my Homepage to get my number. Also see: http://nachi.org/forum/showthread.ph...hlight=icynene

Last edited by mboyett; 4/24/07 at 11:19 AM..
Reply With Quote
  #4  
Old 4/24/07, 11:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: HVAC in unvented, spray foam insulated attic?

http://www.nachi.org/forum/showthrea...unvented+attic



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 4/24/07, 12:00 PM
Larry E. Freeze Larry E. Freeze is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Leander, TX
Posts: 27
Default Re: HVAC in unvented, spray foam insulated attic?

Cen Tex temps in sealed attics, insulated w/ spray foam...
Isocynene 'advertises' attic temps reach only about 80 degrees
instead of 130 degree range...
Have you found this to be somewhat accurate? such
a considerable reduction in attic temps in Cen Tex?
Reply With Quote
  #6  
Old 4/24/07, 12:08 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: HVAC in unvented, spray foam insulated attic?

We are moving toward spray foam insulated attics without ventilation in this area. I inspected one last week that was a few years old. The outside temperature was 80, and the temp in the attic was 76 in the mid afternoon sun. The attic I was in earlier in the day was well over 100 degrees with standard insulation and ventilation.

The utility bills on this home were also very low, comparatively.

I saw no issues in the attic or on the roof, however I understand that there is some concern that this type of insulation will cause a shorter service life on asphalt/fiberglass composition shingles.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #7  
Old 4/24/07, 12:28 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC in unvented, spray foam insulated attic?

Quote:
Originally Posted by bwiley
We are moving toward spray foam insulated attics without ventilation in this area. I inspected one last week that was a few years old. The outside temperature was 80, and the temp in the attic was 76 in the mid afternoon sun. The attic I was in earlier in the day was well over 100 degrees with standard insulation and ventilation.

The utility bills on this home were also very low, comparatively.

I saw no issues in the attic or on the roof, however I understand that there is some concern that this type of insulation will cause a shorter service life on asphalt/fiberglass composition shingles.
I can not find it now but the article I read said there was not much difference in life and the Temp of shingles was only 5 degrees different .

. Sounds like a great way to go with all that I have read .

RoyCooke
Reply With Quote
  #8  
Old 4/24/07, 12:51 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,607
Default Re: HVAC in unvented, spray foam insulated attic?

When this first started there was a big concern with the shingles and warranty issuse, but there are several of the big roofing manuf. that warrant this type of contruction. http://www.jlconline.com/cgi-local/v...177f000001053f



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #9  
Old 4/26/07, 10:40 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC in unvented, spray foam insulated attic?

This method of insulating is being used in quite a few of the "Build America" homes with the HVAC unit/ducting in the attic. It's a big energy saver since any heating/cooling loss of conditioned air is essentially into the conditioned space of the attic and the ducting does not "see" the extremes of freezing winter and boiling summer temps. It also saves airsealing all the wiring and other penetrations of the ceiling.

This was brought into the program by a Canadian ex-R2000 engineer, Joe Lstiburek, the principal at Building Science Corporation ( www.buildingscience.com ) He has also worked with the American Lung Association on their "Health House" program as co-chair of the technical committee. Believe it or Not!!! A healthy new home is airtight and heavily insulated.
Reply With Quote
  #10  
Old 4/26/07, 11:25 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: HVAC in unvented, spray foam insulated attic?

Here is one from last year. Appeared to be working fine. I have some concerns about not being able to find a leaking roof until too late. Brought this concern to buyers attention, they were non-pulsed about it.

Last edited by dedwards; 5/3/07 at 6:34 PM..
Reply With Quote
  #11  
Old 4/26/07, 11:31 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: HVAC in unvented, spray foam insulated attic?

and another

Last edited by dedwards; 5/3/07 at 6:34 PM..
Reply With Quote
  #12  
Old 4/28/07, 12:33 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC in unvented, spray foam insulated attic?

I still have reservations about the life of roof coverings, but getting more convinced daily. One thing for sure: We'll all have to get better at spotting leaks in their early stages, before obvious damage takes place, since water would most likely be wicked into sheathing material. I'd like to hear others thoughts on this.
Reply With Quote
  #13  
Old 4/28/07, 12:54 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,492
Send a message via ICQ to kshepard
Default Re: HVAC in unvented, spray foam insulated attic?

It can out-perform ventilated attics, but there does need to be some way for moisture to escape from the home to maintain indoor air quality because the home will be more tightly sealed when the underside of the roof is foamed.

Joe Lstiburek from the Building Science Corporation puts it a lot better than I can. His article doesn't have all the figures included yet but when it come to building science... HE'S THE MAN!




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #14  
Old 4/28/07, 1:14 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,492
Send a message via ICQ to kshepard
Default Re: HVAC in unvented, spray foam insulated attic?

Quote:
Originally Posted by jbreazeale
I still have reservations about the life of roof coverings...
Venting the attic only cools the roof by about 5%. Light colored roof-covering material can cool it by about 25% and that's tops. (Building Science Corp. & DOE).

They recommend a low-permeability foam be used, so my question is more about the likelihood of roof sheathing decay if moisture gets trapped between the roof-covering material and the foam, especially if the roof membrane is also low-perm.
The one advantage I see to ventilated attics is that they allow the sheathing to dry to the attic side if the roof leaks.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #15  
Old 4/28/07, 4:20 AM
Todd Stromdahl's Avatar
Todd Stromdahl Todd Stromdahl is offline
InterNACHI Member
 
Join Date: May 2006
Location: Fernandina Beach, FL
Posts: 24
Default Re: HVAC in unvented, spray foam insulated attic?

My day job is working in the roofing industry at the manufacturing level, quality control lab. The issues about shortened life of roofing are not an issue do to the fact that the temperatures under the shingles (roof deck) are much lower than they would be in a vented attic. In Florida it's not uncommon to have temps of over 140 degrees in vented attics. The temps in the attic with rigid spray foam are similar to the temperatures in the rest of the house. As to the issue of make up air, some type of energy recovery system is needed (air to air heat exchanger) this will bring in fresh air and allow stale moist air out, without this it would be like placing your house in a plastic bag. Bad.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about exposed styrofoam insulation. mlong Exterior 9 12/21/07 9:33 AM
Foam spray roof ? jlybolt Exterior 28 10/24/07 1:35 PM
Foam spray roof ? jlybolt Exterior 0 10/22/07 12:30 PM
Foam spray roof ? jlybolt Exterior 0 10/22/07 12:30 PM
Spray Foam to the Rescue ? mcyr Structural 3 3/27/07 8:29 PM


All times are GMT -4. The time now is 8:39 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts