Default HVAC wiring

Is this wiring correct correct see pics below
Attached Thumbnails
heating-venting-air-conditioning-wiring-dscf2037.jpg   heating-venting-air-conditioning-wiring-dscf2038.jpg   heating-venting-air-conditioning-wiring-dscf2046.jpg  
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/6/11, 8:14 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HVAC wiring

I don't see a problem they are feeding from the primary to the secondary breaker which probably is just thru the sequencer to the blower motor, are you concerned that you are double tapping if so that is not the case.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 9/6/11, 9:01 PM
Philip J. Cavalcante Philip J. Cavalcante is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Callaway, Md
Posts: 246
Default Re: HVAC wiring

Thanks I had the unit running and the breaker tripped and would not reset. I was also concerned with the breaker size as its a 60 and 30 amp haven't seen that large of a amperage together in a small unit.
Reply With Quote
  #4  
Old 9/6/11, 9:02 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: HVAC wiring

Charley, do you think those lugs are rated for 2 wires?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 9/6/11, 10:52 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,253
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC wiring

Quote:
Originally Posted by mlarson View Post
Charley, do you think those lugs are rated for 2 wires?

I don't. The copper and aluminum together (dissimilar metals) is also a potential problem. The aluminum EGC split into two lugs is also not correct.
Reply With Quote
  #6  
Old 9/6/11, 10:57 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: HVAC wiring

Quote:
Originally Posted by Robert Meier View Post
I don't. The copper and aluminum together (dissimilar metals) is also a potential problem. The aluminum EGC split into two lugs is also not correct.
Sorry Robert I did not pay attention to the Al you are correct



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 9/7/11, 10:08 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: HVAC wiring

Quote:
Originally Posted by Robert Meier View Post
I don't. The copper and aluminum together (dissimilar metals) is also a potential problem. The aluminum EGC split into two lugs is also not correct.
Exactly, I don't know what Charley was looking at.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
1910 Build mcyr Electrical Inspections 12 8/1/10 1:41 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 5:15 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM