#1
|
||||
|
||||
|
Model LUF80C84/95D16
Serial # 8405E00422 Leaking Carbon monoxide @ 18PPM at registers Rick Kie |
|
#2
|
|||
|
|||
|
May 05 80% efficent, oil fired.
It could put out 85,000 or 97,000 btu depending on the nozzel size. Mark Jones Allmark Home Inspection Services Inc. Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake Phone: 847 651 2053 E-Mail: AllmarkInspect@aol.com www.AllmarkHomeInspection.com |
|
#3
|
|||
|
|||
|
Mark,
You spelled nozzle wrong. Mark Jones Allmark Home Inspection Services Inc. Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake Phone: 847 651 2053 E-Mail: AllmarkInspect@aol.com www.AllmarkHomeInspection.com |
|
#4
|
||||
|
||||
|
Armstrong is owned by Lennox. With Lennox it would be May 2005.
The first two no. are the plant, 2nd two are the year, the letter in 5th slot the month. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#5
|
||||
|
||||
|
3 years old and spewing carbon monoxide Thank you for your help.
Rick Kie |
|
#6
|
|||
|
|||
|
I have a grandaughter who's 1 and some of the gases coming out of her are amazing,
I'm so proud! Mark Jones Allmark Home Inspection Services Inc. Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake Phone: 847 651 2053 E-Mail: AllmarkInspect@aol.com www.AllmarkHomeInspection.com |
|
#7
|
||||
|
||||
|
Congradulations Grandpa! does she take after grandpa?
Rick Kie |
|
#8
|
||||
|
||||
|
Very unusual to get readings out of the newer furnaces, even if the the heat exchanger is cracked...due to the induction motor, which lowers the pressure in the exchanger and makes it much more difficult for the gases inside the exchanger to mix with the air blowing around the outside of the exchanger. Was the induction motor working or had it's safety been tampered with? Chimney pluggged? Massive heat exchanger failure??? Curious, if you find out...
Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right! (website) http://inspectorpages.com/dhadler
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Armstrong oil Furnace | dgoudreau | Inspecting HVAC Systems | 3 | 7/19/08 12:21 PM |
| Date code For Armstrong Furnace | kmalone | Inspecting HVAC Systems | 4 | 4/27/08 9:30 AM |
| Date code For Armstrong Furnace | kmalone | Inspecting HVAC Systems | 0 | 4/26/08 3:05 PM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 1:26 AM |
| Armstrong Ultra 80 Oil Forced air furnace | Stephen Frazer | Inspecting HVAC Systems | 19 | 4/9/07 8:00 PM |