I ran into an Amana 90% Furnace yesterday (model # GUC090B35C / Serial Number 910110599
There is a closet on 1 side of the family room with louvred doors out to the family room (closet room is about 7' x 7'). On the opposite side of the family room is a kids bedroom. To get to the bedroom you have to go thru the family room (about 20' x 20'). The kids bedroom only has 1 entry - thru the familyroom. There is only 1 pvc pipe leaving the furnace / It goes out the roof and terminates with a "U-Shaped" elbow on the roof end. I don't see a pipe in a pipe at the roof vent BUT I don't see intake opening into furnace below. I'm trying to find installation instruction on this unit and have had no luck. Feel its totally wrong installation and improper C/A, but looking for info to see how its allowed to be vented. |
| Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
That kinda puzzles me also the U bend on the roof is normally for intake sounds like they got confused. In my area the intake does not have to go through the roof. I presume the furnace is in the closet behind the louvered doors using the SQ FT area of the basement for combustion air. Not sure why you can not see the combustion intake on the furnace?????
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#3
|
|||
|
|||
|
Geez Charlie,what a dimwit I am .... Just realized the door was off the furnace when I got there and nowhere in sight. Looked on I-net; that model has louvred upper door ..... Duh.
Heres roof shot and furnace shot. More than enough reasons to have HVAC service and repair .... Leaks at condensate and inducer; clogged blower motor; boot on roof split; R/A grill too close to burners; location of unit & size of room for C/A requirements; etc BUT I was brain dead on C/A location Last edited by dbowers; 1/15/12 at 10:41 PM.. |
|
#4
|
||||
|
||||
|
That is a upflow furnace and appears to have a return grill real close to the unit. Was there a knock out on the top left side of the housing the way they left it the combustion blower can draw from the burner area should in my opinion at least be outside and above the unit
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#5
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#6
|
||||
|
||||
|
Preston's Guide lists that model as a 1992/93.
BPI Certified Professional Building Analyst BPI Certified Envelope Professional Infraspection Institute Certified Level II Thermographer # 8510 www.dapkusinspections.com www.chicagoinfraredthermalimaging.com www.mychicagohomeinspector.com www.commercialbuildinginspectionchicago.com Professional Infrared Network Chicago Energy Audit Aerial Infrared Inspection Certified Infrared Thermal Imaging |
|
#7
|
|||
|
|||
|
Thanks Linus ... Also the gas valve was date stamped with 91/49
49th week of 1991 SO a double check on age |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Amana Furnace Age | bhartley | Inspecting HVAC Systems | 4 | 5/6/11 9:02 PM |
| Amana Furnace Age | jgromkoski | Inspecting HVAC Systems | 4 | 1/13/11 8:12 AM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 1:26 AM |
| Amana Furnace Age | ekartal6 | Inspecting HVAC Systems | 7 | 1/1/08 9:37 PM |
| Amana furnace age | cjs | Inspecting HVAC Systems | 2 | 3/25/06 5:16 PM |