I ran into an Amana 90% Furnace yesterday (model # GUC090B35C / Serial Number 910110599. The basement has been finished out fully, and is divided into a big family room with full doors to the upstairs.

There is a closet on 1 side of the family room with louvred doors out to the family room (closet room is about 7' x 7'). On the opposite side of the family room is a kids bedroom. To get to the bedroom you have to go thru the family room (about 20' x 20'). The kids bedroom only has 1 entry - thru the familyroom.

There is only 1 pvc pipe leaving the furnace / It goes out the roof and terminates with a "U-Shaped" elbow on the roof end. I don't see a pipe in a pipe at the roof vent BUT I don't see intake opening into furnace below.

I'm trying to find installation instruction on this unit and have had no luck.

Feel its totally wrong installation and improper C/A, but looking for info to see how its allowed to be vented.
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/15/12, 9:58 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Help With Amana 90% Furnace

That kinda puzzles me also the U bend on the roof is normally for intake sounds like they got confused. In my area the intake does not have to go through the roof. I presume the furnace is in the closet behind the louvered doors using the SQ FT area of the basement for combustion air. Not sure why you can not see the combustion intake on the furnace?????



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 1/15/12, 10:38 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Help With Amana 90% Furnace

Geez Charlie,what a dimwit I am .... Just realized the door was off the furnace when I got there and nowhere in sight. Looked on I-net; that model has louvred upper door ..... Duh.

Heres roof shot and furnace shot.

More than enough reasons to have HVAC service and repair .... Leaks at condensate and inducer; clogged blower motor; boot on roof split; R/A grill too close to burners; location of unit & size of room for C/A requirements; etc BUT I was brain dead on C/A location
Attached Thumbnails
help-amana-90-furnace-img_4257.jpg   help-amana-90-furnace-img_4309.jpg  

Last edited by dbowers; 1/15/12 at 10:41 PM..
Reply With Quote
  #4  
Old 1/15/12, 10:47 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Help With Amana 90% Furnace

That is a upflow furnace and appears to have a return grill real close to the unit. Was there a knock out on the top left side of the housing the way they left it the combustion blower can draw from the burner area should in my opinion at least be outside and above the unit



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 1/15/12, 10:49 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Help With Amana 90% Furnace

Quote:
Originally Posted by dbowers View Post
Geez Charlie,what a dimwit I am .... Just realized the door was off the furnace when I got there and nowhere in sight. Looked on I-net; that model has louvred upper door ..... Duh.

Heres roof shot and furnace shot.

More than enough reasons to have HVAC service and repair .... Leaks at condensate and inducer; clogged blower motor; boot on roof split; R/A grill too close to burners; location of unit & size of room for C/A requirements; etc BUT I was brain dead on C/A location
Been there done that sometimes can not see the trees for the forest



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 1/16/12, 6:18 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Help With Amana 90% Furnace

Preston's Guide lists that model as a 1992/93.
Reply With Quote
  #7  
Old 1/18/12, 10:36 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Help With Amana 90% Furnace

Thanks Linus ... Also the gas valve was date stamped with 91/49

49th week of 1991 SO a double check on age
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Amana Furnace Age bhartley Inspecting HVAC Systems 4 5/6/11 9:02 PM
Amana Furnace Age jgromkoski Inspecting HVAC Systems 4 1/13/11 8:12 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Amana Furnace Age ekartal6 Inspecting HVAC Systems 7 1/1/08 9:37 PM