Inspected a condo today.
The condenser units data sticker says, "max fuse or ckt. bkr. 20 amps". The disconnect has a 60 amp 2 pole breaker installed in it. I noticed that the disconnect serves two condensers. How can this be right. I did not remove the cover of the disconnect box because there were mud dauber nests all over it.


The data sticker on the air handler says "max. current rating of supply circuit fuse or HACR type ckt. bkr. 30/25". The disconnect box had a 60 amp breaker in it.

Seems to me that both units are overfused. What say you?
Reply With Quote
  #2  
Old 1/28/07, 5:26 AM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,021
Default Re: Help with first report

You are referring to the disconnect next to the condensers, right?

If you've got one 60 Amp breaker protecting two condensers, that's simply overfused and double tapped inside. Safety issue, big time.

And if the residential Air Handler is protected by a 60 Amp breaker also, you've got overfusing there too.
Reply With Quote
  #3  
Old 1/28/07, 5:35 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help with first report

Thought so. Thanks.
Reply With Quote
  #4  
Old 1/28/07, 9:16 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with first report

Over fusing is very common on A/C units. For one the disconnects are sometimes installed by the HVAC installer, who is only concerned that the fuse doesn't blow, and two a lot of A/C units are replacements and the installer doesn't bother to check or change the disconnect.
Could you tell me, just out of curiosity, how you were able to tell the size of the breaker without opening the disconnect? If the breaker is in a weather proof enclosure the breaker shouldn't have been visible.
Reply With Quote
  #5  
Old 1/28/07, 12:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Help with first report

Wesley,

I would say the feeding (2) outside units from a single disconnect leaves me saying have it evaluated...most certainly if we are only talking about a single 20A supply.

As for a general understanding, many times a disconnect at a outside unit or even inside unit will have 60A on it but are then protected back at the panel with a lets say 30A breaker ( for arguement sake )...the 60A breaker or disconnect at the unit would then simply be the service switch at the unit for disconnection means and not the overcurrent protection device...this would take place back at the panel....just in case anyone wanted to know about that.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 1/28/07, 2:50 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help with first report

Quote:
Originally Posted by smcarthur
Over fusing is very common on A/C units. For one the disconnects are sometimes installed by the HVAC installer, who is only concerned that the fuse doesn't blow, and two a lot of A/C units are replacements and the installer doesn't bother to check or change the disconnect.
Could you tell me, just out of curiosity, how you were able to tell the size of the breaker without opening the disconnect? If the breaker is in a weather proof enclosure the breaker shouldn't have been visible.
I could open the lid but not remove the cover. Breaker or switch was inscribed 60.

Attachment 8748

Last edited by waksell; 5/6/07 at 3:06 PM..
Reply With Quote
  #7  
Old 1/28/07, 3:06 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Help with first report

Quote:
Originally Posted by pabernathy
Wesley,

I would say the feeding (2) outside units from a single disconnect leaves me saying have it evaluated...most certainly if we are only talking about a single 20A supply.

As for a general understanding, many times a disconnect at a outside unit or even inside unit will have 60A on it but are then protected back at the panel with a lets say 30A breaker ( for arguement sake )...the 60A breaker or disconnect at the unit would then simply be the service switch at the unit for disconnection means and not the overcurrent protection device...this would take place back at the panel....just in case anyone wanted to know about that.
Paul, I would say that I was mistaken when I said that the disconnect served two units. I was so nervous on my first inspection that I was not thinking clear. The disconnect had two flexes coming out of the bottom, one to the unit in question, and another "toward another unit a few feet away". I assumed it was serving that unit. After my post I realized that the other flex was actually coming from out of the ground and providing power to, not from, the disconnect.

Attachment 8752
Attachment 8751

Last edited by waksell; 5/6/07 at 3:06 PM..
Reply With Quote
  #8  
Old 1/28/07, 5:02 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: Help with first report

Normally I do not get too excited about circuit breakers that are larger than recommended by the equipment manufacturer as long as they are not excessively large.

The way I look at this issue is that the circuit breaker is there to protect the wiring from the breaker to the unit (or another subpanel).
Next, the issue that you may have found (if you had opened up the panel, which I feel you should have) is that the wire must be rated for the circuit breaker size. Depending on the type of wire, 60 amp conductor may be excessively large to be attached to the magnetic contactor (in most cases always is). So, this is reverse engineering to some extent. We have a unit that can handle 20 amp wire size. If the wire is properly sized for the 60 and breaker then it is oversized and will not attach properly to the unit and that is a problem.

If the wire is not properly sized for the 60 amp breaker than that is the issue.
Why didn't you open the panel? Mud wasps are not active in the wintertime anywhere. They are simply dormant nests. If you saw one circuit breaker and feel that there is two condensing unit's operating from that one disconnect, it should be obvious that a double tap is possible. Unless there is a swarm of bees actively staring you in the face I think I would have opened the panel.

I am not suggesting that you do not "report" be over amperage breaker.
Reply With Quote
  #9  
Old 1/29/07, 2:42 AM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Help with first report

Normally, my rule of thumb is that you want the weakest link in any electrical circuit to be the circuit breaker. It can't be undersized or oversized. You want it to trip at the right time to protect whatever the load is. The manufacturer's spec plate on the condensor should indicate what the recommended breakers size is.

That is why you also check wire size. If it's too thin, it over heats and becomes a fusible link. Not a good thing.
Reply With Quote
  #10  
Old 1/29/07, 6:20 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Help with first report

Congratulations on your 1st Inspection. Enjoy what your doing and the nerves should go away. Remeber your only human
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
**HOT** Texas Inspectors use of REI-7A-0 escanlan Legislation, Licensing & Legal Issues 27 11/20/07 1:09 AM
New Report Upload Technology cdemsky Misc. Discussion 49 5/1/07 11:19 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues 0 2/14/06 4:38 AM


All times are GMT -4. The time now is 6:10 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts