Default high humidity and floor lifting

Have a situation in a condo building where the laminate floor is lifting in an area near the kitchen. First thing I noticed when myself and my other inspector walked in was the felling of the humidity. The floor has expanded but it seems like more then normal expansion. When we checked the A/C air handler there was no water in the condensate tray under the evaporator coil, it was completely dry along with the drain pipe when I stuck my finger in. My assessment at that point was that the airhandler instead of removing the moisture from the air was blowing it back into the air. The owner did not want the humidity tested. Any thoughts?



Preston L. Halstead
VP FL Home & Insurance Inspectors Chapter
Elite Property Inspection & Management
LICENSED GENERAL CONTRACTOR CGC1515203
LICENSED BUILDING INSPECTOR BN6262
LICENSED HOME INSPECTOR HI549



HOME INSPECTION ~ WIND MITIGATION INSPECTION
Serving Boca Raton, Boynton Beach, Delray Beach, Juno Beach, Jupiter, Lake Park, Lake Worth, Lantana, North Palm Beach, Palm Beach, Palm Beach Gardens, Royal Palm Beach, Wellington, West Palm Beach.
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/7/11, 8:58 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: high humidity and floor lifting

Where you doing an inspection if so why did you not just set you tester down to see what the humidity was.
How did you get involved with the home owner.
I just do my inspection as per usual... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 7/7/11, 9:10 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: high humidity and floor lifting

Quote:
Originally Posted by phalstead View Post
Have a situation in a condo building where the laminate floor is lifting in an area near the kitchen. First thing I noticed when myself and my other inspector walked in was the felling of the humidity. The floor has expanded but it seems like more then normal expansion. When we checked the A/C air handler there was no water in the condensate tray under the evaporator coil, it was completely dry along with the drain pipe when I stuck my finger in. My assessment at that point was that the airhandler instead of removing the moisture from the air was blowing it back into the air. The owner did not want the humidity tested. Any thoughts?
Ac the proper size?



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #4  
Old 7/7/11, 9:23 AM
Preston L. Halstead Preston L. Halstead is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: West Palm Beaach, FL
Posts: 696
Default Re: high humidity and floor lifting

Quote:
Originally Posted by rcooke View Post
Where you doing an inspection if so why did you not just set you tester down to see what the humidity was.
How did you get involved with the home owner.
I just do my inspection as per usual... Roy
This was actually part of a construction project our other company performed last year. It was a quick stop by and when we mentioned we wanted to do a full assessment we were no longer welcom in the home.



Preston L. Halstead
VP FL Home & Insurance Inspectors Chapter
Elite Property Inspection & Management
LICENSED GENERAL CONTRACTOR CGC1515203
LICENSED BUILDING INSPECTOR BN6262
LICENSED HOME INSPECTOR HI549



HOME INSPECTION ~ WIND MITIGATION INSPECTION
Serving Boca Raton, Boynton Beach, Delray Beach, Juno Beach, Jupiter, Lake Park, Lake Worth, Lantana, North Palm Beach, Palm Beach, Palm Beach Gardens, Royal Palm Beach, Wellington, West Palm Beach.
Reply With Quote
  #5  
Old 7/7/11, 10:03 AM
David Garton's Avatar
David Garton David Garton is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Northern CA.
Posts: 277
Default Re: high humidity and floor lifting

Quote:
Originally Posted by phalstead View Post
This was actually part of a construction project our other company performed last year. It was a quick stop by and when we mentioned we wanted to do a full assessment we were no longer welcom in the home.
Just blame it on the other company



David Garton
Eagle Eye Inspection Services
david@yubacityhomeinspection.com
http://yubacityhomeinspection.com
Licensed Building Contractor
Serving Yuba City, CA. and the surrounding areas
(530) 415-1269
Reply With Quote
  #6  
Old 7/7/11, 10:29 AM
Preston L. Halstead Preston L. Halstead is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: West Palm Beaach, FL
Posts: 696
Default Re: high humidity and floor lifting

Quote:
Originally Posted by dgarton View Post
Just blame it on the other company
The airhandler is existing and wasn't part of the construction project. my question is more of if the condensation is not being removed through the drain where is it going.



Preston L. Halstead
VP FL Home & Insurance Inspectors Chapter
Elite Property Inspection & Management
LICENSED GENERAL CONTRACTOR CGC1515203
LICENSED BUILDING INSPECTOR BN6262
LICENSED HOME INSPECTOR HI549



HOME INSPECTION ~ WIND MITIGATION INSPECTION
Serving Boca Raton, Boynton Beach, Delray Beach, Juno Beach, Jupiter, Lake Park, Lake Worth, Lantana, North Palm Beach, Palm Beach, Palm Beach Gardens, Royal Palm Beach, Wellington, West Palm Beach.
Reply With Quote
  #7  
Old 7/7/11, 11:01 AM
Jamie R. Wilks's Avatar
Jamie R. Wilks Jamie R. Wilks is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Southeast, Virginia
Posts: 133
Default Re: high humidity and floor lifting

Just like wayne was refering to; Maybe the AC system is too large, cooling so fast no humidity is being removed from the home/condo.



Jamie R Wilks
North Star Home Inspections
VCHI #3380000351
InterNACHI #05081596
Reply With Quote
  #8  
Old 7/7/11, 11:14 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: high humidity and floor lifting

If it was just the A/C wouldn't there be other signs other than that one area in the kitchen?



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #9  
Old 7/7/11, 11:17 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: high humidity and floor lifting

Quote:
Originally Posted by jbraun View Post
If it was just the A/C wouldn't there be other signs other than that one area in the kitchen?
You better test for toxic mold. The buyers can develop serious neurological problems or even die if you don't.
Reply With Quote
  #10  
Old 7/7/11, 11:17 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: high humidity and floor lifting

Maybe not James Depends on what other material present. carpet, hardwood so on



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #11  
Old 7/7/11, 11:19 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: high humidity and floor lifting

Location-West Palm Beach Florida.

Very highly unlikely that any unit incompatibility with the application will not produce some sort of moisture in Florida.

Two potential issues:

1) the HVAC unit is leaking condensate somewhere else, not were you checked it. Maybe associated with lifting flooring because water is flowing under the floor.

2) the HVAC unit is not producing condensate because it is not working.

If the air temperature in the house is lower than the outside air temperature than something is working and water is leaking somewhere else.

If the condensate is frozen it will not drain…

I guess if you have no access to the building for further evaluation because you're not welcome then just hang it up. Insufficient information to provide any further analysis.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 7/7/11, 11:22 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: high humidity and floor lifting

By the way, the air handler does not put moisture into the air.

I don't know how many times we have to say this but energy cannot be created or destroyed out of thin air!

Moisture just doesn't appear or disappear, it is transformed from another state.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #13  
Old 7/7/11, 11:50 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: high humidity and floor lifting

Quote:
Originally Posted by wwilson3 View Post
Maybe not James Depends on what other material present. carpet, hardwood so on
I would think the whole kitchen floor would have about equal damage if it was the A/C cycling too much. Since no moisture readings were taken, it nothing but a big guess. Usually with very high humidity (enough to cause flooring to warp), the porous materials in the rest of the house will smell some due to bacteria, mold and other growths.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/7/11, 12:02 PM
Preston L. Halstead Preston L. Halstead is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: West Palm Beaach, FL
Posts: 696
Default Re: high humidity and floor lifting

Quote:
Originally Posted by dandersen View Post
I guess if you have no access to the building for further evaluation because you're not welcome then just hang it up. Insufficient information to provide any further analysis.
Interesting that when it was mentioned that we wanted to evaluate further that we were no longer welcome in the home.....

If the coils have condensation and it isnt making its way to the pan and draining out wouldnt it be working similar to a swamp cooler and re-introducing moisture to the air?

funny thing as far as the floor goes is no one every said it wouldnt get fixed. We just stated that we wanted to evaluate it first. Thats when we were told we were not allowed back.



Preston L. Halstead
VP FL Home & Insurance Inspectors Chapter
Elite Property Inspection & Management
LICENSED GENERAL CONTRACTOR CGC1515203
LICENSED BUILDING INSPECTOR BN6262
LICENSED HOME INSPECTOR HI549



HOME INSPECTION ~ WIND MITIGATION INSPECTION
Serving Boca Raton, Boynton Beach, Delray Beach, Juno Beach, Jupiter, Lake Park, Lake Worth, Lantana, North Palm Beach, Palm Beach, Palm Beach Gardens, Royal Palm Beach, Wellington, West Palm Beach.
Reply With Quote
  #15  
Old 7/7/11, 12:27 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: high humidity and floor lifting

Quote:
If the coils have condensation and it isnt making its way to the pan and draining out wouldnt it be working similar to a swamp cooler and re-introducing moisture to the air?
No; the reason that the water is forming on the coil was because it is at saturation temperature. That means there is enough BTUs being removed from the air passing by the coil to change its state. It takes about 970 BTUs per pound of condensate to change state from vapor to liquid (at the same temperature). So long as the equipment is removing this quantity of BTUs, condensate will form and will not evaporate.

The only possible time that you will evaporate condensate is if you turn off the air conditioner and leave the blower fan in the on position.

This will never occur under normal automatic operation as the unit will never shut off. As long as it runs, the coil is at saturation temperature and is basically absorbing moisture from the air and turning it into condensate. The moisture in the air cannot get past the evaporator coil without some of it condensing.

There is a bypass factor involved were a percentage of the air is not treated by the coil on the first pass. However, the volume of moisture in the air downstream of the coil will always be a lower humidity level then that entering upstream of the coil. (Not to be confused with the fact that the relative humidity goes to one hundred percent).
If you are to artificially induce the evaporation of condensed condensate and if nothing went down the condensate drain, you could never increase the volume of moisture within the house. You can only put back what you took out.

Again, energy cannot be created or destroyed. Energy you ask? Yes, there is a huge amount of energy transferred that takes place when water is condensed or evaporated. This is called the latent heat of fusion and the latent heat of evaporation. It requires a source of energy transfer.

At what temperature does water freeze? 32°F? Can water exist in a liquid state at 32°F? Yes it can and yes it does.

A humidifier uses energy to produce water vapor to be injected into the supply air. This is the only way that you can increase humidity inside the house beyond that of the outside air..

Vapor pressure will equalize. You cannot increase moisture beyond equilibrium.
Furnaces do not dehydrate the air. Air conditioners do not hydrate the air.

If inspectors would learn these very simple basic perceptions, it would vastly improve their analysis of what's going on in their building inspections.
 



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts