Default hmmm

They said it's ok its a power vent
Attached Thumbnails
hmmm-100_1893.jpg  
Reply With Quote
Need a home inspection in Colorado? Check out InterNACHI's listing of Colorado certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/31/10, 6:32 PM
Steven Taylor's Avatar
Steven Taylor Steven Taylor is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 106
Default Re: hmmm

Well that makes sense. The fan would push out the gases instead of relying on natural draft.
Reply With Quote
  #3  
Old 2/1/10, 11:50 PM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: hmmm

I’m sure Dave has explained this before, but no one else is touching it so here goes. (Where’s Ben Dave???) LMAO

Short answer it is acceptable to be vented horizontally with a maximum downward (yes downward) pitch of ¼ inch per foot.

Long answer…
Ronald if the gas appliance is using B-Vent it is a Cat I Appliance and in this case would be a Fan Assist Cat I Appliance. The "power vent" of a Cat I doesn’t create a positive vent pressure to exhaust and therefore still relies on the buoyancy of the hot flue gasses to vent them horizontally to the exterior.
You can vent them horizontally with a maximum downward pitch of ¼ inch per foot when AHJ allow it. You also have limitations with horizontal distances that cannot be exceeded as per manufacturers’ specs along with termination points.

Definition of a Cat I Appliance is one that operates with a nonpositive vent static pressure and a flue loss not less than 17%. Flue gas temperature 140F above its dew point so it won’t (shouldn’t) condense.

Steve the only time flue gasses are pushed out is with Cat IV high efficiency furnaces and are vented with plastics like PVC, ABS or 636 or Cat III Appliances that are vented with stainless steel all of which are a sealed venting systems to contain the products of combustion under a positive vent pressure.
The fan assist of a Cat I has say a two inch exhaust port. When you attach a 4 inch or 5 inch vent to the two inch port it becomes a non positive pressure at that point.
Hold a match to any screw hole on C vent and it will pull the flame in, nonpositive vent pressure.

Definition of a Cat III Appliance is one that operates with a positive vent static pressure and with a flue loss not less than 17%. Flue gas temperature 140F above its dew point temperature won’t (shouldn’t) condense.

Definition of a Cat IV Appliance is one that operates with a positive vent static pressure and with a flue loss less than 17%. Flue gas temperature is less than 140 F above its dew point moisture in flue gasses will condense.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hmmm I wonder? bkelly2 HVAC 1 12/3/09 6:43 PM
Hmmm! tlower Structural 11 9/19/09 4:29 PM
Hmmm.. psmothers Plumbing 2 3/11/06 2:28 PM


All times are GMT -4. The time now is 6:15 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts