Default Hmmmm Low Delta T?????????

Can't even imagine why????????

Last edited by bkelly2; 10/13/08 at 7:09 PM..
Reply With Quote
  #2  
Old 9/2/08, 7:44 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Hmmmm Low Delta T?????????

Ran into a similar situation last week. After moving a dead rat in a huge trap out of the way I saw where he had eaten thru the covering, the insulation and the inner duct to build a nest in a nice, cool section of the flex duct. You can't really see it in this photo but 50-70% of the conditioned air from that duct was being lost to the attic of this 1936 home.

hmmmm-low-delta-t-flex.jpg
Reply With Quote
  #3  
Old 9/3/08, 7:15 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by bkelly2
Can't even imagine why????????
Brian:

Did you check the temps of the cooled air before it moved past these points with deteriorated plastic covering. My thinking is that if the insulation was still fully intact with the inner air-carrying duct being air tight, the delta T still may be low from poorly operating/serviced AC unit.
Reply With Quote
  #4  
Old 9/3/08, 7:33 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Hmmmm Low Delta T?????????

I had pretty much written off the HVAC before I got into the attic Brian, this was just one more nail in the coffin. Unit was original circa 1985.

Last edited by bkelly2; 10/13/08 at 7:09 PM..
Reply With Quote
  #5  
Old 9/4/08, 11:37 AM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by mboyett
Ran into a similar situation last week. After moving a dead rat in a huge trap out of the way I saw where he had eaten thru the covering, the insulation and the inner duct to build a nest in a nice, cool section of the flex duct. You can't really see it in this photo but 50-70% of the conditioned air from that duct was being lost to the attic of this 1936 home.

Attachment 23688
Michael, what are you doing moving personal property?



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #6  
Old 9/4/08, 4:36 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hmmmm Low Delta T?????????

I hate to start this but BK here goes anyway David A. is on vacation so let her rip take my pics of 72 degrees within the home and 55 degrees on the supply and move the delta T to 85 within the home and 67 degrees on the supply. What would you say about the system then???????
Attached Thumbnails
hmmmm-low-delta-t-3602-s.-garland-enid-9-4-08-065.jpg   hmmmm-low-delta-t-3602-s.-garland-enid-9-4-08-066.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 9/4/08, 4:39 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by cbottger
I hate to start this but BK here goes anyway David A. is on vacation so let her rip take my pics of 72 degrees within the home and 55 degrees on the supply and move the delta T to 85 within the home and 67 degrees on the supply. What would you say about the system then???????
Nice try Charley, but not enough info.

But if it has not been serviced in the last year, they better have a HVAC contractor out there to check it out.

I do not like the dirty rusty registers either.
Reply With Quote
  #8  
Old 9/4/08, 4:39 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Hmmmm Low Delta T?????????

Working good Charley----

Yep....you're damn lucky David is on vacation----------------
Reply With Quote
  #9  
Old 9/4/08, 4:43 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by bkelly2
Nice try Charley, but not enough info.

But if it has not been serviced in the last year, they better have a HVAC contractor out there to check it out.
For what?-----------------

Oh my, you and OUR court system seem to have you gun-shy----
---

Me too, actually-------
Reply With Quote
  #10  
Old 9/4/08, 5:00 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by bkelly2
Nice try Charley, but not enough info.

But if it has not been serviced in the last year, they better have a HVAC contractor out there to check it out.

I do not like the dirty rusty registers either.
Come on Wuss what more do you need put those temps on any unit that you have looked at.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 9/4/08, 5:02 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by cbottger
Come on Wuss what more do you need put those temps on any unit that you have looked at.

Ah therein lies the rub Charley, I haven't looked at that unit now have I?

And the register is still dirty and rusty.
Reply With Quote
  #12  
Old 9/4/08, 5:03 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by dduffy
Working good Charley----

Yep....you're damn lucky David is on vacation----------------
You got that right I am sure I will catch hell for this



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 9/4/08, 5:12 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by bkelly2
Ah therein lies the rub Charley, I haven't looked at that unit now have I?

And the register is still dirty and rusty.
Don't want to rub you and don't care about the dirt and rust you are avoiding the subject



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 9/8/08, 6:20 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by cbottger
the delta T to 85 within the home and 67 degrees on the supply. What would you say about the system then???????
...this is unhealthful to my delicate psyche



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #15  
Old 9/8/08, 7:57 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Hmmmm Low Delta T?????????

Quote:
Originally Posted by cbottger
..take my pics of 72 degrees within the home and 55 degrees on the supply and move the delta T to 85 within the home and 67 degrees on the supply. What would you say about the system then???????
Based on my limited knowledge & training I would let the system run for 12-15 minutes and if the room temp was coming down to say 82 or so then to 80 I would call the system operating properly with a delta T of around 18°. Now, I'm sure that's the wrong answer so feel free to berate me and inform me of my shortcomings...maybe we will all learn something.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Delta T can be tough cbottger Thermal Imaging, Infrared Cameras & Energy Audits 0 5/7/08 10:07 PM
Hmmmm bkelly2 Interior Inspections 20 3/26/07 2:49 AM


All times are GMT -4. The time now is 5:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts