I wanted to expand on a statement that I made concerning the checks that I perform on the older type gas fired furnaces. I stated that I do not check the limit switch. What I should of stated was I do not check the high set point of this switch by turning off the fan blower and checking what temperature this switch opens at thus shutting down the gas valve. My checks are all performed strictly by operation from the thermostat.
What I do check concerning the limit switch is premature opening of this switch during normal operation. This switch normally opens in the area of 200 degrees at the heat exchanger. I usually average 2 to 4 furnaces a year that the limit switch is malfunctioning and this is determined by simply observing the furnace to ensure the burners are not cycling on and off before the set point of the thermostat is reached. This is something that I consider very easy to overlook and is probally missed by many inspectors. </IMG> |
|
#34
|
||||
|
||||
|
Quote:
Quote:
Quote:
Quote:
NACHI 2005 U.S. Member of the Year
|
|
#35
|
|||
|
|||
|
I wrote about the way reporting on "a leaky faucet" has evolved over the years, as we attempt to better protect ourselves. However, I heard it first in a seminar given by Bob Pearson, of Marion Allen Insurance. The story has the virtue of being funny, very real, veryu serious, and very educational. P.S. I'm trying to persuade Bob to do a seminar with me on avoiding litigation for NACHI, and hope he'll take me up on it. It'll be interesting.
|
|
#36
|
||||
|
||||
|
Quote:
Brian, I posted a question on another thread you authored: Quote:
Why. was it too SIMPLE? The fact of the matter is that HVAC is so damn backwards (as Jae posted) that few (to include seasoned HVAC Vets) understand the true operation of what is really going on. If you would like to stick to this thread, how about explaining the simple process of "Dynamic Loss" or the effect of "Apparatus Dew Point" on the temperature split. I would like to expand this subject to cover the Sensible Heat Factor and By-pass factor of evaporator coil design and a few other simple processes that apply. But, that subject may be too elementary and bore too many folks to discuss!? |
|
#37
|
||||
|
||||
|
Quote:
Let the sleeping dog lye you are getting to deep for this board I do not consider Hvac as backward,scientific or complicated just a simple pressure/temperature releationship. </IMG> |
|
#38
|
||||
|
||||
|
Quote:
Short cycling is a good choice of words. Point being how many inspectors stay in front of the furnace to determine this. If the burner cycles on and off enough it will eventually reach set point of the stat. |
|
#39
|
|||
|
|||
|
Not if it is cycling due to tstat anticapator(older stats not eletronics).
|
|
#40
|
||||
|
||||
|
Quote:
The anticapator has notta to do with cycling the burner unless set point was reached as they were designed to do exactly as their name indicates. (Anticapate) Energize the gas valve approximately 2 degrees below set point. If you have a burnt out Anticapator you will have no flame the gas valve will not open. </IMG></IMG></IMG> |
|
#41
|
||||
|
||||
|
What are we talking about here Charley?
Quote:
It can not energize anything if "it" is not energized. The "anticipation", is when you get close to set point while the unit is running. Anticipating the approaching set point. It's job is to make the t-stat reach set point before the room temp actually gets there. This prevents the furnace overshooting the set point (Due to the delayed reaction of the produced heat from the furnace reaching the t-stat location). Quote:
The anticipator overheats and shuts down the t-stat prematurely. Once off and the anticipator is off, the t-stat cools quickly (from the cold room temp) and the furnace comes right back on. It appears this is another one of those "backwards", it's not what you would expect HVAC things!? Quote:
Last edited by dandersen; 7/24/06 at 12:08 AM.. |
|
#42
|
||||
|
||||
|
David we were originally talking about short cycling the furnace burner on a limit switch that was opening premature and some how the stat got brought into play.
Yes the heat anticapitor setting has to be matched with the amp draw of the gas valve or it will not maintain temp close to stat setting but in my thinking this is not a true short cycle in relation to the short cycle from a bad limit switch as the anticapitor will cycle the burner and the blower where as the limit switch being in the air stream of the blower cools much faster than a heat anticapitor at the stat. Most of the time the blower will not have shut down on its fan switch before the gas valve re-opens. Lets just pick some numbers the normal operating range for a fan switch on the older furnaces say closes at 110 degrees and activates the blower motor. In the mean time the limit switch is factory set at say 200 degrees but this switch decides its going to open at say 115 degrees it shuts down the gas valve thus no flame but the blower is still running because it does not shut down until say 90 degrees in the mean time the limit switch has cooled enough to close the circuit and re-active the gas valve creating a short cycle of the burner that Mr. home inspector does not observe because he was not squatted in front of the furnace watching the flame he was back in the hall somewhere waiting to hear the blower shut down giving the false impression that the furnace was performing as intended David I don't know what I was rambling on about the heat anticapitor some times I don't proof read what I am spouting about. Sorry. |
|
#43
|
||||
|
||||
|
That is correct.
Also, we should note that some furnaces may cycle (shortly It's good to get all this "how it works" stuff out. Just for a better understanding for all. I just don't want misinterpretation sending someone down the road to get in legal trouble. I had a local TVA Inspector inspector testing a furnace install that a company just installed. It was 98 degrees outside at 6:30 pm. The furnace was short cycling and he was not going to pass it till it would run without cycling. I forgot what the temps coming out were, but it was close to a blast furnace! I was called in by Trane to trouble shoot. I ended up changing the limit switch to a 300 degree until the inspector left! Some things are just not meant to be! |
|
#44
|
||||
|
||||
|
Typically building heat gain is calculated in tons of refrigeration needed:
· 1 ton of cooling is the amount of cooling provided by melting 1 ton of ice over a 24-hour period. · 1 ton of cooling equals 12,000 British Thermal Units (BTU) per hour. · It takes 1 BTU to raise 1 pound of water 1oF. · It takes approximately 1160 BTU to evaporate 1 pound of water. · It takes 0.24 BTU to raise 1 pound of air 1oF. · One pound of air occupies 13.7 cubic feet of space at sea level when the temperature is 75°F. · Removing 1 ton of building heat requires cooling 570 cubic feet per minute (CFM) of room air from 75°F to 55oF at sea level. · Removing 1 ton of building heat requires cooling 660 CFM of room air from 75°F to 55oF at 5,000 feet in elevation. I believe if you move the decimal place one spot that would answer your BTU question David. Now after reading many posts here I have seen the light, HVAC is one of the most complicated sciences known to mankind. In light of such facts and after much research, I have concluded that HVAC is so complicated that there are no recorded events of homeowner complaints with either heating or cooling of residential homes, because mere homeowners do not posses the knowledge to tell if their system is working or not working. Thank you gentlemen. Oh yea Larry, heat produces perspiration, which leads to evaporation, and you cool off. Last edited by bkelly2; 7/24/06 at 9:29 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Horizontal Furnace in Attic | Anthony Joseph | Inspecting HVAC Systems | 5 | 10/12/07 9:08 AM |
| Horizontal Furnace Installation | bpaull | Inspecting HVAC Systems | 3 | 9/14/07 6:42 PM |
| Common Defects List by Age of House | trausch | Inspection Education & Training | 10 | 6/12/06 4:52 AM |