Default Hot water elec.

I would think that this wire that is feeding the hot water tank needs to have armor cable? This would help to prevent any damage to the wire, this tank is in the garage.

Attachment 10972

Thanks

Gary



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 9:43 AM..
Reply With Quote
  #2  
Old 4/21/07, 5:46 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Quote:
Originally Posted by nbhi
I would think that this wire that is feeding the hot water tank needs to have armor cable? This would help to prevent any damage to the wire, this tank is in the garage.

Attachment 10972

Thanks

Gary
I would write it up.

Also, if its in the garage it needs to be protected from vehicle impact.
Reply With Quote
  #3  
Old 4/21/07, 6:04 PM
mporras mporras is offline
Active Poster
 
Join Date: Mar 2005
Location: Edmond, OK
Posts: 183
Please Note: mporras is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Quote:
Originally Posted by nbhi
I would think that this wire that is feeding the hot water tank needs to have armor cable? This would help to prevent any damage to the wire, this tank is in the garage.

Attachment 10972

Thanks

Gary
...and a disconnect.
Reply With Quote
  #4  
Old 4/21/07, 8:28 PM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default Re: Hot water elec.

Jason

That same theory about vehicle impact, that would also be for the furnace?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #5  
Old 4/21/07, 9:39 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Quote:
Originally Posted by nbhi
Jason

That same theory about vehicle impact, that would also be for the furnace?
Yep, check out IRC 1307.3.1

Also if the furnace is fuel burning it has to be raised above the floor at least 18".

Jason
Reply With Quote
  #6  
Old 4/21/07, 10:18 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Hot water elec.

Electric water heaters need raised 18" above the floor in garages too. The thermostat creates a tiny spark on closing.
Reply With Quote
  #7  
Old 4/22/07, 1:00 AM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Hot water elec.

Anyone flag that for electric water heat that cable might be undersized?

Looks like a 12/2 when I typcially run a 10/2.

tom
Reply With Quote
  #8  
Old 4/22/07, 1:05 AM
hmiller's Avatar
hmiller hmiller is offline
Active Poster
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 668
Please Note: hmiller is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Quote:
Originally Posted by rromoser
Electric water heaters need raised 18" above the floor in garages too. The thermostat creates a tiny spark on closing.
Is there a code reference for that?
Electric water heaters are never installed 18" above the garage floor here, just gas. (not that I ever recall seeing)
Besides the electrical components are at least 18" up the side of the tank, maybe even more. Unlike a gas tank that has a burner and pilot at the bottom.

Agreed on the 12-2 cable....wonder what the breaker is? ...Usually these are 30 amp with 10-2 cable.
Reply With Quote
  #9  
Old 4/22/07, 1:16 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Some AHJ dont require protection on the cable. My area new homes are installed this way every day. Check with your AHJ or recommend it be improved for protection purposes.
Reply With Quote
  #10  
Old 4/23/07, 9:31 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

I think that an NM cable whip to a water heater will last to a very old age and never be damaged. The issue of what is "subject to physical damage" is very... well, subjective. I most often do the water heater whips in MC cable, but you'd be hard pressed to find any code text or any anecdotal evidence of any water heater NM cable whips that are or have ever created a hazard. It can never be stated enough times... just because NM cable is exposed, does not necessarily mean that it's exposed to physical damage.
Reply With Quote
  #11  
Old 4/23/07, 11:41 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Hot water elec.

Quote:
Originally Posted by Jason1
Yep, check out IRC 1307.3.1

Also if the furnace is fuel burning it has to be raised above the floor at least 18".
You referenced 1307.3.1 in regards to providing impact protection to an electric water heater.

The way I read 1307.3.1 is that it is a sub-paragraph of 1307.3 titled "Elevation of ignition source".

Would you consider an electric water heater to have an ignition source such that striking it with an automobile creates a specific fire hazard? How is striking an electric water heater any different from striking a central vacuum?

I would not write it up.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 4/23/07, 11:52 PM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Quote:
Originally Posted by jfunderburk
You referenced 1307.3.1 in regards to providing impact protection to an electric water heater.

The way I read 1307.3.1 is that it is a sub-paragraph of 1307.3 titled "Elevation of ignition source".

Would you consider an electric water heater to have an ignition source such that striking it with an automobile creates a specific fire hazard? How is striking an electric water heater any different from striking a central vacuum?

I would not write it up.
Good point, but in this case he has a gas furnace beside it - so it is all good.

Regardless, if it was my house and knowing my wife, I would put a guard in front of it as I can only afford to replace the water heater once every 10-15 years
Reply With Quote
  #13  
Old 4/24/07, 12:07 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,222
Default Re: Hot water elec.

Looks like the flex line on the left is crushed.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #14  
Old 4/27/07, 3:51 AM
Randy L. Thomas Randy L. Thomas is offline
New User
 
Join Date: Mar 2007
Location: Oregon
Posts: 11
Please Note: Randy L. Thomas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Mosy AHJ's nowdays allow water heaters with the FVIR feature to be installed directly on the garage floor. The 18" rule is in the codebook and likely always will be because there are still older water heaters out there being installed in new homes. Best to check with your local AHJ, but that's what the FVIR feature was designed for. I'm seeing about 50/50 on new homes still being put on 18" platforms. As word gets out, more and more contractors are opting to just set 'em on the floor.

As for impact barriers, they are there to protect the appliances, gas or electric does not matter.
Reply With Quote
  #15  
Old 4/27/07, 9:58 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water elec.

Agreed on the 12-2 cable....wonder what the breaker is? ...Usually these are 30 amp with 10-2 cable.

If this is a nominal 40 gal Imperial (48 gal US, 175 liter) tank with 3000 watt elements, then a 12-2 cable protected by a 20 amp breaker is proper. If it's that size tank with 10-2 wire ....OK, but still the breaker should be downsized to protect the tank wiring which is designed to carry the 12.5 amps that the 3000 watt elements draw!

10-2 wire with a 30 amp breaker is used for a nominal 60 gal Imperial (270 liters, 72 gal US) tank with 4500 watt elements in Canada.

Note: Some conversions are approximates but the wattages and liters are standard spec plate ratings here. Also, I don't know what your standard electric hot water tank volumes and element sizes are but I have seen Rheem and other US brands sold here with similar to above ratings.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
Need Help On Chimney Liners Nick Scibetta Exterior 10 1/11/06 10:53 PM


All times are GMT -4. The time now is 1:03 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts