Default House A/C Question

I have been having issues with my outside compressor tripping the inside breaker. This does not happen frequently (No pattern noticed) but will trip at odd times. After reading some previous comments I think I resolved my issue. I looked at the outside unit and found out the maximum breaker should be 45A. What I need to know would it be OK to use a 50A until I can locate a 45A breaker. I have looked @ our locate Home Depot and Lowes Centers and have not located a 45A breaker, I have been using a 40A but the issue still occurs.
Reply With Quote
Find an InterNACHI certified North Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 8/4/09, 10:42 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: House A/C Question

Quote:
Originally Posted by Eddie Tejada View Post
I have been having issues with my outside compressor tripping the inside breaker. This does not happen frequently (No pattern noticed) but will trip at odd times. After reading some previous comments I think I resolved my issue. I looked at the outside unit and found out the maximum breaker should be 45A. What I need to know would it be OK to use a 50A until I can locate a 45A breaker. I have looked @ our locate Home Depot and Lowes Centers and have not located a 45A breaker, I have been using a 40A but the issue still occurs.
It is probably better to find out what is causing the overcurrent.

Is it an older unit?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 8/4/09, 10:58 AM
Eddie Tejada Eddie Tejada is offline
New User
 
Join Date: Aug 2009
Posts: 4
Please Note: Eddie Tejada is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: House A/C Question

It is a new system about 2 years old. The original Breaker was left in which was a 30A. I switched to a 40A last year. I have determined that the breaker trips at start-up. The outside temp does not normally determine if breaker will trip or not and inside conditions are never the same(i.e. House load,lights,stove...etc) It only trips during the day never at night, when we are at home or when house is empty.
Reply With Quote
  #4  
Old 8/4/09, 11:08 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: House A/C Question

You do not want to get involved in a situation where you're putting in a bigger fuse on a problem circuit. You just turn the wire in the house into a fuse and burn the house down.

A 50 amp breaker is not significantly larger than a 45 amp breaker, so I would venture to guess that you will be okay. If I were there doing it and checked out other conditions of the equipment I would feel safer doing this. I do not recommend you do it.

The circuit breaker is there to protect the wire traveling downstream from the breaker. It may or may not have anything to do with the equipment rating. If your wire to the equipment is not rated for 50 amps, you should not have a 50 amp breaker installed.

Also, circuit breakers are rated for HVAC use. If you install a breaker that is not rated for this service, the inductive load at startup may trip the circuit breaker prematurely causing this nuisance condition.

It says on the breaker if it's rated for HVAC use.

Are the circuit breakers at the big-box store the same breakers required for your service panel? Just because they fit, does not make them okay.

If the tripping breaker is related to equipment load, there should be a pattern. A weather pattern. The HVAC equipment will not max out (even close) to rated capacity until it gets above 100°F.

You really need to get some amperage measurements taken before you consider this problem solved. If you exceed the equipment nameplate ratings it is because the components are wearing out and about to fail.

I highly recommend you get a competent HVAC repair man to fully evaluate the equipment. You could have defective components that are causing an imbalance load to the compressor and causing excessive amperage draw. A $70 compressor contactor failure may result in a $1200 compressor failure.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 8/4/09, 11:15 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: House A/C Question

Quote:
Originally Posted by Eddie Tejada View Post
It is a new system about 2 years old. The original Breaker was left in which was a 30A. I switched to a 40A last year. I have determined that the breaker trips at start-up. The outside temp does not normally determine if breaker will trip or not and inside conditions are never the same(i.e. House load,lights,stove...etc) It only trips during the day never at night, when we are at home or when house is empty.

David's info below (my bold and underline) may be helpful. But, have it checked out by someone qualified.


Quote:
Originally Posted by dandersen View Post
You do not want to get involved in a situation where you're putting in a bigger fuse on a problem circuit. You just turn the wire in the house into a fuse and burn the house down.

A 50 amp breaker is not significantly larger than a 45 amp breaker, so I would venture to guess that you will be okay. If I were there doing it and checked out other conditions of the equipment I would feel safer doing this. I do not recommend you do it.

The circuit breaker is there to protect the wire traveling downstream from the breaker. It may or may not have anything to do with the equipment rating. If your wire to the equipment is not rated for 50 amps, you should not have a 50 amp breaker installed.

Also, circuit breakers are rated for HVAC use. If you install a breaker that is not rated for this service, the inductive load at startup may trip the circuit breaker prematurely causing this nuisance condition.

It says on the breaker if it's rated for HVAC use.

Are the circuit breakers at the big-box store the same breakers required for your service panel? Just because they fit, does not make them okay.

If the tripping breaker is related to equipment load, there should be a pattern. A weather pattern. The HVAC equipment will not max out (even close) to rated capacity until it gets above 100°F.

You really need to get some amperage measurements taken before you consider this problem solved. If you exceed the equipment nameplate ratings it is because the components are wearing out and about to fail.

I highly recommend you get a competent HVAC repair man to fully evaluate the equipment. You could have defective components that are causing an imbalance load to the compressor and causing excessive amperage draw. A $70 compressor contactor failure may result in a $1200 compressor failure.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 8/4/09 at 12:20 PM..
Reply With Quote
  #6  
Old 8/4/09, 11:38 AM
Eddie Tejada Eddie Tejada is offline
New User
 
Join Date: Aug 2009
Posts: 4
Please Note: Eddie Tejada is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: House A/C Question

I personally not aware there was one specific for A/C use. This may be my problem all along. I will double check and see if the breaker is rated for A/C use. The individual who installed the unit did do a load test but could not duplicate the issue while he was hear. He was the one who told me to get the 40A breaker but did not tell me to verify it was rated for A/C
Reply With Quote
  #7  
Old 8/4/09, 11:40 AM
Eddie Tejada Eddie Tejada is offline
New User
 
Join Date: Aug 2009
Posts: 4
Please Note: Eddie Tejada is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: House A/C Question

We do live in Texas and it is always close to 100 this time of year, which come to think of it, the problem only occurs June through August, now that you mention temp.
Reply With Quote
  #8  
Old 8/4/09, 11:56 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,172
Default Re: House A/C Question

Quote:
Originally Posted by Eddie Tejada View Post
I looked at the outside unit and found out the maximum breaker should be 45A. What I need to know would it be OK to use a 50A until I can locate a 45A breaker.
Quote:
Originally Posted by Eddie Tejada
The original Breaker was left in which was a 30A. I switched to a 40A last year.
Are you an electrician? Do you have the knowledge to determine if the circuit is rated for a 45Amp breaker? Just because the system is rated for a 45A, does not mean that the circuit can handle the extra amps. There may be a very good reason why the 30Amp was left in. Call in an electrician, as well as the HVAC guy.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Houses for Sale Stand Vacant jburkeson1 Miscellaneous Discussion for Inspectors 2 1/21/07 8:09 PM
Family's house is infested with mold rspriggs Ancillary Inspection Services & Additional Topics 6 1/28/06 2:05 AM


All times are GMT -4. The time now is 5:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts