Is there a rule of thumb to determine the amount of BTU's a heat pump system equipped with a couple of emergency heating coils should produce? Is the rated amount encoded in the units model #? I have yet to see it spelled out on any mfg. info. tag(s). When I kick in the emergency heat on the thermostat, the electric heating coils each draw around 40 amps., but I don't have any idea how many BTU's are being generated. Thanks in advance for any help.
|
|
#2
|
||||
|
||||
|
I'm no expert on electric heating. Usually electric heat is measured in Kilowatts. I think it is somewhere between 3500 and 4000 btu's per Kilowatt. Let me know if the Kilowatt rating is labeled.
Sincerely, Charles M. Bellefontaine Bellman Group, Inc. 877-316-0600 Extension #802 Click Here to Join our Email Newsletter Get Illinois Home Inspector Pre-License Education and Continuing Education at www.bellmangroup.com |
|
#3
|
||||
|
||||
|
Charles is correct--electric furnaces don't BTU, they KW.
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#4
|
||||
|
||||
|
Amps X Volts = Watts
Watts X 3.413 = BTU/Hr As a side note; HEAT PUMPS are sized for the Air conditioning load and not the heat load, otherwise the air conditioner will be oversized and that's another whole story. |
|
#5
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.