Has anyone ever come across this? At today's inspection I ran the Heat Pump in "heat mode" for about 20 minutes before I noticed ice build-up on the exterior condension unit.

I know this happens in the cooling mode as a result of low refrigerant, but what about in the heating mode?

Kevin
Attached Thumbnails
ice-build-up-censing-unit-heat-mode-cimg3792.jpg  
Reply With Quote
  #2  
Old 11/10/07, 7:27 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Ice Build-up on Censing unit (Heat Mode)

Hi Kevin, heat pumps are not my forte but a google search brought this.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 11/11/07, 12:01 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Ice Build-up on Censing unit (Heat Mode)

I
Quote:
know this happens in the cooling mode as a result of low refrigerant, but what about in the heating mode?
Kevin ice will form on a heat pump not uncommon that is why the have a defrost cycle but in a 20 min period of time you have a problem. What was the outside ambient at the time of inspection.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 11/11/07, 12:45 AM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: Ice Build-up on Censing unit (Heat Mode)

Quote:
Originally Posted by cbottger
I

Kevin ice will form on a heat pump not uncommon that is why the have a defrost cycle but in a 20 min period of time you have a problem. What was the outside ambient at the time of inspection.
Low 50's.

Kevin
Reply With Quote
  #5  
Old 11/11/07, 8:40 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Ice Build-up on Censing unit (Heat Mode)

Hi Kevin,

That is a fairly high temperature for the outside coil to be freezing up, especially as it was only on for 20 mins, remember as well that the ammount of frosting will also depend on the ammount of humidity in the outside air.

The exterior coil in heat mode will always freeze up when run at low temps with high humidity, and is designed to go into defrost mode automatically every hour.

That one of yours probably is low on refridgerant, as it is freezing up to fast and at too high a temp I would recommend that the system be serviced

BTW for comparison my 4 year old outside coil down here in the humidity capital of the world seldom freezes up unless the outside air temp gets around the low 40's with higher humidity.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #6  
Old 11/11/07, 9:06 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Ice Build-up on Censing unit (Heat Mode)

Quote:
Originally Posted by krichardson
Low 50's.

Kevin
Kevin with the outside ambient being in the low 50's that is the ideal temp for a heat pump to operate in for testing purposes. Hot gas vapor being discharged to the indoor A-coil condensing to a warm liquid being sent back to the outdoor unit which is acting as the A-coil complete with its own expansion valve. With a properly charged unit with expansion valve operating properly I would not want to see any ice on the outside unit with the ambient being in the 50's. I would write that unit up as not performing its intended function.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 11/11/07, 9:12 AM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: Ice Build-up on Censing unit (Heat Mode)

Thanks for all the replies, they were very helpful. NACHI members are the best!!

I think I will spend some time today "brushing up" on Heat Pumps

Kevin
Reply With Quote
  #8  
Old 11/11/07, 9:13 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Ice Build-up on Censing unit (Heat Mode)

Quote:
Originally Posted by gbeaumont
Hi Kevin,

That is a fairly high temperature for the outside coil to be freezing up, especially as it was only on for 20 mins, remember as well that the ammount of frosting will also depend on the ammount of humidity in the outside air.

The exterior coil in heat mode will always freeze up when run at low temps with high humidity, and is designed to go into defrost mode automatically every hour.

That one of yours probably is low on refridgerant, as it is freezing up to fast and at too high a temp I would recommend that the system be serviced

BTW for comparison my 4 year old outside coil down here in the humidity capital of the world seldom freezes up unless the outside air temp gets around the low 40's with higher humidity.

Regards

Gerry
Cool Gerry you slipped in here while I was thinking about what to say trying to keep it simple to understand



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 11/11/07, 9:59 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Ice Build-up on Censing unit (Heat Mode)

Quote:
Originally Posted by cbottger
Cool Gerry you slipped in here while I was thinking about what to say trying to keep it simple to understand
Hi Charlie, it's the "keeping it simple" bit thats hard, as we all know a heat pump system is witchcraft . Of all the subjects that I teach Heat Pumps are the most confusing to most people

Lets get it right AC systems and Heat pumps just shouldn't work at all based on what most people understand about boiling points and evaporation

Quote:
"Heat Pump appears to be freezing up, we recommend organizing a black mass with chicken entrails to further diagnose the problem"
Regards

Confused of Clearwater



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #10  
Old 11/11/07, 10:18 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Ice Build-up on Censing unit (Heat Mode)

Quote:
. Of all the subjects that I teach Heat Pumps are the most confusing to most people
I would agree once worked with a guy that spent two
years in a vo tech for HVAC and was unable to wire his first thermostat for a heat pump. He could not do the work so later on they made him a boss????



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 11/11/07, 11:57 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ice Build-up on Censing unit (Heat Mode)

The other possiblity is that the system had the condensing unit replaced without replacing the evaporator. Mismatched systems is getting to be a problem with companies that want to sell that unit without regards to system operation in both modes. At least when 2010 gets here with R22 phaseout this problem should be reduced.


If anyone is interested I can e-mail a pdf file of a test report that Bristol Compressors made on mismatched systems. Just e-mail me at mechacc at essex1.com subject: Mismatch System

If anyone can tell me how to upload a pdf file on this forum I can do that as well.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radiant ceiling heat? bmargiotti Inspecting HVAC Systems 16 1/24/12 10:46 AM
Radiant Ceiling Heat hhull Interior Inspections 9 7/26/07 8:19 AM
Heat Pump Inspection cyezza Inspecting HVAC Systems 18 1/10/07 9:19 PM
Radiant Heat Transfer rmyers1 Structural Inspections 0 5/31/06 11:21 PM


All times are GMT -4. The time now is 11:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts