Rheem Heat Pump. When the evaporater coil was viewed significant condensate was dripping down into the plemun and the lower coils were icing. Temperature splite was 14 degrees. What would cause the icing. Thanks, need answer soon, report due out.
|
|
#2
|
||||
|
||||
|
Condensation on the coil is normal, but if the evaporator coil has ice accumulation, it is caused by either the temperature being too cold (below 65°F inside OR out) or poor air flow through the unit itself. Maybe the fan is slipping on the motors shaft.
Last edited by dvalley; 4/2/08 at 5:44 PM.. |
|
#3
|
||||
|
||||
|
Three biggest causes are the evaporator coil is too dirty to let air pass through, filter is too dirty, or the system is undercharged. Those are the first things I check when I see ice buildup. There are other causes, but these are the most common you will find.
Scott Gilligan 215-888-4943 Infraspection Institute Level III Certified Thermographer Philadelphia Mold Inspections Philadelphia Home Inspections Philadelphia Commercial Inspections Philadelphia Licensed Home Inspector Pennsylvania - New Jersey - Delaware Infrared Thermal Imaging Inspections President The Greater Philadelphia Chapter of InterNACHI http://pa.nachi.org/greaterphiladelphia Vice President & Webmaster National Association of Commercial Building Inspectors and Thermographers |
|
#4
|
|||
|
|||
|
The condesate drain line is open and draining, there is just a lot of condensate dripping down from the coils and like I said the lower two inches of the coils are icing over. Thanks
|
|
#5
|
|||
|
|||
|
Dave is right but add to the list low on Freon - I was told this by used home sales person and that the seller would have the unit serviced so I need not put it on the report.
I was also told that I should not run the unit as long as I did since the problem does not show up during normal operation (How did this person know all this??) rlb |
|
#6
|
|||
|
|||
|
What do you think about the temp. split at 14 degrees along with the dripping and icing. Thanks
|
|
#7
|
||||
|
||||
|
Quote:
I like to see a 12-15 degree differential. If this particular unit makes you nervous, simply recommend service and maintenance before close of escrow. |
|
#8
|
|||
|
|||
|
Thanks everyone for your comments but I'm still wondering why there is an excess of condensate dripage from the coil.
|
|
#9
|
||||
|
||||
|
Been answered but again the unit is not functioning properly due to the 3 conditions noted by others or very hot upon entry or high levels of interior humidity
Here is the basic breakdown I use (ripped off) and in all cases: Seasonal equipment service is recommended it's that time of year 12ºF~14ºF or less- inadequate to marginal operation advise servicing unit(s) immediately to identify problem 15~16ºF – minimally acceptable 17~18ºF - good operation 19~20ºF - very adequate operation 21~22ºF - slightly excessive differential 23ºF or above - excessive differential advise servicing unit(s) to identify problem ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good Last edited by badair; 4/2/08 at 6:49 PM.. |
|
#10
|
||||
|
||||
|
Quote:
This unit needs to be deferred to a HVAC contractor for repair it is not performing as intended by the MFG. Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Explaining MultiWire Circuits- For Fun :) | pabernathy | Electrical Inspections | 38 | 11/8/06 6:04 PM |
| HVAC reclaim coil liquid contents | mcyr | Inspecting HVAC Systems | 0 | 6/29/06 7:01 PM |
| Question on my heat pump | dbush | Inspecting HVAC Systems | 7 | 3/12/06 12:15 AM |
| Evaporator Coil Question | jfunderburk | Inspecting HVAC Systems | 17 | 1/18/06 1:13 AM |