  #1  
Old 4/2/08, 5:36 PM
Mike Pettitt Mike Pettitt is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Crystal River, FL
Posts: 75
Default Ice on evaporater coil

Rheem Heat Pump. When the evaporater coil was viewed significant condensate was dripping down into the plemun and the lower coils were icing. Temperature splite was 14 degrees. What would cause the icing. Thanks, need answer soon, report due out.
Reply With Quote
  #2  
Old 4/2/08, 5:41 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Ice on evaporater coil

Condensation on the coil is normal, but if the evaporator coil has ice accumulation, it is caused by either the temperature being too cold (below 65°F inside OR out) or poor air flow through the unit itself. Maybe the fan is slipping on the motors shaft.

Last edited by dvalley; 4/2/08 at 5:44 PM..
Reply With Quote
  #3  
Old 4/2/08, 5:52 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Ice on evaporater coil

Three biggest causes are the evaporator coil is too dirty to let air pass through, filter is too dirty, or the system is undercharged. Those are the first things I check when I see ice buildup. There are other causes, but these are the most common you will find.
Reply With Quote
  #4  
Old 4/2/08, 5:52 PM
Mike Pettitt Mike Pettitt is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Crystal River, FL
Posts: 75
Default Re: Ice on evaporater coil

The condesate drain line is open and draining, there is just a lot of condensate dripping down from the coils and like I said the lower two inches of the coils are icing over. Thanks
Reply With Quote
  #5  
Old 4/2/08, 5:55 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Ice on evaporater coil

Dave is right but add to the list low on Freon - I was told this by used home sales person and that the seller would have the unit serviced so I need not put it on the report.

I was also told that I should not run the unit as long as I did since the problem does not show up during normal operation

(How did this person know all this??)

rlb
Reply With Quote
  #6  
Old 4/2/08, 5:59 PM
Mike Pettitt Mike Pettitt is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Crystal River, FL
Posts: 75
Default Re: Ice on evaporater coil

What do you think about the temp. split at 14 degrees along with the dripping and icing. Thanks
Reply With Quote
  #7  
Old 4/2/08, 6:01 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Ice on evaporater coil

Quote:
Originally Posted by mpettitt
What do you think about the temp. split at 14 degrees along with the dripping and icing. Thanks
14 degrees sounds good to me.

I like to see a 12-15 degree differential.

If this particular unit makes you nervous, simply recommend service and maintenance before close of escrow.
Reply With Quote
  #8  
Old 4/2/08, 6:34 PM
Mike Pettitt Mike Pettitt is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Crystal River, FL
Posts: 75
Default Re: Ice on evaporater coil

Thanks everyone for your comments but I'm still wondering why there is an excess of condensate dripage from the coil.
Reply With Quote
  #9  
Old 4/2/08, 6:43 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Ice on evaporater coil

Been answered but again the unit is not functioning properly due to the 3 conditions noted by others or very hot upon entry or high levels of interior humidity

Here is the basic breakdown I use (ripped off) and in all cases:

Seasonal equipment service is recommended it's that time of year


12ºF~14ºF or less- inadequate to marginal operation advise servicing unit(s) immediately to identify problem
15~16ºF – minimally acceptable

17~18ºF - good operation
19~20ºF - very adequate operation
21~22ºF - slightly excessive differential
23ºF or above - excessive differential advise servicing unit(s) to identify problem



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 4/2/08 at 6:49 PM..
Reply With Quote
  #10  
Old 4/2/08, 8:18 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Ice on evaporater coil

Quote:
Originally Posted by mpettitt
Thanks everyone for your comments but I'm still wondering why there is an excess of condensate dripage from the coil.
Any time you have ice on the A-coil on a residential A/C unit there is a problem. The excess condensate you are referring to is created by the edge of the ice trying to melt and simply dripping from the edge of the ice and not traveling down the fins of the coil as intended. Also if there is any lint build up this will also cause the condensate not to travel down the fins to the drain pan.

This unit needs to be deferred to a HVAC contractor for repair it is not performing as intended by the MFG.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Explaining MultiWire Circuits- For Fun :) pabernathy Electrical Inspections 38 11/8/06 6:04 PM
HVAC reclaim coil liquid contents mcyr Inspecting HVAC Systems 0 6/29/06 7:01 PM
Question on my heat pump dbush Inspecting HVAC Systems 7 3/12/06 12:15 AM
Evaporator Coil Question jfunderburk Inspecting HVAC Systems 17 1/18/06 1:13 AM


All times are GMT -4. The time now is 11:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts