Identification help please

The label on this unit didn’t state the manufacture… Can you help with: Make, BTU & Age?

Electric Furnace
M: ARUF042-00A-1A
S: 0408159457

PS. This was supposedly installed the same time as the Goodman AC unit in 2004.

Hi Mark

here you go:

http://villa-villekulla.com/villa/cut-sheets/Goodman%20Air%20Handler%20Specs.pdf

serial # supports it being an 04

Regards

Gerry

48,000 btu goodman electric furnace. manuf. aug '04

Thanks Gerry, I just printed this to add to my notes.

Thanks Mark,
How did you figure the 48,000 btu number?

It’s actually a 3.5 ton unit (from the 42)

Ok… Here’s the update… 66 degrees outside. The output temp on the unit is 59 degrees, and the return is only 66 degrees : 7 degrees difference.

The seller is there an very nicely explains that that particular unit won’t kick on if the outside temp is less than 70 degrees. He said that he had the owners manual and it documents that. But I didn’t get to see it.

What say you? Is he full of it, or is this reasonable. (BTW, by his countenance, I believe that he believes what he is telling me is the truth. So I don’t think he’s lying, but I don’t know if he is correct or not.)

Yes, there are low ambient thermostats that will prevent the operation of the cooling equipment when the temperature is below a certain setpoint. They are field-installed in the outdoor unit. It would be unusual for the setting to be 70 degrees, but it certainly could be set there.

As a home inspector, you’re sorta stuck. Is the homeowner lying to you, and the system has a problem, or is he right? What do you do in that case? Did you confirm that the outdoor unit was indeed not running when you observed this low delta-T?

I would document what the owner said in the report and move on.

No I was talking to the guy after the fact, and didn’t re-check it.

Yea that’s kind of where I’m at. I was just hoping that someone could jump in and say that this is what this model is designed for…

The seller was a very old gentleman, who had been forced to give up his home because of health reasons. It’s very possible that he misunderstood or didn’t remember the details well.

I would have to think the elderly gentleman was confused If the outdoor unit was locked out on a stat the indoor blower would not have been operating either you stated 66 degrees outside ambient how did you get any delta T if the unit was not operating.

From inside the home, when I took the delta T, it appeared to me that everything was operating. It was blowing at 59 degrees. So I’m thinking he was confused. Like I said, I didn’t think to re-check it and go outside to see if it was running too.

It would not have been 59 degrees if the unit was not operating it would have been the same as the return or the temp within the home

[FONT=TrebuchetMS-Bold][size=1][FONT=TrebuchetMS-Bold][size=1]Model
Nominal
Cooling
Capacity
(BTUH)
Voltage
CFM
@ 0.3” ESP
High/Low
Electric Heat
Capacity (kW)
Dimensions
W x D x H
Service Valve Shipping
Weight
Liquid Suction (pounds
[/size][/FONT][/size][/FONT][FONT=TrebuchetMS][size=1][FONT=TrebuchetMS][size=1]
ARUF042-00A-1A 42,000 208/240 1,470/1,420 3, 5, 6, 8, 10, 15, 20 19½” x 22” x 46¾” 3/8” 3/4” 144
ARUF048-00A-1A 48,000 208/240 1,530/1,470 3, 5, 6, 8, 10, 15, 20 22” x 24” x 53¼” 3/8” 3/4” 173
ARUF049-00A-1A 48,000 208/240 1,530/1,470 3, 5, 6, 8, 10, 15, 20 22” x 24” x 53¼” 3/8” 7/8” 173
ARUF060-00A-1A 60,000 208/240 2,000/1,780 3, 5, 6, 8, 10, 15, 20 22” x 24” x 53¼” 3/8” 7/8” 192
ARUF061-00A-1A 60,000 208/240 2,000/1,780 3, 5, 6, 8, 10, 15, 20 22” x 24” x 53¼” 3/8” 7/8” 192
[/size][/FONT][/size][/FONT][FONT=GoudyOldStyleBT-Roman][size=3][FONT=GoudyOldStyleBT-Roman][size=3]The Goodman[/size][/FONT][/size][/FONT][FONT=GoudyOldStyleBT-Roman][size=1][FONT=GoudyOldStyleBT-Roman][size=1]® [/size][/FONT][/size][/FONT][FONT=GoudyOldStyleBT-Roman][size=3][FONT=GoudyOldStyleBT-Roman][size=3]ARUF[/size][/FONT][/size][/FONT][FONT=GoudyOldStyleBT-Roman][size=3][FONT=GoudyOldStyleBT-Roman][size=3]