When inspecting air handlers I am finding more and more unused condensation drain outlets are not plugged. I report it as a concern. Is this a legitimate concern and if so, why.
Reply With Quote
  #2  
Old 7/19/07, 6:14 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Improper installation

I have never seen them completely unplugged but I have seen the plugs half in/half out. Even with them half in, there is a considerable amount of conditioned air being blown through it. I push them back in and move on but I would say it was a concern because of that reason. Same goes for trapless lines that have conditioned air blown out of the pvc vent for the line. What do you guys say to this?
Reply With Quote
  #3  
Old 7/19/07, 6:35 PM
Robert Robson Robert Robson is offline
New User
 
Join Date: Aug 2005
Posts: 4
Please Note: Robert Robson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Improper installation

I feel they should caped after installation because they let unfiltered air into the system as well as insects and rodents. The installers are just lazy.
Reply With Quote
  #4  
Old 7/20/07, 8:50 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Improper installation

Quote:
Originally Posted by Robert Robson
I feel they should caped after installation because they let unfiltered air into the system as well as insects and rodents. The installers are just lazy.
There are two types of drains. Positive pressure, where evaporator coil is on discharge side of the blower; and negative pressure where the coil is located on the inlet side of the blower. Negative pressure drains must be trapped to allow proper draining of the water. In addition a vented tee assembly must be installed at the outlet of the trap. This prevents air trapping of the water in the drain line by breaking the negative pressure after the trap. Capping such a tee could result in back up of water. A better solution if it is deemed necessary would be to screen the opening to prevent insect entry.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about improper installation cbell1 Exterior Inspections 3 10/24/07 9:13 PM
Pull Down Staircase Installation nwagner Interior Inspections 11 7/27/07 10:32 PM
Bonding wire installation requirements ?? rnewman1 Electrical Inspections 7 7/31/06 2:31 PM
Window installation jmichalski Exterior Inspections 17 1/24/06 9:42 PM
Common Installation Deficiencies jkline Electrical Inspections 0 1/12/06 8:58 AM


All times are GMT -4. The time now is 11:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts