#1
|
||||
|
||||
|
When inspecting A/C duct work on a upflow furnace with the ducts in the attic what do you look for.
|
|
#2
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Google the air difussion coucil. They have some really good information there.
|
|
#3
|
||||
|
||||
|
Last edited by dvalley; 10/7/07 at 5:42 PM.. |
|
#4
|
||||
|
||||
|
Quote:
What do you as an inspector look for as a discrepancy in the duct work that would end up on the repair list of your report. |
|
#5
|
|||
|
|||
|
Attic ducts, at least around here, are flex ducts. I check for separations, tears on the protective (plastic) covering, type of duct (some brands are very flimsy and are not well insulated), flattened areas (some tradesmen will lay on the duct for protection from fiberglass insulation), kinks, excessive length of supply ducts...
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
|||
|
|||
|
I don't care for flexduct anywhere, especially in a crawlspace. Because of the difficulty in working in crawls, installers are usually in a hurry to get it done and get out of there. That leads to some poor workmanship.
Attic and crawlspace installations are also very susceptable to attack by wildlife. Squirrels, rats, foxes, cats, dogs, rackety-coons and other critters can do a number on flexduct. Who monitors these places?? Nobody ever checks to see how things are going under the house. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#8
|
||||
|
||||
|
Charley,
If the duct work is in tact and the insulation is not exposed and (as Jae already mentioned) not kinked, separated or torn, then that pretty much covers your duct inspection. |
|
#9
|
||||
|
||||
|
Quote:
I might interject a couple of thoughts of my own that I do with flex duct. I do a visual check at the plenum and the Wye's to see if the plastic banding straps were used I refer to this as my quality check as Jae stated other trades will abuse the duct and if bands were not used as they should be this duct will separate. I simply view the overall installation of the duct and if no pride was used in craftmanship with the duct the remaining install is probally the same way. It just kind of gives me a heads up to be watchful in other areas. |
|
#10
|
||||
|
||||
|
Look for stuff like this
Last edited by dedwards; 5/3/07 at 6:34 PM.. |
|
#11
|
||||
|
||||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Did work before I confirmed, probably not getting paid, what now?? | Ashli Norton | General Inspection Discussion | 7 | 8/8/07 8:53 AM |
| furnace return air duct | vwood | Inspecting HVAC Systems | 5 | 6/19/07 2:18 PM |
| Free! NACHI Chapter Electrical Inspection Seminars | jtedesco1 | Inspection Education & Training | 0 | 10/2/06 5:40 PM |
| The duct tape guys | dmacy | Inspecting HVAC Systems | 13 | 3/20/06 3:53 AM |