Default Insufficient Return Air??

Does this install allow sufficient return air? This is the only return on a zoned system with the filter right at the top of the stairwell.



I seem to recall about 180 sq inches needed for a 3 ton unit.

The install itself is ugly... and yes it's New Construction.
Attached Thumbnails
insufficient-return-air-2415-thoreau-083.jpg   insufficient-return-air-2415-thoreau-086.jpg   insufficient-return-air-2415-thoreau-085.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 9/26/07, 6:20 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Insufficient Return Air??

That sucks,or should I say it doesn't.
Your right it is not enough.
Got a 7pm and hope it is better than that.
I assume from your comment this is at least a two story job.
Reply With Quote
  #3  
Old 9/26/07, 6:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insufficient Return Air??

The workmanship is poor, at least. Looks like the person doesn't know how to squeegee down their tape, and also looks like they used leftover fire alarm cable for the thermostat wiring.
Reply With Quote
  #4  
Old 9/26/07, 7:14 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Insufficient Return Air??

Quote:
Originally Posted by relliott
That sucks,or should I say it doesn't.
Your right it is not enough.
Got a 7pm and hope it is better than that.
I assume from your comment this is at least a two story job.
It's a 1700' ft two story home...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #5  
Old 9/26/07, 8:10 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Insufficient Return Air??

1700sf typically has a 20x25 filter



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 9/26/07, 8:14 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Insufficient Return Air??

This one had a 14x30 filter but only a 14x16 hole in the actual wall for the free air which was then reduced to about 13x9 as it runs under the air handler...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #7  
Old 9/26/07, 8:16 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Insufficient Return Air??

I actually think it would have been better to place a louvered door in the room and simple bottom filter installation...

But's that why I'm asking the HVAC gurus out there.... I'm not one, but I play one on TV...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #8  
Old 9/26/07, 11:47 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Insufficient Return Air??

Nope going to be very noisy and almost guaranteed hot spots



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 9/27/07, 12:11 AM
mbarnett mbarnett is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Lancaster, CA
Posts: 19
Default Re: Insufficient Return Air??

Definatly poor workmanship...I would defer to a contractor for further evaluation.



Michael Barnett C.H.I. #NACHI07081803, HIF#9725A
Barnett's Certified Home Inspections BL#10009708
(661) 816-4123
www.barnetts-inspections.com
mbarnett@ca.nachi.org
www.nachi.org
Reply With Quote
  #10  
Old 9/27/07, 12:25 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Insufficient Return Air??

Quote:
I would defer to a contractor for further evaluation.
Whom do you suppose installed this in the first place me thinks you need to evulate the evaluator.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 9/27/07, 8:54 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Insufficient Return Air??

Is this the only unit for a two story home? Around here, you almost always see two units, even if it is a zoned system. Workmanship, unfortunately, looks a lot like some that was done when my home was built !!



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #12  
Old 9/27/07, 11:22 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Insufficient Return Air??

Forbid they use a micro filter.
Reply With Quote
  #13  
Old 9/28/07, 7:37 PM
Dan G. Happer Dan G. Happer is offline
New User
 
Join Date: Sep 2007
Posts: 1
Please Note: Dan G. Happer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insufficient Return Air??

when sizing duct, most professional HVAC people use the CFM approach which is warrented for each install. i have no idea total length of duct and sizing throughout so I could not say off hand what size return is needed. You really can't judge air flow by duct work. BUT, looking at pics, I can say it is definetly needs to be tidied up and checked by HVAC pros
Dan
Reply With Quote
  #14  
Old 9/29/07, 11:28 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insufficient Return Air??

Quote:
Originally Posted by mgault
Does this install allow sufficient return air? This is the only return on a zoned system with the filter right at the top of the stairwell.



I seem to recall about 180 sq inches needed for a 3 ton unit.

The install itself is ugly... and yes it's New Construction.
Uusally try to design about 400 cfm per ton and return ducts about 20% larger than supply.....so from a local HVAC supplier catalogue "INFO" section:
If all zones were calling for AC together, you would need about 270 sq in for return air.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Return air from crawl space WHI Inspecting HVAC Systems 11 1/9/12 7:43 PM
Critter in the return air duct... swaskewicz Inspecting HVAC Systems 11 11/28/07 3:49 PM
Reduced return air duct mmorgan Inspecting HVAC Systems 4 6/6/07 7:39 PM
strong return? mharrod Inspecting HVAC Systems 14 12/6/06 6:28 PM


All times are GMT -4. The time now is 5:59 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts