What would be the cause of a 7 year old Armstrong mid efficiency furnace with monoport burners & electronic igniter to have intermintent operation?

The furnace would operate, ignite and then after about 2-5 seconds the gas would go off at the burners and then the furnace would try to ignite again?

Thanks
Reply With Quote
  #2  
Old 4/7/07, 4:45 PM
Jeff S. Vogan's Avatar
Jeff S. Vogan Jeff S. Vogan is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Default Re: Intermintent operation

David,
I have seen this once before. After the electronic ignition lights the burner, there is a sensor at the end of the burner that tells the unit that the burner got lit. If that sensor gets "dirty" or is faulty, and does not detect the flame when it is lit, it thinks the burner did not ignite, and is just pumping out gas. As a safety precaution, it will shut the gas to the burner off thinking it isn't lit. Then, it will attempt to re-light it. This cycle will continue over and over and over........
Reply With Quote
  #3  
Old 4/7/07, 4:58 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: Intermintent operation

Quote:
Originally Posted by jvogan
David,
I have seen this once before. After the electronic ignition lights the burner, there is a sensor at the end of the burner that tells the unit that the burner got lit. If that sensor gets "dirty" or is faulty, and does not detect the flame when it is lit, it thinks the burner did not ignite, and is just pumping out gas. As a safety precaution, it will shut the gas to the burner off thinking it isn't lit. Then, it will attempt to re-light it. This cycle will continue over and over and over........
So it just needs a new ignitor? Thanks. I have seen this before and now with your help I can better explain if I happen to have this scenerio again.
Reply With Quote
  #4  
Old 4/7/07, 5:01 PM
Jeff S. Vogan's Avatar
Jeff S. Vogan Jeff S. Vogan is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Default Re: Intermintent operation

Not a new ignitor, the ignitor is lighting the burner. It needs a new flame sensor...a very minor repair by an HVAC guy. Literally takes about 5 minutes to replace...minor costs! Good catch, BTW!
Reply With Quote
  #5  
Old 4/7/07, 5:12 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: Intermintent operation

Quote:
Originally Posted by jvogan
Not a new ignitor, the ignitor is lighting the burner. It needs a new flame sensor...a very minor repair by an HVAC guy. Literally takes about 5 minutes to replace...minor costs! Good catch, BTW!
Thank you very much.

The weather here is brutal. More snow & cold then in the winter. I told my six year old that santa claus is dropping off the eggs and the easter bunny is staying in the ground until it warms up.
Reply With Quote
  #6  
Old 4/7/07, 10:37 PM
cwillick1 cwillick1 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Nanaimo, BC
Posts: 132
Default Re: Intermintent operation

i believe Jeff is correct. i have seen the same thing where the senors eye was covered, in this case not dirt but with a film from burning to rich. how did the flame look?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hours of operation dmacy Misc. Discussion 10 5/14/07 11:58 AM
The AC Equipment is blocking the operation of the switch jtedesco1 HVAC 7 1/4/06 8:20 PM


All times are GMT -4. The time now is 9:58 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts