Default Intermintent operation

What would be the cause of a 7 year old Armstrong mid efficiency furnace with monoport burners & electronic igniter to have intermintent operation?

The furnace would operate, ignite and then after about 2-5 seconds the gas would go off at the burners and then the furnace would try to ignite again?

Thanks
Reply With Quote
  #2  
Old 4/7/07, 3:45 PM
jvogan's Avatar
jvogan jvogan is offline
Active Poster
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Please Note: jvogan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Intermintent operation

David,
I have seen this once before. After the electronic ignition lights the burner, there is a sensor at the end of the burner that tells the unit that the burner got lit. If that sensor gets "dirty" or is faulty, and does not detect the flame when it is lit, it thinks the burner did not ignite, and is just pumping out gas. As a safety precaution, it will shut the gas to the burner off thinking it isn't lit. Then, it will attempt to re-light it. This cycle will continue over and over and over........
Reply With Quote
  #3  
Old 4/7/07, 3:58 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Intermintent operation

Quote:
Originally Posted by jvogan
David,
I have seen this once before. After the electronic ignition lights the burner, there is a sensor at the end of the burner that tells the unit that the burner got lit. If that sensor gets "dirty" or is faulty, and does not detect the flame when it is lit, it thinks the burner did not ignite, and is just pumping out gas. As a safety precaution, it will shut the gas to the burner off thinking it isn't lit. Then, it will attempt to re-light it. This cycle will continue over and over and over........
So it just needs a new ignitor? Thanks. I have seen this before and now with your help I can better explain if I happen to have this scenerio again.
Reply With Quote
  #4  
Old 4/7/07, 4:01 PM
jvogan's Avatar
jvogan jvogan is offline
Active Poster
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Please Note: jvogan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Intermintent operation

Not a new ignitor, the ignitor is lighting the burner. It needs a new flame sensor...a very minor repair by an HVAC guy. Literally takes about 5 minutes to replace...minor costs! Good catch, BTW!
Reply With Quote
  #5  
Old 4/7/07, 4:12 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Intermintent operation

Quote:
Originally Posted by jvogan
Not a new ignitor, the ignitor is lighting the burner. It needs a new flame sensor...a very minor repair by an HVAC guy. Literally takes about 5 minutes to replace...minor costs! Good catch, BTW!
Thank you very much.

The weather here is brutal. More snow & cold then in the winter. I told my six year old that santa claus is dropping off the eggs and the easter bunny is staying in the ground until it warms up.
Reply With Quote
  #6  
Old 4/7/07, 9:37 PM
cwillick1 cwillick1 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Nanaimo, BC
Posts: 132
Default Re: Intermintent operation

i believe Jeff is correct. i have seen the same thing where the senors eye was covered, in this case not dirt but with a film from burning to rich. how did the flame look?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hours of operation dmacy Miscellaneous Discussion for Inspectors 10 5/14/07 10:58 AM
The AC Equipment is blocking the operation of the switch jtedesco1 Inspecting HVAC Systems 7 1/4/06 7:20 PM


All times are GMT -4. The time now is 6:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts