For those of you guys that are really into A/C I want to know how it is significant (worth noting as a defect) if two feet of insulation is damaged or even missing from the soil to the condensing unit on the suction line with respect to the functionality of the system.
| Find an InterNACHI certified Nebraska Home Inspector (and anywhere else in North America) |
None.
The first primary purpose for insulating is to prevent moisture condensation. Due to the location of the damage, this condensation affects nothing. There is a slight loss in efficiency if the suction line is located over a long distance in a very hot location. Condensation is an indication of an efficiency loss of about 970 BTUs per pound of water it produces. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
The insulation is there for a purpose. If it is missing or damaged it should be reported.
Reporting (in licensed states) is required when an issue is a significant defect or a safety concern. I see neither. If you would like to quote the insulation requirements at the outdoor condenser IAW ASHRAE or other published standard that would help. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission Last edited by dandersen; 11/30/09 at 10:49 AM.. |
All line sets come with an insulated suction line. It must serve a purpose. I don't understand why anyone would quote code.
I call out all missing or deteriorated insulation on A/C condenser pressure lines. It doesn't require a HVAC contractor to install this insulation tube. Any DYI'er can install this split insulation tubing in 5-10 minutes. I change mine every two or three years. |
gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is more a mositure issue for me when the insulation is missing inside, outside not so much of an issue at all.
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
No, just inefficient.
Someone post some installation instructions and we will see.
The manufactureres don't insulate the last two feet from the suction service valve to the compressor so I idon't think efficiency is a major concern.
"The refrigerant temperature inside the suction line is generally cooler than surrounding air. Therefore it is always good practice to insulate the entire suction line to prevent loss of capacity due to heat gain.
Also any heat gained by the suction line puts an additional load on the system that reduces cooling capacity and also may result in improper motor cooling with some compressor designs." page 35 Here is a nice 89 page air conditioning clinic from Trane. http://www.scribd.com/doc/15509472/0...ning-Clinicpdf Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
You're wrong! |
| AC suction line | kgrabowski | Inspecting HVAC Systems | 8 | 8/27/09 10:54 PM |
| Suction line bend | lprinzi | Inspecting HVAC Systems | 6 | 2/7/09 1:57 PM |