Default Joined Primary and Secondary and Float switch

Can the secondary (pan drain) be joined in with the primary (obviously not ducted to a 'conspicuous location') if they've also installed a float switch?

All in an air handler in the attic above framing.

I know I'd like to see them separated, but is it okay this way?
Attached Images
File Type: jpg S4020850.JPG (47.2 KB, 64 views)
File Type: jpg S4020848.JPG (45.9 KB, 60 views)



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 9/17/07, 8:31 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 984
Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted
Default Re: Joined Primary and Secondary and Float switch

Bump....


17 views, nothing yet....



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #3  
Old 9/17/07, 8:52 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,516
Brian E. Kelly .
Default Re: Joined Primary and Secondary and Float switch

Are you going to make me search the code book Michael?





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #4  
Old 9/17/07, 8:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,988
Jeffrey R. Pope .
Default Re: Joined Primary and Secondary and Float switch

The float switch essentially negates the necessity for a "conspicuous" secondary. There's nothing more "conspicuous" than your system shutting down



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #5  
Old 9/17/07, 9:11 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 984
Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted
Default Re: Joined Primary and Secondary and Float switch

I know Jeff, I just dislike the heck outta this install.

I've seen other production builders (Centex to be specific) install the pan drain where it exits above a kitchen sink window... now that's conspicuous!

They also have the float switch to disable them as well (I tell people it's really a tertiary safety as you should observe the dripping secondary prior to the float be actuated).

My issue with the float switch in-lieu-of a conspicuous secondary is that it doesn't always "shut off" the system - it'll still 'blow' just not as cool... and the pan is now FULL of water...

Here's another joined I saw today as well in a different builder's town home... through this is easier to 'fix'...
Attached Images
File Type: jpg S4020976.JPG (28.6 KB, 46 views)



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #6  
Old 9/17/07, 9:37 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 984
Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by bkelly2
Are you going to make me search the code book Michael?
No, I know what it says; I'm just looking for someone else to validate my thoughts that this is certainly not (as Big Will says) Best Building Practice...

And maybe some thoughts on how to 'recommend' something different.



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #7  
Old 9/17/07, 9:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,988
Jeffrey R. Pope .
Default Re: Joined Primary and Secondary and Float switch

If your jurisdiction follows the IRC, here's the reference. . .

M1411.3.1 Auxiliary and secondary drain systems.

. . . The auxiliary pan drain shall discharge to a conspicuous point of disposal to alert occupants in the event of a stoppage of the primary drain. . .

Regardless of any float switch or other system.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #8  
Old 9/18/07, 8:26 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 984
Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted
Default Re: Joined Primary and Secondary and Float switch

Thanks Jeff....

I pretty much said it was okay, but not the best possible design... we'll see what we see...


At least I've perfected the double lugged neutral call out!



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #9  
Old 9/19/07, 2:39 PM
Robert J. OConnor, P.E.'s Avatar
Robert J. OConnor, P.E. Robert J. OConnor, P.E. is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 739
Robert J. OConnor, P.E. is often very helpful Robert J. OConnor, P.E. is often very helpful
Default Re: Joined Primary and Secondary and Float switch

You can add a float switch as backup to a separate secondary drain, as long as the secondary drain discharge is to a clearly visible ("conspicuous") location. But there shouldn't be a concealed secondary drain discharge with a float switch.

If the secondary drain discharge is not clearly visible (e.g. both connected together and/or discharging into say a gutter or waste line), and there is a problem with system, nobody will even know there is a problem ... unless the secondary line clogs and the pan fills up to activate the float switch. It might work, but it's not ideal or the way it should be done.

Also note that IRC Section M1411.3.1 states that ... "One of the following methods shall be used" which then continues with the three options of: pan with visible secondary drain; high visible secondary drain; or pan with float switch. A pan with a concealed secondary drain and a float switch isn't one of the options.

JMO



Robert O'Connor, PE
Eagle Engineering & Inspections
Adjunct Professor
NACHI Education Committee
www.reporthost.com/eagleengineering

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #10  
Old 9/19/07, 2:58 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,361
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by roconnor
"One of the following methods shall be used" which then continues with the three options of: pan with visible secondary drain; high visible secondary drain; or pan with float switch. A pan with a concealed secondary drain and a float switch isn't one of the options.

JMO
Since the float switch meets one of the three options by itself the secondary drain would not be required and in this case is in addtion to the requirement IMHO.
Reply With Quote
  #11  
Old 9/19/07, 5:23 PM
Robert J. OConnor, P.E.'s Avatar
Robert J. OConnor, P.E. Robert J. OConnor, P.E. is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 739
Robert J. OConnor, P.E. is often very helpful Robert J. OConnor, P.E. is often very helpful
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by mlarson
Since the float switch meets one of the three options by itself the secondary drain would not be required and in this case is in addtion to the requirement IMHO.
Actually, the IRC does not allow a secondary drain line if the float switch option is used.

Quote:
Originally Posted by IRC M1411.3.1 Partial
3) An auxiliary drain pan without a separate drain line shall be provided under the coils on which condensate will occur. Such pan shall be equipped with a water level detection device that will shut off the equipment served prior to overflow of the pan.
Now if you use a pan that has a secondary drain line to a clearly visible location that would meet one of the options, and then if you add the float switch that would be supplementary.

The point is that a pan with a concealed secondary drain and a float switch isn't one of the options, and doesn't meet the IRC provisions.

JMO



Robert O'Connor, PE
Eagle Engineering & Inspections
Adjunct Professor
NACHI Education Committee
www.reporthost.com/eagleengineering

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 9/19/07 at 5:27 PM.
Reply With Quote
  #12  
Old 9/19/07, 5:33 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,361
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Joined Primary and Secondary and Float switch

If it is as you say, then the fix would simply be to plug the secondary drain line in this case.

Since that seems ridiculous on its face (because it decreases protection), the IRC should probaly be re-written for clarification. JMO

Last edited by mlarson; 9/19/07 at 5:36 PM.
Reply With Quote
  #13  
Old 9/20/07, 4:05 AM
Robert J. OConnor, P.E.'s Avatar
Robert J. OConnor, P.E. Robert J. OConnor, P.E. is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 739
Robert J. OConnor, P.E. is often very helpful Robert J. OConnor, P.E. is often very helpful
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by mlarson
.. then the fix would simply be to plug the secondary drain line in this case.
Actually the correct fix would be to route the secondary drain line to a visible location. The float switch could stay as an optional back-up in case the secondary drain clogs.

The IRC restrictions make sense to me as the intent is if there's a problem with the primary drain which starts overflowing the owners should be aware of that (visible condensate flowing or the unit shuts down). Otherwise if there is a primary drain problem, it could be overflowing for quite some time before it's noticed, which can damage the equipment and/or pans, as well as the building.

I know of at least one case locally where the secondary drain discharge was not visible, and the primary drain clogged (it happens). Over time it damaged the unit and pan, which then started leaking onto a ceiling below. The unit and pan, as well as a section of the ceiling, insulation, and floor below had to be replaced.



Robert O'Connor, PE
Eagle Engineering & Inspections
Adjunct Professor
NACHI Education Committee
www.reporthost.com/eagleengineering

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #14  
Old 9/20/07, 8:55 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,361
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by roconnor
Actually the correct fix would be to route the secondary drain line to a visible location. The float switch could stay as an optional back-up in case the secondary drain clogs.
Why? If a secondary drain is not required, then one could simply plug the secondary drain line in this example and rely on the float switch as the second means of protection from flooding. It would then meet the requirements as stated in the IRC. No re-routing to a visible location necessary. It's like the seconddary drain line wasn't even there. This installation goes above the minimum requirments of the IRC. Though non-standard, it is not wrong.
Reply With Quote
  #15  
Old 9/20/07, 10:57 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
jlybolt hasn't had much positive or negative feedback
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Joined Primary and Secondary and Float switch

IRC is mininum standards.