  #16  
Old 9/20/07, 12:51 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by jlybolt
IRC is mininum standards.
Exactly

Per the IRC it wouldn't be wrong to just plug the secondary drain and rely on the pan float switch. But the drain line is already installed, so IMO the correct fix would be to reroute the discharge to a visible location (stub outside, slop sink, etc), which also provides better protection.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #17  
Old 9/20/07, 12:58 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by roconnor
Exactly

Per the IRC it wouldn't be wrong to just plug the secondary drain and rely on the pan float switch. But the drain line is already installed, so IMO the correct fix would be to reroute the discharge to a visible location (stub outside, slop sink, etc), which also provides better protection.
The minimum standards are met if you remove the drain line on the secondary pan completely. Nuff said.
Reply With Quote
  #18  
Old 9/20/07, 1:37 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Joined Primary and Secondary and Float switch

Feel free to recommend what you are comfortable with.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #19  
Old 9/22/07, 12:03 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Joined Primary and Secondary and Float switch

It violates common sense. I often say this:

"The auxiliary condensate drain discharges into the primary condensate drain pipe. Should the primary drain pipe ever clog, water may overflow the drain pan and damage the ceilings below. Service by a licensed HVAC contractor is recommended."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #20  
Old 9/22/07, 8:12 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by jfunderburk
It violates common sense. I often say this:

"The auxiliary condensate drain discharges into the primary condensate drain pipe. Should the primary drain pipe ever clog, water may overflow the drain pan and damage the ceilings below. Service by a licensed HVAC contractor is recommended."
To drive the point across and better CYA you may want to add

"The auxiliary condensate drain discharges into the primary condensate drain pipe. Should the primary drain pipe ever clog, water may overflow the drain pan and potentially damage the service floor, insulation, ceiling joist/plaster/sheetrock, and furnishings or flooring below. Service by a licensed HVAC contractor is highly recommended."

but I did like the intent of the original, Thanks!



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #21  
Old 9/22/07, 10:58 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Joined Primary and Secondary and Float switch

Quote:
Originally Posted by badair
I did like the intent of the original, Thanks!
I like yours better. Thanks.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #22  
Old 9/22/07, 3:19 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Joined Primary and Secondary and Float switch

That Texan writes good...

Thanks Barry...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Washer Secondary Drain roconnor Plumbing Inspections 7 4/2/06 1:02 PM


All times are GMT -4. The time now is 11:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts