Default L vent to single wall?

This oil-fired boiler vent reduces at the flue. Am I correct in saying that it transitions from a double walled L-vent to a single walled pipe (maintaining the interior diameter)? BTW - the label was no help.
Attached Thumbnails
l-vent-single-wall-vent-conn-reduces.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/17/11, 4:58 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: L vent to single wall?

Are you sure thats double wall L-Vent on the right? It looks like older single wall crimped into a reducer fitting.

Also there are special fittings to go from double to single wall, with one side an insert-and-twist for the double wall, and the other side insert-and-screw for the single wall.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #3  
Old 10/17/11, 5:00 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: L vent to single wall?

I agree looks like that to me also ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #4  
Old 10/17/11, 5:12 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: L vent to single wall?

You are right Rob (and Roy) - it was a single wall. There were no twist and fit joints. Therefore - the reduction is improper, correct?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #5  
Old 10/17/11, 5:23 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: L vent to single wall?

Quote:
Originally Posted by bsmith View Post
You are right Rob (and Roy) - it was a single wall. There were no twist and fit joints. Therefore - the reduction is improper, correct?
Correct... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 10/17/11, 5:30 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: L vent to single wall?

Thanks Roy.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #7  
Old 10/17/11, 7:13 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: L vent to single wall?

Yes you not reduce a oil fired burner, At least 15 years ago you couldn't lol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Oil Furnace with flexible exhaust to concentric wall vent jfisher1 Canadian Inspectors 11 11/10/11 9:30 PM
Wall Mounted Gas Fireplace Vent krigler Inspecting HVAC Systems 2 8/10/10 9:11 AM
single row of brick for foundation wall bking Structural Inspections 23 7/9/09 7:40 AM


All times are GMT -4. The time now is 11:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts