The first Pic shows the entry into the attic I wonder how many large HI'S or should I say fat HI'S would have disclaimed this entry hole as being to small. Once into the attic the hot water heater vent disconnected and within 4 feet of the open return air vent.

When I arrived this morning the A/C unit was turned off and the inside temp was above 80 I let the A/C unit run while I made my outside rounds and the roof. I had just felt of the suction line while outside and knew that there was a problem because the suction line felt to warm to me even on a warm house.

After running the A/C for approximately 45 minutes the inside temp fell to 76 but the supply was only reading 70. My mind was churning telling me that the return in the attic had to be open and sure enough that is what I found.


There were also 3 supply ducts under the home that were disconnected cooling the crawl space.

This was probally the worst abortion that I have inspected in a while. So many issues it will take a book to write. Furnace was installed in a bedroom closet with improper combustion air. Had to unscrew the closet wall to locate the furnace. The condensate was dripping out of the bottom of the furnace supply air plenum under the home. No ridge gas pipe into furnace cabinet. The supply plenum was constructed around a gas and domestic water supply piping.


</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 11:17 PM..
Reply With Quote
  #2  
Old 7/18/07, 5:04 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Leathal combination??????

Y' know...I spent nearly forty years in an HVAC business and came across a whole bunch of "doozies". But that has to be the "dooziest".

It's one thing to find individual, really gross issues, but that many done on purpose is way too much.

Somebody just don't care enough to be the very best they can be.

That's what I would tell the people who worked with me--"Care enough to be the best you can be". (Credit Hallmark and the US Army)



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #3  
Old 7/18/07, 5:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Leathal combination??????

Quote:
Originally Posted by jwilliams4
Y' know...I spent nearly forty years in an HVAC business and came across a whole bunch of "doozies". But that has to be the "dooziest".

It's one thing to find individual, really gross issues, but that many done on purpose is way too much.

Somebody just don't care enough to be the very best they can be.

That's what I would tell the people who worked with me--"Care enough to be the best you can be". (Credit Hallmark and the US Army)
Yea J What really got my goat the A/C unit and furnace was an 05 model and someone just installed new units on a pile of junk duct work and never even looked to see what kind of shape or condition the rest of the system was.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 7/18/07, 6:36 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Leathal combination??????

I'm currently "battling" with an HVAC company over the gas-fired clothes-dryer vent that passes through the return-air plenum.

They want me to tell my client that it is perfectly acceptable



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 7/18/07, 7:20 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Leathal combination??????

Jeff,
Is that the new plenum rated gas vent.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 7/18/07, 7:53 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Leathal combination??????

Quote:
Originally Posted by jpope
I'm currently "battling" with an HVAC company over the gas-fired clothes-dryer vent that passes through the return-air plenum.

They want me to tell my client that it is perfectly acceptable

That should not be a battle at all you should win hands down. Drop a dime to the gas Co they will shut the gas off in most places and see who wins that one.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 7/18/07, 8:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Leathal combination??????

You would think. The HVAC company want me to "sign-off" on this, because it was "built like this originally in 1997."

I've told them I will not endorse this installation, nor will I tell my client that it is acceptable. They are making idol threats, but I'm not budging. They don't want to put anything in writing either - I wonder why. . .

I couldn't get the picture to load properly, but here is the report page showing the inside of the plenum. . .
Attached Files
File Type: pdf 07051401.pdf (58.1 KB, 129 views)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 7/18/07, 9:55 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Leathal combination??????

Quote:
Originally Posted by jpope
You would think. The HVAC company want me to "sign-off" on this, because it was "built like this originally in 1997."

I've told them I will not endorse this installation, nor will I tell my client that it is acceptable. They are making idol threats, but I'm not budging. They don't want to put anything in writing either - I wonder why. . .

I couldn't get the picture to load properly, but here is the report page showing the inside of the plenum. . .
No fault here I would have held to my guns also.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
ICC Residential Combination Inspector Certification Exam Prep. Jen L. Lifshotz Inspection Education & Training 2 8/28/07 4:47 PM
Hallucinogens and masonry are a bad combination kshepard Exterior Inspections 7 3/3/07 5:41 PM
Combination Air Gap/Fountain cbuell Plumbing Inspections 1 9/12/06 11:56 AM


All times are GMT -4. The time now is 4:44 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts